    Thumbs up Air conditioning



    Hi,
    Can anybody clear my doubt pls
    I believe that when the room attains the set temperature the thermostat will de energise the liquid line solenoid valve so that the the compressor will cut off through low pressure switch

    My doubt is if the compressor cut off in LP switch then how it will restart again when the room temperature starts increasing

    i heard that if the unit trips through LP switch, without resetting we cannot start the unit

    can anybody brief me how the cycle is controlled ill be thankful to you because iam weak in controls and i feel difficult to understand the control circuits

    regards,
    Balaji



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Air conditioning

    That depend on LP switch and used controller settings.
    You could have Lp switch with manual or automatic reset.
    You could also have control that needs manual resetting and other one that is automatically reset few times and after that you need manual reset.

    In case when pump down circuit is used (like your example) Lp switch is automatically reset.

  3. #3
    Join Date
    Nov 2007
    Location
    singapore
    Age
    45
    Posts
    24
    Rep Power
    0

    Re: Air conditioning

    Hi nike,
    Thanks for your reply. i want to develop my knowledge in control circuits is there any reference book, if you have please forward to me. except you nobody reply to this thread why? I asked silly questions ?
    regards,
    Balaji

  4. #4
    Join Date
    Mar 2005
    Location
    u.a.e
    Age
    68
    Posts
    169
    Rep Power
    20

    Re: Air conditioning

    A question is a question,
    AND IT IS BETTER TO ASK THEN NOT TO ASK....
    What you asked is a pump down type system and when temperature satisfied the thermostat cuts solinoid and system stops by L.P, Normally this type of systems works with two L.P switches, One for the Pump down and second one for SAFETY CUT OUT, The second L.P swith set point is much lower then pump down L.P.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Air conditioning

    Quote Originally Posted by balaji View Post
    I asked silly questions ?
    regards,
    Balaji
    Check my signature!

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Air conditioning

    Quote Originally Posted by balaji View Post
    Hi nike,
    Thanks for your reply. i want to develop my knowledge in control circuits is there any reference book, if you have please forward to me.
    No, I don't have any book.
    Most of required knowledge you could gather by reading service manuals of equipment.

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Air conditioning

    Quote Originally Posted by malik55 View Post
    A question is a question,
    AND IT IS BETTER TO ASK THEN NOT TO ASK....
    What you asked is a pump down type system and when temperature satisfied the thermostat cuts solinoid and system stops by L.P, Normally this type of systems works with two L.P switches, One for the Pump down and second one for SAFETY CUT OUT, The second L.P swith set point is much lower then pump down L.P.
    To add to that, Pump down LP switch is automatically reset type and safety cut out switch is manually reset type.

  8. #8
    Join Date
    Nov 2008
    Location
    United Kingdom
    Age
    46
    Posts
    33
    Rep Power
    0

    Re: Air conditioning

    Nike, check the posters signature name... and relax.

    To Balaji... try to use screwdriver for LP adjustment. It helps to understand how switch works.

  9. #9
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Air conditioning

    balagi, i could see the use of this type of control on a refrigeration plant but it will not cut out on low pressure as such just a differential pressure, if you had a system cutting out like this everytime it reached thermostat i can't see it being good for the compressor.

  10. #10
    Join Date
    Nov 2007
    Location
    singapore
    Age
    45
    Posts
    24
    Rep Power
    0

    Re: Air conditioning

    Thank you guys atleast i received 8 replies, iam satisfied and i hope no need to go for two LP switch even a single LP with three set points can do that

  11. #11
    Join Date
    Mar 2005
    Location
    New Zealand
    Age
    43
    Posts
    64
    Rep Power
    20

    Re: Air conditioning

    Balaji, This is very straight forward, You are correct in saying that when the thermostat reaches temp it de-energises the solenoid and allows the compressor to pump down then cut out on the LP switch, when the thermostat calls for cooling again, the solenoid opens and, the pressure rises, closing the contacts of the LP switch and the copmpressor will restart. This type of control circuit is not always needed on a chiller but almost always on a freezer. The advantage of this circuit is if there is a great distance between the compressor and Evaporator, you do not need any cables running between as you can locate the Solenoid inside with the Evaporator. Hope this helps.

  12. #12
    Join Date
    Mar 2005
    Location
    u.a.e
    Age
    68
    Posts
    169
    Rep Power
    20

    Re: Air conditioning

    Different type of controls can do same things, A systems can pump downs by a thermostat and also by a L.P switch.

  13. #13
    Join Date
    Jan 2008
    Location
    India
    Age
    70
    Posts
    171
    Rep Power
    17

    Re: Air conditioning

    Normally LP is auto reset where as the HP will have to be manually reset.

Similar Threads

  1. Air Conditioning Courses
    By stesmith1981 in forum Industrial
    Replies: 8
    Last Post: 09-03-2010, 06:33 PM
  2. Replies: 11
    Last Post: 13-08-2008, 01:22 PM
  3. Unique cooling system Port-A-Cool replaces air conditioning
    By LC-Europe in forum New Technologies
    Replies: 20
    Last Post: 30-01-2008, 08:29 AM
  4. Replies: 2
    Last Post: 01-07-2007, 04:30 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •