    Ok guys, what is your first taughts when you see this picture. Insulation you see behind was covering that bulb and pipe section. Bulb is of TXV !
    And another angle:
    11,025
    Re: Check this!!
    Well, I suppose it stops any metal to metal vibration and wear.
    4,712
    Re: Check this!!
    Please tell me , did it ever run?
    I see it with my own eyes but can't believe it!
    Just when did the expansion valve control any thing? Must be undercharged or the valve is blocked.
    Otherwise it surely would suffer from liquid carryover?
    Do you know where the install was Nike?
    Apr 2008
    west wyalong
    7
    Re: Check this!!
    I would say some cowboy has done this,The bulb would of originally been in contact with the pipework and both the bulb and pipe wrapped in the insulation you see on the bottom of the pipe.the cable tie and flex around the bulb are not factory fitted
    Apr 2006
    stafford
    42
    974
    Re: Check this!!
    just when you thought it was safe to take a look
    Paul
    "KEEP IT COOL"
    Oct 2006
    1,843
    Re: Check this!!
    Is that a suction slop pot (accumilator) that the thing is clamped to.
    It would appear that the bulb is in a rubber case and then the armaflex must have covered it?
    If the armaflex covered it completly I spose some thermal conductivity would take place and
    any liquid carry over would be dealt with in the slop pot?
    Class job!!!!
    Cheers taz
    Aug 2005
    5,302
    Re: Check this!!
    Someone went to a lot of trouble to braze copper pipe half-section to the suction line for the bulb, then insulated the bulb from the copper. Amazing, what some folks will do.
    I suppose since the accumulator always filled up with liquid, they cranked the TXV adjusting stem closed to prevent that from happening.
    Jul 2007
    Australia
    1,845
    Re: Check this!!
    This is what happens when an engineer tells someone who doesn't know what they are doing to "insulate the bulb"
    Split Croatia
    6,151
    Re: Check this!!
    These were my taught also, but since day of install (10 years ago) I was responsible for this unit.
    I taught that somebody was there and that customer don't telling me that fact.
    Then I went to other identical unit near by, opened her and found same thing.
    It is factory fitted at that way.
    This is Fujitu ABY36RGA3W and it seems that that black thing is some heat conductive rubber.
    Taz was right here!
    NZ
    85
    Re: Check this!!
    maybe its a form of thermal damping to slow down the valve action , maybe to stop it snaping shut and sending the compressor out on lp
    Jul 2007
    Czech
    61
    374
    Re: Check this!!
    Nike, great job, working 10 years
    Write to us, the reason for the assembly, you suspect that you have shown us the real reason.
    Split Croatia
    6,151
    Re: Check this!!
    Quote Originally Posted by WINJA View Post
    Could be, but there is no LP (or HP) switch.
    Also, cooling cycle is controlled by capillary tube. TEV is only for heating cycle.
    Split Croatia
    6,151
    Re: Check this!!
    Quote Originally Posted by josef View Post
    I was simply checking if unit works as it should be when I spot this and I was stumped.
    Owner complained that unit doesn't heat when outdoor is below 0°C.
    I checked capacity at 5°C outdoor and it was as stated at technical manual.
    Space, what it heats, is too large and made of glass walls and sheet roof (addition to solid building, bar) and when it is cold enough outdoor temperature, indoor temperature is also low (below 10°C), unit goes constantly to cold air blowing prevention mode. Therefore, owner thinks that unit doesn't work as it should be, even he agree that space conditions (insulation) is not favorable.
    He have identical one in basement (100m2), and that one heat perfectly even when outdoor is -7°C, therefore he thinks that this one is faulty.
    Originally, when unit is fitted space was about 40m2 and now is more than 70m2.
    Jul 2008
    Re: Check this!!
    protection against freezing ?
    Spencer ma.
    108
    Re: Check this!!
    I had a customer who has 15 slit ac units w/ Tandem compressors the in house guy hung ALL the txv in the return air stream
    I was there to do 4 tandems I found it when I saw a 44 deg t/d I told the customer that I had TO CHANG THEM all.
    they said no they work great for 10 yr the way the are fun fun fun
    so I just change the ones I did 22 deg t/d
  1. Installation of NRVS check valves
    By Josip in forum NH3
    Last Post: 02-12-2008, 01:33 PM
  2. Replies: 3
    Last Post: 17-07-2008, 01:42 AM
  3. Air conditioning maintenance procedure
    By Andy T in forum Air Conditioning
    Last Post: 27-05-2006, 06:57 PM
  4. Double check needed
    By Latte in forum Trouble Shooting
    Last Post: 11-08-2004, 12:46 PM
  5. Compressor Check for locked rotor voltage
    By shogun7 in forum Trouble Shooting
    Last Post: 04-04-2004, 12:44 AM