Results 1 to 10 of 10
Thread: LG not bringing on outdoor fan
31-12-2008, 04:47 PM #1
Got an LG wall mount AS-H12 R407c. We have found that the unit outdoor fan won't run.
Heating
On first start up the indoor fan runs as normal (which I would not expect) then the comp runs but the outdoor fan doesn't.
Checking power from indoor -
1 comp (live
2 N
3 RV (live)
4 Fan (dead)
Not checked on cooling due to time available.
We suspect the indoor board but we were told that had been changed recently.
Any clues
Multisync
london
31-12-2008, 05:06 PM #2
Re: LG not bringing on outdoor fan
Perhaps the outdoor temperature too low to allow the fan to run.
Some makes do this to prevent overloading the system, don't know about LG, sorry.Brian - Newton Abbot, Devon, UK
31-12-2008, 07:40 PM #3
31-12-2008, 08:08 PM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Where did you check power? On indoor or outdoor unit?
31-12-2008, 08:10 PM #5
31-12-2008, 08:17 PM #6
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
01-01-2009, 11:54 PM #7
I gather this is just a conventional compressor with only an indoor PCB? ie. not inverter and there's no defrost PCB in the outdoor?
If so, like nike123 says, in heat mode if the indoor coil thermistor is reading above ~55C, the indoor PCB will disable the outdoor fan to bring the coil temp down.
If the indoor coil is below 55C, then possible thermistor fault.
02-01-2009, 12:57 PM #8
Yes combined with the indoor fan running at start up rather than waiting for the coil to warm suggests coil sensor is faulty..
Thanks all
Multisync
London
02-01-2009, 02:08 PM #9
check fan motor neutral is not being broken through compressor contactor as this used to be an issue with lg outdoors,
02-01-2009, 04:42 PM #10