07-01-2009, 06:47 PM #1
R22 pipe work & replace technology
Hi all
I have a site with 2 x R22 Fujitsu units to be removed and 2 new cassettes to be installed. The pipe work is run through walls, up risers and over a plastered ceiling so i was thinking of re using the existing pipe work and fitting either a Daikin, Mitsi Electric or Toshiba system which i know has their 'replace technology' to use existing pipe work.
I was wondering if anyone has any tips or recommendations for this install?. The pipe work sizes are the correct size for the new units and as far as i can tell at the survey there has not been any compressor failures.
Many thanks, Gareth
-
07-01-2009, 06:58 PM #2
Re: R22 pipe work & replace technology
I'd like to know of any experiences in this department also!
He who dies with the most Toys, WINS!
-
07-01-2009, 08:25 PM #3
Re: R22 pipe work & replace technology
I can recomend the ME Mr Slim option.
It has the special filter which is used to flush & clean the system on first start up.
This is has the benifit of positively cleaning up all the system & removing all contamination oil or other contamination into the filter which is then isolated from the system.
This seem to me a better option than having a new system with some fancy oil which can operate with some oil mineral oil mix as this still leaves any other contamination to circulate & possibly cause futher damage down the line.
-
07-01-2009, 08:28 PM #4
Re: R22 pipe work & replace technology
Just check with the manufacturer for the limitations on pipe length for the pipe size & unit size you need to make sure you are within the max pipe length for that combination.
-
07-01-2009, 09:12 PM #5
Re: R22 pipe work & replace technology
The cassettes are a 7kw & a 10kw. Pipe work lengths are about 25 metres with a 3 metre rise so should be ok with all the manufacturers?
Gareth
-
07-01-2009, 09:37 PM #6
Re: R22 pipe work & replace technology
Hi I,ve used Endo-flush many times with no problems
Please read previous thread
http://www.refrigeration-engineer.co...ght=endo+flush
Cheers Bernie
-
07-01-2009, 10:50 PM #7
Re: R22 pipe work & replace technology
i have used solkane to flush which works quite well.
Similar Threads
-
Chilled water pipe work blocked
By puddleboy3 in forum Air ConditioningReplies: 11Last Post: 24-10-2009, 08:22 PM -
Measurement of pipe lengths
By batfink in forum Technical DiscussionsReplies: 11Last Post: 23-09-2008, 09:50 PM -
Mitsubishi Replace Technology
By Daikin=Overated in forum Air ConditioningReplies: 3Last Post: 10-05-2008, 12:21 PM -
new 410 old 22 pipe work
By MRC Guts in forum RefrigerantsReplies: 10Last Post: 10-03-2007, 12:04 AM -
old pipe work
By bernard in forum CommercialReplies: 12Last Post: 27-03-2004, 12:09 PM