    Question Air conditioner tripping on low oil pressure.



    Hi,
    The air conditioner having 20 hp semi hermatic compressor, trips on low oil pressure some time.The temperature of the cold room is to be maintain around 6 degree centigrade ,and the atmosheric temperatur of the (Winter)vary from -2 to -15 degree centigrade.
    Seeking help.
    Thanks,
    g.karsandas



  2. #2
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Air conditioner tripping on low oil pressure.

    Quote Originally Posted by g.karsandas View Post
    Hi,
    The air conditioner having 20 hp semi hermatic compressor, trips on low oil pressure some time.The temperature of the cold room is to be maintain around 6 degree centigrade ,and the atmosheric temperatur of the (Winter)vary from -2 to -15 degree centigrade.
    Seeking help.
    Thanks,
    g.karsandas
    Hello g.karsandas


    6 deg c seems low for A/C normally without defrosting.

    Would the unit be freezing up then carrying liquid back to the compressor causing it to go out on oil.

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  3. #3
    Join Date
    Apr 2002
    Location
    Canada
    Age
    66
    Posts
    16
    Rep Power
    0

    Re: Air conditioner tripping on low oil pressure.

    HI Andy,
    You can say it is a cold storage.It does have a defrost,it operate once in 24 hours.The defrost timer is kept for 1/2 an hour.
    Thanks,
    Gkarsandas

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Air conditioner tripping on low oil pressure.

    Is the compressor in a warm room or is it sitting in the cold air?

    Without crankcase heaters on it, you might see the same problem... The oil is diluted by liquid refrigerant in the crankcase. Even thought the refrigerant is liquid the oil pump will not generate sufficient pressure to keep the oil safety switch closed.
    If all else fails, ask for help.


  5. #5
    Join Date
    Apr 2002
    Location
    Canada
    Age
    66
    Posts
    16
    Rep Power
    0

    Question Re: Air conditioner tripping on low oil pressure.

    Quote Originally Posted by US Iceman View Post
    Is the compressor in a warm room or is it sitting in the cold air?

    Without crankcase heaters on it, you might see the same problem... The oil is diluted by liquid refrigerant in the crankcase. Even thought the refrigerant is liquid the oil pump will not generate sufficient pressure to keep the oil safety switch closed.
    Hi Iceman,
    The condensing unit is on roof top.The unit is having crank case heater.Defrost timer is set for half an hour, and once in 24 hrs.It runs good but some time it trips.
    Thanks,
    g.karsandas

  6. #6
    Join Date
    Apr 2008
    Location
    phillippines
    Posts
    125
    Rep Power
    17

    Re: Air conditioner tripping on low oil pressure.

    g.karsandas,

    what brand is that low pressure control?

    regards,
    abet

  7. #7
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Air conditioner tripping on low oil pressure.

    Quote Originally Posted by g.karsandas View Post
    Hi Iceman,
    The condensing unit is on roof top.The unit is having crank case heater.Defrost timer is set for half an hour, and once in 24 hrs.It runs good but some time it trips.
    Thanks,
    g.karsandas
    Does the switch trip sometime in the defrost cycle?

    Does the unit have a pump down solenoid valve?
    If all else fails, ask for help.


  8. #8
    Join Date
    Apr 2002
    Location
    Canada
    Age
    66
    Posts
    16
    Rep Power
    0

    Re: Air conditioner tripping on low oil pressure.

    Quote Originally Posted by US Iceman View Post
    Does the switch trip sometime in the defrost cycle?

    Does the unit have a pump down solenoid valve?
    Hi US Iceman,
    I dont have idea as defrost timer is kept at midnigh.
    Yes unit have punp down solenoid.
    g.karsandas

  9. #9
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: Air conditioner tripping on low oil pressure.

    Quote Originally Posted by g.karsandas View Post
    Hi,
    The air conditioner having 20 hp semi hermatic compressor, trips on low oil pressure some time.The temperature of the cold room is to be maintain around 6 degree centigrade ,and the atmosheric temperatur of the (Winter)vary from -2 to -15 degree centigrade.
    Seeking help.
    Thanks,
    g.karsandas
    HI Just a thought what controls the head pressure in low ambient temperatures

    Norm
    My wife used to say you never listen to a word I say at least I think that what she said

  10. #10
    Join Date
    Oct 2007
    Location
    NZ
    Posts
    85
    Rep Power
    17

    Re: Air conditioner tripping on low oil pressure.

    Is the oil preasure safety wired last in the control circuit?
    Ie thermistor then hp/lp switch then oil preasure switch

  11. #11
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Air conditioner tripping on low oil pressure.

    Quote Originally Posted by g.karsandas View Post
    Hi US Iceman,
    I dont have idea as defrost timer is kept at midnigh.
    Yes unit have punp down solenoid.
    g.karsandas
    Hello g.karsandas

    probably a good idea to move the defrost to during the day to see if the trip is before, during or after the defrost. This would also let you see if the defrost is fully clearing the frost and ice.

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  12. #12
    Join Date
    Aug 2006
    Location
    Spencer ma.
    Age
    60
    Posts
    108
    Rep Power
    18

    Re: Air conditioner tripping on low oil pressure.

    Air conditioner tripping on low oil pressure now are you shore its triping on oil or is the compressor trying to start but gose off on overload and the o.p.s. times out. I had this some time back. or is the o.p.s. one of these setronic where the serscer sits in the oil they need to be remved and cleaned.

  13. #13
    Join Date
    Apr 2002
    Location
    Canada
    Age
    66
    Posts
    16
    Rep Power
    0

    Red face Re: Air conditioner tripping on low oil pressure.

    Quote Originally Posted by Andy View Post
    Hello g.karsandas

    probably a good idea to move the defrost to during the day to see if the trip is before, during or after the defrost. This would also let you see if the defrost is fully clearing the frost and ice.

    Kind Regards Andy
    Hi Andy,
    It seems to be tripping by night.
    I am going to change the defrost timing during day time.
    Thanks,
    g.karsandas

  14. #14
    Join Date
    Jan 2009
    Location
    Queensland
    Age
    64
    Posts
    113
    Rep Power
    16

    Re: Air conditioner tripping on low oil pressure.

    gedday k.G, is this a new system that's had the oil problem since it was installed or is it an old system that has run fine till recently?
    Do you have some sort of head pressure control on it?
    What's your operating head, suction and oil pressure?
    What type of compressor are we looking at?
    What's the temperature of the suction line at the compressor?
    If you can answer all these questions it may make it easier to work out what is causing your problem.
    Cheers,
    Slatts

  15. #15
    Join Date
    Jan 2009
    Location
    Queensland
    Age
    64
    Posts
    113
    Rep Power
    16

    Re: Air conditioner tripping on low oil pressure.

    Almost forgot, What refrigerant is in the system?
    What type of compressor is it?

  16. #16
    Join Date
    Apr 2002
    Location
    Canada
    Age
    66
    Posts
    16
    Rep Power
    0

    Question Re: Air conditioner tripping on low oil pressure.

    Quote Originally Posted by Slatts View Post
    Almost forgot, What refrigerant is in the system?
    What type of compressor is it?
    Hi,
    It is Copland semi hermetic,with R 22 refrigerant.
    Thanks,
    g.karsandas

  17. #17
    Join Date
    Jan 2009
    Location
    Queensland
    Age
    64
    Posts
    113
    Rep Power
    16

    Re: Air conditioner tripping on low oil pressure.

    Quote Originally Posted by g.karsandas View Post
    Hi,
    It is Copland semi hermetic,with R 22 refrigerant.
    Thanks,
    g.karsandas
    Thanks g.k but what about the rest of the info I asked about in the previous post?
    Did moving the defrost to day time make any difference?

  18. #18
    markdenford's Avatar
    markdenford Guest

    Re: Air conditioner tripping on low oil pressure.

    sounds to me like the system is not getting enough defrost, if the room is to maintain +6c (chiller) it should have 6 defrost in a 24hr period! i take it oil level is ok/filter ok? has system got oil seperator on it?

  19. #19
    Join Date
    Jan 2009
    Location
    Canada
    Posts
    8
    Rep Power
    0

    Re: Air conditioner tripping on low oil pressure.

    I ran into this type problem on a freezer that had a condensing unit on the roof, discovered a faulty OFS (Johnson Contrls) last in cct to the comp contactor.

    had to Re&Re it....
    The OFS first took a pounding from controlling 208V cicuit, but what I noticed is that when the unit got close to satisfying some liquid would make it back past the Accumulator and washout the oil going through the oil pump. the OFS then would trip out after a 90 second time out.

    I ended up checking the superheat to the comp and noticed that it was to low @ around 5º, I increased it to 18º by (patiently) adjusting the TXV. the system works fantastic now....

  20. #20
    Join Date
    Jan 2009
    Location
    Queensland
    Age
    64
    Posts
    113
    Rep Power
    16

    Re: Air conditioner tripping on low oil pressure.

    Quote Originally Posted by markdenford View Post
    sounds to me like the system is not getting enough defrost, if the room is to maintain +6c (chiller) it should have 6 defrost in a 24hr period! i take it oil level is ok/filter ok? has system got oil seperator on it?
    Gedday Mark. The number of defrosts per day is related to the duty of the room (how heavily the room is used eg; the number of times the door is opened), ambient conditions (Temperature and humidity),type of stock in the room and coil TD.
    On a little used room, full of cans of drink installed in a dry, air conditioned room, you may well get away with 1 defrost per day.
    Horses for courses mate.

    Quote Originally Posted by Enthalpy Eng View Post
    I ran into this type problem on a freezer that had a condensing unit on the roof, discovered a faulty OFS (Johnson Contrls) last in cct to the comp contactor.

    had to Re&Re it....
    The OFS first took a pounding from controlling 208V cicuit, but what I noticed is that when the unit got close to satisfying some liquid would make it back past the Accumulator and washout the oil going through the oil pump. the OFS then would trip out after a 90 second time out.

    I ended up checking the superheat to the comp and noticed that it was to low @ around 5º, I increased it to 18º by (patiently) adjusting the TXV. the system works fantastic now....
    Enthalpy, I take it you haven't been doing this long?
    Sounds like the oil safety was just doing what it was supposed to do.
    You need to check the SH at the evaporator.
    Set it up at 4 to 6K at the TX valve bulb then check your SH at the compressor.
    Since the system has a suction accumulator you should have heaps of SH at the suction service valve once the TX valve is set up properly.
    If you just shut the valve down to get some SH at the compressor you could still be either flooding the coil and suction line, there by increasing the suction pressure and wasting capacity or you could end up starving the evaporator and loose capacity that way.

    Either way we seem to have misplaced the OP.

  21. #21
    Join Date
    Jan 2009
    Location
    Canada
    Posts
    8
    Rep Power
    0

    Re: Air conditioner tripping on low oil pressure.

    Enthalpy, I take it you haven't been doing this long?
    Sounds like the oil safety was just doing what it was supposed to do.
    You need to check the SH at the evaporator.
    Set it up at 4 to 6K at the TX valve bulb then check your SH at the compressor.
    Since the system has a suction accumulator you should have heaps of SH at the suction service valve once the TX valve is set up properly.
    If you just shut the valve down to get some SH at the compressor you could still be either flooding the coil and suction line, there by increasing the suction pressure and wasting capacity or you could end up starving the evaporator and loose capacity that way.

    Either way we seem to have misplaced the OP.[/QUOTE]

    nope in my case the OFS was faulty........

  22. #22
    Join Date
    Jan 2009
    Location
    Queensland
    Age
    64
    Posts
    113
    Rep Power
    16

    Re: Air conditioner tripping on low oil pressure.

    Quote Originally Posted by Enthalpy Eng View Post
    nope in my case the OFS was faulty........
    Fair enough. Did you check the superheat at the evap, or just at the compressor?

Similar Threads

  1. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  2. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM
  3. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •