    Hitachi Inverter compatibility



    Can anyone help? I have been given a brand new RAC 60NH4 Outside unit (24 000 BTU) and RAK 50NH5 Indoor Unit (17 000 BTU). Can they be used together, given the mismatch in capacity.

    The refrigerant pipes on the outside unit are 6,3mm & 12,7mm, whereas the indoor unit is 6,3mm and 9,5mm, so I would need to use a reducer to connect them.

    Thanks,



  2. #2
    Join Date
    Aug 2008
    Location
    Bulgaria
    Age
    39
    Posts
    28
    Rep Power
    0

    Re: Hitachi Inverter compatibility

    I don't thik that's good idea, but you can try. Electric should be matched. If you do this, it's better to keep indoor fan in med. or high.
    Why you don't try to change any of units, to be 100% sure?

  3. #3
    Join Date
    Oct 2008
    Location
    Australia
    Posts
    210
    Rep Power
    16

    Re: Hitachi Inverter compatibility

    it wont work.

    On heating it will keep tripping out on High Pressure

  4. #4
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: Hitachi Inverter compatibility

    Quote Originally Posted by rude View Post
    it wont work.

    On heating it will keep tripping out on High Pressure

    Not a fan of Hitachis by any means but two things spring to mind.

    1 The few I've done have dip switches for different indoor units
    2 Will the inverter not stop it from tripping by slowing down when it starts to ramp near its hp set point?

    Just asking

    Multisync
    London

  5. #5
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: Hitachi Inverter compatibility

    I'm not an expert at any of this but........you do see it the other way around quite often where there is a high sensible heat load. Bigger indoor unit than outdoor unit.

    Seems to work fine, why not the other way around??

    Eggs

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: Hitachi Inverter compatibility

    With a Daikin split, the outdoor will handshake the indoor pcb but if a different capacity setting is read then an error will be generated.
    This is why you must fit a new capacity resistor to the indoor board when you change the pcb. The capacity is set via software in the factory during production but must be set manually on a board change.

    I doubt any mis-matched indoor / outdoor combinations would work, no matter what the make, due to the software programming.

  7. #7
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: Hitachi Inverter compatibility

    Quote Originally Posted by frank View Post
    With a Daikin split, the outdoor will handshake the indoor pcb but if a different capacity setting is read then an error will be generated.
    This is why you must fit a new capacity resistor to the indoor board when you change the pcb. The capacity is set via software in the factory during production but must be set manually on a board change.

    I doubt any mis-matched indoor / outdoor combinations would work, no matter what the make, due to the software programming.
    I'm sure your more well up on this kind of thing Frank, but i can assure you i have installed at least 20 Mitsi Elec, 5hp cassettes to 4hp outdoor units into laboratories in the last 12 months.

    They all work fine.

    eggs

  8. #8
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,451
    Rep Power
    41

    Re: Hitachi Inverter compatibility

    these are the domestic hitachi range, not dip switchable as far as i know, also they appear to be different generations, NH4 and YH5.

    The YH5 supports a hard wired remote that the YH4 doesn't.

    these things are cheap as chips, buy the matching indoor
    although i don't ship that far!!

    Al

  9. #9
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Hitachi Inverter compatibility

    Eggs

    Q are the ME high sensible 4hp outdoor connected to 5hp indoor units type A control R407c / R410a or the older type K control R22 systems.

    Can you advise model numbers ?
    Do ME provide full warrnaty for this non standard combination & high sensible application.

  10. #10
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: Hitachi Inverter compatibility

    Evening Thermatech

    Quote Originally Posted by Thermatech View Post
    Eggs

    Q are the ME high sensible 4hp outdoor connected to 5hp indoor units type A control R407c / R410a or the older type K control R22 systems. Presume type A, as they are on 410a, sorry can't help more as i never spec MEUK for any of our jobs so i don't know much about them. On these jobs we just hang, pipe, wire, suck, blow and go.

    Can you advise model numbers ?I see if i have copies of the commissioning sheets on tomorrow
    Do ME provide full warrnaty for this non standard combination & high sensible application.Pass? we have done them labour only for a specialist Lab contractor
    I'll dig out what info i can tomorrow.

    Cheers

    Eggs

  11. #11
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Hitachi Inverter compatibility

    I know that some Toshiba outdoor inverters are for more than one capacity and, only thing you need to do, is to change some jumper configuration on outdoor PCB to match indoor and outdoor unit.
    Here they are (indoor and outdoor unit) selling them independently, but if you order more than 2-3 unmatched pairs , they immediately suspect that you want to spare some money buying cheaper, lower rated outdoor unit model (and patching it to higher capacity for same lower price) , and doesn't allow that order.

  12. #12
    Join Date
    Nov 2008
    Location
    UK
    Posts
    69
    Rep Power
    16

    Re: Hitachi Inverter compatibility

    Quote Originally Posted by Thermatech View Post
    Eggs

    Do ME provide full warrnaty for this non standard combination & high sensible application.
    Officially, no they don't. You only have to supply the model of the unit the fault is on, so for instance if you need a new indoor pcb the model number of the indoor unit and invoice no. of the original order are all you would have to supply, they then supply the relevent spare. If they're on the ball and look in detail at the original order and see that it contains mismatched units, they can question it but ultimately the only way they can prove the systems on site are mismatched is by going there and taking a look themselves, I don't yet know of any instance that any manufacturer or distributor has gone to these lengths to void a warranty claim unless it's a site with multiple failures.

Similar Threads

  1. Testing Inverters
    By fridge doctor in forum Air Conditioning
    Replies: 38
    Last Post: 15-06-2011, 06:52 AM
  2. Well Done / Thanks Hitachi UK
    By Latte in forum Chit Chat & Service Stories
    Replies: 4
    Last Post: 24-11-2008, 07:52 PM
  3. Difference between AC Inverter & DC Inverter Compressor
    By berrytmy in forum New Technologies
    Replies: 0
    Last Post: 24-04-2008, 11:43 AM
  4. Hitachi Inverter Systems
    By Vishnukurup in forum Air Conditioning
    Replies: 13
    Last Post: 15-11-2007, 01:15 PM
  5. hitachi dc inverter
    By refaircon in forum Air Conditioning
    Replies: 3
    Last Post: 17-06-2007, 11:45 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •