    Check this!!



    Ok guys, what is your first taughts when you see this picture. Insulation you see behind was covering that bulb and pipe section. Bulb is of TXV !



    And another angle:
    Last edited by nike123; 29-12-2008 at 10:25 PM.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Check this!!

    Well, I suppose it stops any metal to metal vibration and wear.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Check this!!

    Please tell me , did it ever run?
    I see it with my own eyes but can't believe it!
    Just when did the expansion valve control any thing? Must be undercharged or the valve is blocked.
    Otherwise it surely would suffer from liquid carryover?

    Do you know where the install was Nike?
    Grizzly

  4. #4
    Join Date
    Apr 2008
    Location
    west wyalong
    Age
    60
    Posts
    7
    Rep Power
    0

    Re: Check this!!

    I would say some cowboy has done this,The bulb would of originally been in contact with the pipework and both the bulb and pipe wrapped in the insulation you see on the bottom of the pipe.the cable tie and flex around the bulb are not factory fitted

  5. #5
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    985
    Rep Power
    19

    Re: Check this!!

    just when you thought it was safe to take a look
    Paul


    "KEEP IT COOL"

  6. #6
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,847
    Rep Power
    21

    Re: Check this!!

    .

    Is that a suction slop pot (accumilator) that the thing is clamped to.

    It would appear that the bulb is in a rubber case and then the armaflex must have covered it?
    If the armaflex covered it completly I spose some thermal conductivity would take place and
    any liquid carry over would be dealt with in the slop pot?

    Class job!!!!

    Cheers taz

    .

  7. #7
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Check this!!

    Someone went to a lot of trouble to braze copper pipe half-section to the suction line for the bulb, then insulated the bulb from the copper. Amazing, what some folks will do.

    I suppose since the accumulator always filled up with liquid, they cranked the TXV adjusting stem closed to prevent that from happening.
    If all else fails, ask for help.


  8. #8
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,855
    Rep Power
    20

    Re: Check this!!

    This is what happens when an engineer tells someone who doesn't know what they are doing to "insulate the bulb"

  9. #9
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Check this!!

    These were my taught also, but since day of install (10 years ago) I was responsible for this unit.
    I taught that somebody was there and that customer don't telling me that fact.
    Then I went to other identical unit near by, opened her and found same thing.
    It is factory fitted at that way.
    This is Fujitu ABY36RGA3W and it seems that that black thing is some heat conductive rubber.

    Taz was right here!

  10. #10
    Join Date
    Oct 2007
    Location
    NZ
    Posts
    85
    Rep Power
    17

    Re: Check this!!

    maybe its a form of thermal damping to slow down the valve action , maybe to stop it snaping shut and sending the compressor out on lp

  11. #11
    Join Date
    Jul 2007
    Location
    Czech
    Age
    61
    Posts
    373
    Rep Power
    18

    Re: Check this!!

    Nike, great job, working 10 years
    Write to us, the reason for the assembly, you suspect that you have shown us the real reason.

  12. #12
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Check this!!

    Quote Originally Posted by WINJA View Post
    maybe its a form of thermal damping to slow down the valve action , maybe to stop it snaping shut and sending the compressor out on lp
    Could be, but there is no LP (or HP) switch.
    Also, cooling cycle is controlled by capillary tube. TEV is only for heating cycle.

  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Check this!!

    Quote Originally Posted by josef View Post
    Nike, great job, working 10 years
    Write to us, the reason for the assembly, you suspect that you have shown us the real reason.
    I was simply checking if unit works as it should be when I spot this and I was stumped.
    Owner complained that unit doesn't heat when outdoor is below 0°C.
    I checked capacity at 5°C outdoor and it was as stated at technical manual.
    Space, what it heats, is too large and made of glass walls and sheet roof (addition to solid building, bar) and when it is cold enough outdoor temperature, indoor temperature is also low (below 10°C), unit goes constantly to cold air blowing prevention mode. Therefore, owner thinks that unit doesn't work as it should be, even he agree that space conditions (insulation) is not favorable.
    He have identical one in basement (100m2), and that one heat perfectly even when outdoor is -7°C, therefore he thinks that this one is faulty.
    Originally, when unit is fitted space was about 40m2 and now is more than 70m2.

  14. #14
    Join Date
    Jul 2008
    Location
    Belgium
    Age
    56
    Posts
    6
    Rep Power
    0

    Re: Check this!!

    protection against freezing ?

  15. #15
    Join Date
    Aug 2006
    Location
    Spencer ma.
    Age
    60
    Posts
    108
    Rep Power
    18

    Re: Check this!!

    I had a customer who has 15 slit ac units w/ Tandem compressors the in house guy hung ALL the txv in the return air stream
    I was there to do 4 tandems I found it when I saw a 44 deg t/d I told the customer that I had TO CHANG THEM all.
    they said no they work great for 10 yr the way the are fun fun fun
    so I just change the ones I did 22 deg t/d

Similar Threads

  1. Installation of NRVS check valves
    By Josip in forum NH3
    Replies: 10
    Last Post: 02-12-2008, 02:33 PM
  2. Replies: 3
    Last Post: 17-07-2008, 01:42 AM
  3. Air conditioning maintenance procedure
    By Andy T in forum Air Conditioning
    Replies: 12
    Last Post: 27-05-2006, 06:57 PM
  4. Double check needed
    By Latte in forum Trouble Shooting
    Replies: 14
    Last Post: 11-08-2004, 12:46 PM
  5. Compressor Check for locked rotor voltage
    By shogun7 in forum Trouble Shooting
    Replies: 0
    Last Post: 04-04-2004, 12:44 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •