    old pipe work



    hi there o wise ones

    We ever possible I always replace old for new.But on this occasion i am tempted to re_use the old pipe work. The old system is R 22 the new system is R 407 c. I do not have much faith in endo flush can you recommend something else.

    Many thanks

    Bernard



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: old pipe work

    check before if the diameter of the old pipes will be suitable for R407C.

    if the old pipes are in good condition, it will be a good idea toflush and seal the ends and keep them for another job.

    chemi

  3. #3
    Join Date
    Mar 2004
    Location
    UK
    Posts
    624
    Rep Power
    21

    Smile Re: old pipe work

    Sorry chem cool

    I am removing an old ac system and replacing it with new. The pipe work runs under floor boards and would be very difficult and time consuming to run new pipes can you recommend something better than endo flush to wash the old pipe work

    regard

    bernard

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: old pipe work

    if the capacity of the new system is the same, it should be ok.
    but you will have to wash, to get out the mineral oil.

    I belive the new unit comes with POE oil and they dont like mixing.

    chemi

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: old pipe work

    Bernard, sell them one of the new Mitsi invertors, they will self-clean the piepwork for you.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Mar 2004
    Location
    UK
    Posts
    624
    Rep Power
    21

    Re: old pipe work

    hi brian

    please tell me more

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: old pipe work

    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Mar 2004
    Location
    UK
    Posts
    624
    Rep Power
    21

    Re: old pipe work

    brian

    many thanks very interesting

    bernard

  9. #9
    rbartlett's Avatar
    rbartlett Guest

    Re: old pipe work

    i have quoted some of these recently but i do wonder about the quality of the pipework as it's going from 22 to 410..'could' be an answer but equally could be a bit of a gift horse..

    cheers

    richard

  10. #10
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: old pipe work

    hi richard,

    he says its for R407C, so no problem with the pressure.

    if the pipes are in one piece, I would say its ok to go with changing as lond as you clean the system.

    chemi

  11. #11
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: old pipe work

    If you are upgrading to a system that uses R410a then the pipework must be changed - not cleaned - as the new pipework must meet the requirements for the increased pressures. Obviously, if the old pipework has the correct wall thickness then all will be OK if you can get the mineral oil out, but I doubt the old pipework will meet the new requirements.

  12. #12
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: old pipe work

    With old pipework you inherit old problems.

    Contamination from previous burn-outs you may not know of, incompatible oil residues and unknown leaks. Not to mention insulation that may be past its sell-by-date.

    I don't care who endorses it, thoroughly bad practice and needs to be discouraged.
    ________
    herbal vaporizers
    Last edited by Argus; 07-02-2011 at 08:02 AM.

  13. #13
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: old pipe work

    Well said Argus !!
    a problem shared is a problem halved

Similar Threads

  1. Prison vs Work
    By Abe in forum Chit Chat & Service Stories
    Replies: 11
    Last Post: 06-09-2010, 08:47 PM
  2. part p
    By eggs in forum Electrical
    Replies: 25
    Last Post: 15-11-2007, 08:55 PM
  3. Replies: 17
    Last Post: 25-08-2003, 09:56 PM
  4. Pipe sizes
    By benncool in forum Chit Chat & Service Stories
    Replies: 10
    Last Post: 08-07-2003, 10:58 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •