    freecooling



    hi
    can anyone help with how to calculate the airflow requirements and motor sizing of a system to cool a data centre using ambient air only.plan is to cool data ctr when ambient temp low enough to permit this. ac units still used when neccessary.
    size of room 8 mtrs by 8 mtrs by 3 mtrs. heat load 130kw. had several quotes but can tell these would never meet the demand, any help on how best to calculate this very much appreciated.



  2. #2
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: freecooling

    Intel have done a lot of research in the desert on just using ambient only.

    http://www.itbusinessedge.com/cm/com...nter/?cs=20341

    We are much cooler and yet we have not seen one new one using this method. Most farms are now using integral cabinets from Rittal or similar HP, Airedale Knarp (sp).

    http://www.42u.com/rittal-lcp.htm

  3. #3
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: freecooling

    For sensible heat load
    KW = 1.21 × M ³/s × ∆t


    So for example your outside ambient air is introduced into the room at 10°C & you want the room temp not higher than 25°C.
    then you may be looking at about 7M ³/s supply air volume.


    But if the outside air is 20°C & you still require room temp at 25°C then you may be looking at about 21M ³/s supply air volume.

    For very low outside ambient temperature the AHU will need some RA mix with SA as you would not want for example -5°C supply air into the room & then have condensation issues.


    The implications for air velocity in the room & the size / control of the AHU plant are clear.
    There will be some practical limitations for what is realistically achievable.

    Introducing some cool outside air for some free cooling will make usefull reduction in power consumption but trying to provide 100% free cooling for most of the year I would suggest be very difficult.

    I have myself never yet seen such a system installed in the UK but if you are able to post more details that would be interesting as the resident design experts could take this further.

  4. #4
    Join Date
    Dec 2008
    Location
    England
    Age
    41
    Posts
    24
    Rep Power
    0

    Re: freecooling

    The draugt problem could be overcome by using a low impulse textile duct, for 7 m/s it would need to be about 1100mm diameter.

  5. #5
    Join Date
    Dec 2008
    Location
    England
    Age
    41
    Posts
    24
    Rep Power
    0

    Re: freecooling

    The textile duct itself would remain condensation free without himidity control.

  6. #6
    Join Date
    Dec 2008
    Location
    England
    Age
    41
    Posts
    24
    Rep Power
    0

    Re: freecooling

    http://i17.photobucket.com/albums/b9...Animation2.gif
    15 posts, and now i can put a link in :-)

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: freecooling

    OK, so you now have 15 posts but please do not keep expecting free advertising for your products
    Brian - Newton Abbot, Devon, UK