    Daikin E4



    Been to a server room callout today, system installed by myself 18 months ago. FAQ71B & RZQ71B9.
    Got called out two weeks ago to the E4 fault but when got there customer had restarted sytem and it was running away as normal. So I ran up fault history, cleared the E4 by holding on/off, did a complete restart and all was fine again, waited around for an hour, no faults, outdoor leds all ok. System showing all signs of a full charge of refrigerant.
    Got there today with the E4 back up and outdoor red led solid (protection device activated) went though E4 flow chart checked dc voltage (X64A on pcb) going to l.p sensor was 5V, coming back, 0V. Spoke to daikin tech he thought was definately faulty l.p sensor.
    So my question is, has anyone had this before and if so is it a case of complete recovery or is the l.p sensor somthing that just screws on and off quickly?



  2. #2
    Join Date
    Oct 2006
    Location
    UK
    Age
    57
    Posts
    165
    Rep Power
    18

    Re: Daikin E4

    Hi slim
    I am 80% sure that on the B9 models the pressure sensor is a screw on compression fitting. An easy was to tell is if there is a brass nut between the pressure sensor and the piping stub. If yes than you can remove the pressure sensor without having to recover the gas. If not then it’s a braze in type. (like on the new RZQ – C series)

    Happy New Year

    Obi Wan

  3. #3
    Join Date
    Dec 2008
    Location
    UK
    Posts
    564
    Rep Power
    24

    Re: Daikin E4

    If you go onto the Daikin Extranet, you will be able to access the exploded diagram. I think that this unit has a mechanical fitting LP sensor. It is a fairly common failure, the insulation on the sensor breaks down and moisture gets in causing intermittent failure. Daikin spares department may be able to help identify which type of fitting it has before you order it.

  4. #4
    Join Date
    Mar 2006
    Location
    Glasgow, Scotland
    Posts
    177
    Rep Power
    19

    Re: Daikin E4

    Can you tell us what the pipe length is between the indoor and outdoor?

  5. #5
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Re: Daikin E4

    Thanks for the replies, yes there is a brass nut inbetween the sensor and piping stub so thats good I wont have to recover.

    Pipe run from what I can remember, allowing for bends etc, is around 35m. Additional 410a charged was 500g, as per chart on outdoor unit cover: +500g for 31-40m pipe run.

  6. #6
    Join Date
    Sep 2006
    Location
    italy
    Age
    53
    Posts
    93
    Rep Power
    18

    Re: Daikin E4

    Happy New Year!

    If this phenomena still remain after LP sensor replacement then maybe there is some moisture in the refrigerant system. If LP value drops below 1,5bar then you will get E4 allarm.

    All the best,
    Nicola

  7. #7
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Daikin E4

    i don't think it will be the lp sensor at fault.
    check that the expansion valve is opening and closing ok and check the reading of the indoor coil thermister, as the system is in a low humidity application the indoor coil will not evaporate the refrigerant quick enough causing the exv to close off prematurly to cause this, it could also be a blockage in the filter before the expansion valve or a refrigerant leak.
    Also make sure that the indoor unit is not short cycling as this will cause the exv to close off prematurely.

  8. #8
    Join Date
    Mar 2006
    Location
    Glasgow, Scotland
    Posts
    177
    Rep Power
    19

    Re: Daikin E4

    Quote Originally Posted by brunstar View Post
    i don't think it will be the lp sensor at fault.
    check that the expansion valve is opening and closing ok and check the reading of the indoor coil thermister, as the system is in a low humidity application the indoor coil will not evaporate the refrigerant quick enough causing the exv to close off prematurly to cause this, it could also be a blockage in the filter before the expansion valve or a refrigerant leak.
    Also make sure that the indoor unit is not short cycling as this will cause the exv to close off prematurely.
    Even if this system is installed within a low humidity area you would be able to adjust the EDP setting as this unit is desgined for use in computer rooms etc.

  9. #9
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Talking Re: Daikin E4

    Quote Originally Posted by puddleboy3 View Post
    Even if this system is installed within a low humidity area you would be able to adjust the EDP setting as this unit is desgined for use in computer rooms etc.
    EDP true true yes i just assumed that this was already set but you should never assume..

  10. #10
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Re: Daikin E4

    Fitted the new low pressure sensor on monday, cleared the E4 and everything has been back to normal.
    In the end i decided to reclaim the lot to change the sensor, I dont think I would of have to but wasn't 100% sure of the fitting it was like a T piece inside the brass nut?? and this would also rule out any signs of a leak. Reclaimed 3.3kgs which was exact charge.
    Another point aswell I recovered from the suction shut off valve schreader, when my gauges got to zero I'd only got around 2kg in the bottle. Then I remember reading a thread on here about someone getting nitro trapped on an RZQS condenser, so i put gauges onto the suction port pass the eev and there was gas stuck inside. Powered up the outdoor which obviously opens the eev and reclaimed the remaining 410!
    Passed nitro through every schreader to double check was ok and there were no signs of a blockage, so in this case was definately a faulty sensor!

  11. #11
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daikin E4

    Thanks for the update, glad that you've got it sorted.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Daikin, Why do we bother?
    By gwilliamson in forum Air Conditioning
    Replies: 21
    Last Post: 02-02-2010, 09:38 AM
  3. daikin controllers
    By declan simmonds in forum Air Conditioning
    Replies: 25
    Last Post: 10-07-2009, 10:54 PM
  4. Daikin Comp and inverter
    By WCC73 in forum Air Conditioning
    Replies: 5
    Last Post: 08-11-2008, 08:44 PM
  5. Getting a price from Daikin....
    By monkey spanners in forum Chit Chat & Service Stories
    Replies: 4
    Last Post: 17-08-2008, 09:46 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •