    Please help on DAIKIN rzq/FBQ125 !!!



    Hello, i'm french. I don't speak english very well so excuse me.
    I'm looking for the "big manual" for rzq 125. It is to know all code of the controller and the outdoor unit.
    You can mail me information to nak210479@free.fr

    Thank you !!!and happy new year 2009!!!!
    Cédric



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Please help on DAIKIN rzq/FBQ125 !!!

    Quote Originally Posted by nak210479 View Post
    Hello, i'm french. I don't speak english very well so excuse me.
    I'm looking for the "big manual" for rzq 125. It is to know all code of the controller and the outdoor unit.
    You can mail me information to nak210479@free.fr

    Thank you !!!and happy new year 2009!!!!
    Cédric
    Check here:

    http://www.daikinac.com/landing.asp


    And this is direct download!

    Last edited by nike123; 02-01-2009 at 09:45 AM.

  3. #3
    Join Date
    Apr 2008
    Location
    france
    Age
    45
    Posts
    13
    Rep Power
    0

    Re: Please help on DAIKIN rzq/FBQ125 !!!

    ok thanks.
    My defrost is too long(11 min). In only 5 min max there is not frost. How can i modif this setting.

    Cédric

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Please help on DAIKIN rzq/FBQ125 !!!

    Quote Originally Posted by nak210479 View Post
    ok thanks.
    My defrost is too long(11 min). In only 5 min max there is not frost. How can i modif this setting.

    Cédric
    Since you are not service technician, I would suggest you to consult with your service technician, because such adjustment is not for someone who doesn't understand consequence of such action.

    Why is bothering you your defrost time?

  5. #5
    Join Date
    Apr 2008
    Location
    france
    Age
    45
    Posts
    13
    Rep Power
    0

    Re: Please help on DAIKIN rzq/FBQ125 !!!

    because it is too long so when it is below 1° outside there is lot of defrost. the temperature does not arrive has go up, it consume more for nothing and it do not heat up, it defrost while it can be heating up.

    I hope you understang what i try to write.
    Cédric

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Please help on DAIKIN rzq/FBQ125 !!!

    Quote Originally Posted by nak210479 View Post
    because it is too long so when it is below 1° outside there is lot of defrost. the temperature does not arrive has go up, it consume more for nothing and it do not heat up, it defrost while it can be heating up.

    I hope you understang what i try to write.
    Cédric

    What is your humidity in that area?
    Are you sure that AC works fine, maybe it is short of gas?
    It gives simmilar symptoms when gas leaks.
    Do not attempt to change anything if you are not qualified. Call for expert.

  7. #7
    Join Date
    Apr 2008
    Location
    france
    Age
    45
    Posts
    13
    Rep Power
    0

    Re: Please help on DAIKIN rzq/FBQ125 !!!

    it is not pas leaks. humidity is between 70and 80% but there is defrost when T° outside is 11°. And there is not frost !!!

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Please help on DAIKIN rzq/FBQ125 !!!

    Quote Originally Posted by nak210479 View Post
    it is not pas leaks. humidity is between 70and 80% but there is defrost when T° outside is 11°. And there is not frost !!!
    Then call your service technician, because defrost should not happen below 7°C outside temp.

  9. #9
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Please help on DAIKIN rzq/FBQ125 !!!

    In relation to your unit, you either have a refrigerant leak or the outdoor unit is short cycling.
    If your indoor filters are blocked and the unit does not see a change in the return air temperature it may also go into a premature defrost..

  10. #10
    Join Date
    Apr 2008
    Location
    france
    Age
    45
    Posts
    13
    Rep Power
    0

    Re: Please help on DAIKIN rzq/FBQ125 !!!

    the outdoor unit is long cycle (16 03 03)
    i have a thermometer inside my home but outside the indore unit. So the T° checked is that of the room.

  11. #11
    Join Date
    Apr 2008
    Location
    france
    Age
    45
    Posts
    13
    Rep Power
    0

    Re: Please help on DAIKIN rzq/FBQ125 !!!

    Quote Originally Posted by nike123 View Post
    Then call your service technician, because defrost should not happen below 7°C outside temp.
    My technician says all is right....
    he doesn't know very well this unit i think....

  12. #12
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Please help on DAIKIN rzq/FBQ125 !!!

    Quote Originally Posted by nak210479 View Post
    the outdoor unit is long cycle (16 03 03)

    Short cycling at which Brunstar refers is when discharged air from outdoor unit doesn't freely goes out. Instead, some significant portion of that air rebates from surrounding obstacles and circulate again in outdoor unit heat exchanger, and therefore, efects outdoor air entereng temperature to be lower than actualy outside air temperature is. That causes uneccesary defrosting.

    What you are refiring is page 155 of manual.

    Temperatures about what you are speaking in your posts are not clear any more after last post. So, please measure again outdoor temperature and humidity and indoor temperatures at inlet and outlet of indoor units!
    Also put your indoor units on high fan and temperature at max (30°C) and check temperatures after 5 min has pased. If needed, you could open windows partialy to alow that indoor units works at maximum power.

    Also give us model# of indoor units. This is in order to calculate power emited from indor units and to evaluate proper functioning of outdoor unit!

  13. #13
    Join Date
    Apr 2008
    Location
    france
    Age
    45
    Posts
    13
    Rep Power
    0

    Re: Please help on DAIKIN rzq/FBQ125 !!!

    sorry it 16(26) 3 02

  14. #14
    Join Date
    Apr 2008
    Location
    france
    Age
    45
    Posts
    13
    Rep Power
    0

    Re: Please help on DAIKIN rzq/FBQ125 !!!

    OK, i take T° tomorrow.
    Bye
    Cédric

  15. #15
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Please help on DAIKIN rzq/FBQ125 !!!

    Quote Originally Posted by nak210479 View Post
    sorry it 16(26) 3 02
    From what I read in manual, that is slow defrost starting, and if I correctly interpret that, and what you are saying until now, your unit behave opposite of that.
    Yet another symptom of faulty unit.

  16. #16
    Join Date
    Apr 2008
    Location
    france
    Age
    45
    Posts
    13
    Rep Power
    0

    Re: Please help on DAIKIN rzq/FBQ125 !!!

    hello,
    outdoor temp=-3.5°
    humidity 80%
    indoor aking for 21
    temp is 20 no more
    temp of indoor unit 41° and one defrost(11min)/H
    I try tomorrow with asking 30°.
    Thanks.
    Cédric

  17. #17
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Please help on DAIKIN rzq/FBQ125 !!!

    Quote Originally Posted by nak210479 View Post
    hello,
    outdoor temp=-3.5°
    humidity 80%
    indoor aking for 21
    temp is 20 no more
    temp of indoor unit 41° and one defrost(11min)/H
    I try tomorrow with asking 30°.
    Thanks.
    Cédric
    By my calculations, that unit gives you around 14 kW of heat if you have 2100m3/h as stated on technical data of indoor unit. According to that, it probably works fine and your space require more heat and unit is probably undersized for space requirements.

  18. #18
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Please help on DAIKIN rzq/FBQ125 !!!

    with a coil temp of that i think that this unit is operating very well considering the ambient is -3.5 deg c.

    that unit won't give you 14kw output at those temperatures but i think it is operating well for the conditions it is under.
    What is the floor area in meters square it is trying to serve?

  19. #19
    Join Date
    Apr 2008
    Location
    france
    Age
    45
    Posts
    13
    Rep Power
    0

    Re: Please help on DAIKIN rzq/FBQ125 !!!

    120M² +80m² upstaire.
    And the first level is open to the second for 10M²

  20. #20
    Join Date
    Apr 2008
    Location
    france
    Age
    45
    Posts
    13
    Rep Power
    0

    Re: Please help on DAIKIN rzq/FBQ125 !!!

    the techincian says the rzq100 was enought !!!
    i have buy the 125 and it is too small....

  21. #21
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Please help on DAIKIN rzq/FBQ125 !!!

    Quote Originally Posted by nak210479 View Post
    the techincian says the rzq100 was enought !!!
    i have buy the 125 and it is too small....
    That is the problem with rule of thumb calculations!
    Try to partition that part which is open to second floor with cardboard or PVC foil and then see what happens with your indoor temperature.
    Last edited by nike123; 08-01-2009 at 06:28 PM.

  22. #22
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Please help on DAIKIN rzq/FBQ125 !!!

    200 square meters, at 120 watts per square meter you will need 24kw and you have about 12.5kw, have you done a heat loss calculation on the place?

  23. #23
    Join Date
    Apr 2008
    Location
    france
    Age
    45
    Posts
    13
    Rep Power
    0

    Re: Please help on DAIKIN rzq/FBQ125 !!!

    the technician had done a heat loss calculation and say the rzq100 was enought. With my calculation i thought the 125 maybe could be ok.
    Today humidity is 75% and T° -1. I have 22 indoor !!!!

  24. #24
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Please help on DAIKIN rzq/FBQ125 !!!

    That is indication that your AC produce insufficient heat for that outdoor conditions. Either you need some backup heating, or you need additional AC for harsh weather conditions, depending on your climate (if that AC is OK, and appears it is).

  25. #25
    Join Date
    Apr 2008
    Location
    france
    Age
    45
    Posts
    13
    Rep Power
    0

    Re: Please help on DAIKIN rzq/FBQ125 !!!

    ok thanks.
    Cédric

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Daikin, Why do we bother?
    By gwilliamson in forum Air Conditioning
    Replies: 21
    Last Post: 02-02-2010, 09:38 AM
  3. Daikin Comp and inverter
    By WCC73 in forum Air Conditioning
    Replies: 5
    Last Post: 08-11-2008, 08:44 PM
  4. Getting a price from Daikin....
    By monkey spanners in forum Chit Chat & Service Stories
    Replies: 4
    Last Post: 17-08-2008, 09:46 PM
  5. DAIKIN - Weybridge: How to get a Quote.
    By Makeit go Right in forum Air Conditioning
    Replies: 12
    Last Post: 25-04-2007, 08:50 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •