    Broken compressor



    Some pictures, compressor 1 month old.
    Not for sensitive peoples.
    Freezer applicaton Copeland
    Liquid slugging, ***** wash-out.
    Afbeelding (5): piston twisted in the cylinder
    Afbeelding: right piston is gone.
    Attached Images Attached Images
    Last edited by Peter_1; 27-03-2004 at 06:35 AM.



  2. #2
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: Broken compressor

    Certainly a gruesome sight. Was that Coppper plating I saw on the piston head? That would indicate moisture presence to me.....

    Certainly looks like a dry set of bearings on the bottom end and the crankshaft.

    I have encountered similar failures in air cooled air conditioners that were grossly overcharged. The first the manufacturer knows is a waranty claim.

    The scenario goes like this.....

    1. Some idiot packs a double or treble charge into the unit. (Remember, packaged A/C has no receiver and operates on a measured charge).
    2. In winter months the unit shuts down over a weekend.
    3. When the building temperature decays and stabilises, there is likely to be a TD of 15 degrees C or more between the in and out sections.
    4. The refrigerant in the indoor section migrates to the outdoor unit.
    5. It fills the condenser, overflows and runs down the discharge pipe by gravity.
    6. If it overflows the muffler and settles on top of the piston / valve assembly the rapid expansion when the compressor restarts and injects hot gas into this body of static cold liquid will split a piston or connecting rod and sometimes blow a muffler apart.

    Far fetched? It happens and the usual explanation is a bad batch of compressors?.. When the real problem is hydraulic damage due to overcharging and bearing failure due to liquid washing.

    Seen it many times. Peter.
    ________
    Mercedes-Benz 300SEL 6.3 history
    Last edited by Argus; 07-02-2011 at 08:02 AM.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Broken compressor

    Ooops........
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Unhappy Re: Broken compressor

    sorry about your compressor, peter.

    one of the ways to avoid these situations is to keep the system heated at all times.

    a 200W heater in the crankcase, and a 170W heater around the liquid saperator.

    everything on the pictures is related to liquid entering the compressor.

    another helpful thing that I do, is checking that pumpdown realy empty the system.

    chemi

  5. #5
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    Re: Broken compressor

    Hi peter

    What application was the compressor running pack/single unit(CU).etc

    Regards Mark

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Broken compressor

    Quote Originally Posted by MarkFiddy
    Hi peter

    What application was the compressor running pack/single unit(CU).etc

    Regards Mark
    Single unit, remote KUBA condensor on a KUBA SGB evaporator.
    Not very nice after some weeks.

  7. #7
    Join Date
    Oct 2001
    Location
    Perth, Australia
    Posts
    87
    Rep Power
    23

    Re: Broken compressor

    It will be interesting to see how Trane with their ceramic bearings and TurboCor with their magnetic bearing compressors get on. It would certainly make life easier to not have any oil in the system.
    Mark Baker

  8. #8
    rbartlett's Avatar
    rbartlett Guest

    Re: Broken compressor

    a good engineer would have got that running again till the new one arrived ;-)

    cheers

    richard

  9. #9
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Talking Re: Broken compressor

    Quote Originally Posted by rbartlett
    a good engineer would have got that running again till the new one arrived ;-)

    cheers

    richard
    No problem with that: when I arrived, it was running really smooth, no vibration at all, (very) low discharge temperatures, low discharge pressures, AMPS low, so... why in fact looking at it ?
    So.. am i a good engineer now?
    It was running this way for some days.

    It was due to a sump full of WD40 that it was running that smooth.

    Sure I have WD40: a good friend of me is working at the sole Belgium importer of that stuff.
    Ever tried this ? Spray WD40 on the thread of a light bulb, screw it in the socket, put in the wall socket and immerse the bulb completely under water. Light will light under water and normally, no safety device will trip at all.
    Try at your own risk but that's the way he always impresses customers.

  10. #10
    Join Date
    Mar 2002
    Location
    San Francisco Bay Area
    Posts
    180
    Rep Power
    23

    Re: Broken compressor

    Quote Originally Posted by Peter_1
    Sure I have WD40: a good friend of me is working at the sole Belgium importer of that stuff.
    Ever tried this ? Spray WD40 on the thread of a light bulb, screw it in the socket, put in the wall socket and immerse the bulb completely under water. Light will light under water and normally, no safety device will trip at all.
    Try at your own risk but that's the way he always impresses customers.
    A bit off topic here, but I have cleaned up enough gummed-up sliding doors on deli cases, roller tracks on reach-in doors, etc. that I am not a big fan of the stuff. I carry food-grade silicone spray and teflon spray lube, both excellent DRY lubes that will not attract dust and turn into a gummy mess. I carry "liquid wrench" for loosening stuck/rusted screws & bolts and turbine oil for lubricating motors.

    But thanks for the info. If I ever need to do some underwater illumination, it sounds like just the thing! Maybe all those people electrocuted by hair dryers in the bath should be giving the things a good spray with ol' WD40 before jumping in the tub!

    Rog
    Last edited by RogGoetsch; 29-03-2004 at 03:18 AM.

  11. #11
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Broken compressor

    Spray WD40 on the thread of a light bulb, screw it in the socket, put in the wall socket and immerse the bulb completely under water. Light will light under water and normally, no safety device will trip at all.
    Would you have this in QUICKTIME format

  12. #12
    Join Date
    Nov 2003
    Location
    NSW, Australia
    Age
    40
    Posts
    242
    Rep Power
    21

    Re: Broken compressor

    INOX, any of you guys other then aussies heard of inox? its based on lanolin and made in australia - i prefer it to a can of wd40, seems thinner and gets into all those nice rusted nuts and bolts good, available in a bottle or pressure spray can like wd40. also great for bearings frees them up a treat compared to wd which makes them feel binding through the tacky oil.

    not suitable to sliders etc as Rog approach is still the best for those applications.
    "Old fridgies never die, they just run out of gas!"

  13. #13
    rbartlett's Avatar
    rbartlett Guest

    Re: Broken compressor

    [QUOTE=Bones]INOX, any of you guys other then aussies heard of inox? its based on lanolin and made in australia -



    yes but they were never the same since hutchence topped himself

    cheers

    richard

  14. #14
    shogun7's Avatar
    shogun7 Guest

    Re: Broken compressor

    When I was a mechanic and I was troubleshooting an electrical problem I always fixed the problem with WD 40 and never had to replace any defective electric control. Boy thats good stuff LMAO
    Roger

  15. #15
    shogun7's Avatar
    shogun7 Guest

    Re: Broken compressor

    Richard... A little dab il do ya!
    Roger

  16. #16
    Join Date
    Jun 2003
    Location
    Georgia
    Posts
    72
    Rep Power
    21

    Re: Broken compressor

    Quote Originally Posted by Peter_1
    Some pictures, compressor 1 month old.
    Not for sensitive peoples.
    Freezer applicaton Copeland
    Liquid slugging, ***** wash-out.
    Afbeelding (5): piston twisted in the cylinder
    Afbeelding: right piston is gone.
    Peter.... That is not a compressor you are showing! It is the new Copeland Piston Puzzle Kit Toy, part number #00 (Uh Oh)

  17. #17
    Join Date
    Aug 2002
    Location
    uk
    Age
    55
    Posts
    14
    Rep Power
    0

    Exclamation Re: Broken compressor

    are you mad!!!!

  18. #18
    Join Date
    Aug 2002
    Location
    uk
    Age
    55
    Posts
    14
    Rep Power
    0

    Re: Broken compressor

    peter,did you buy new parts or stick them back together?

  19. #19
    Join Date
    May 2003
    Location
    Edmonton alberta Canada
    Posts
    95
    Rep Power
    21

    Re: Broken compressor

    I have spent the better part of my life working on rinks should I say since 1963 so I have seen many broken compressors in nh3 and R22 ,.I always preferred to work on the NH3 but could do both. I saw the pictures and I do agree the compressor was flooding liguid and washed out the oil or diluted it so bad it no longer would lub the mains or throws anyway it is a problem with some systems. I have installed some suction accumulators which do help but you do have to have good oil return. what systems to you use flooded or txv chillers where you are . I do have to go now but am very interested in this subject so will talk later.

    Wes Maxfield
    Wes Maxfield

  20. #20
    Join Date
    May 2003
    Location
    Edmonton alberta Canada
    Posts
    95
    Rep Power
    21

    Re: Broken compressor

    Quote Originally Posted by shogun7
    When I was a mechanic and I was troubleshooting an electrical problem I always fixed the problem with WD 40 and never had to replace any defective electric control. Boy thats good stuff LMAO
    Roger
    Their is not a service truck in Canada without WD40 it is the greatest stuff in the world it will fix anything but a hangover
    and it will even help that. Wes Maxfield
    Wes Maxfield

Similar Threads

  1. can overfilling/overcharging damage a compressor?
    By fredjchavez in forum Trouble Shooting
    Replies: 10
    Last Post: 12-02-2009, 10:30 AM
  2. Compressor pumping efficiency
    By shogun7 in forum Fundamentals
    Replies: 0
    Last Post: 25-02-2004, 10:50 PM
  3. One Half of a Part Wound Compressor Motor is Burnt
    By aygul in forum Trouble Shooting
    Replies: 2
    Last Post: 25-08-2003, 11:11 AM
  4. Compressor failure...... cause
    By herefishy in forum Technical Speculations
    Replies: 8
    Last Post: 06-12-2002, 12:15 AM
  5. Starting a compressor, and receiver questions.
    By DaBit in forum Technical Speculations
    Replies: 9
    Last Post: 24-08-2002, 12:37 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •