Results 1 to 21 of 21

Hybrid View

  1. #1
    Join Date
    Dec 2007
    Location
    London
    Age
    57
    Posts
    82
    Rep Power
    17

    Re: AHU Calculations

    Quote Originally Posted by Abby Normal View Post
    well meausiring at the diffusers then at the coil will tell you if you have duct losses for one.

    measuring at the coil trells you what the unit is actually doing, measuring at the grilles tells you what the room is receiving.

    When there is a big descrepancy (especially if ducts run in unconditioned space) there is room for big improvements to stop wasting energy


    you move more air through a clean filter than a loaded one

    I think you will be most accurate maesuring the air flow into the returns

    Thank you guys.

  2. #2
    Join Date
    Dec 2007
    Location
    London
    Age
    57
    Posts
    82
    Rep Power
    17

    Re: AHU Calculations

    Started to get the knack of it.Today i took some measurments return air flow,duct size,temp.,RH % and i compared to the other system.One of them was running O'K and comparing to the unhealthy one i can spot the difference.We all learn every day.

Similar Threads

  1. Cooling Load Calculations
    By hamidpia in forum Tools and Calculators
    Replies: 7
    Last Post: 05-02-2009, 08:57 PM
  2. Soap Plant Load Calculations
    By tjk2007 in forum Fundamentals
    Replies: 0
    Last Post: 25-11-2007, 05:59 AM
  3. cold room calculations
    By andyg in forum New to RE
    Replies: 2
    Last Post: 25-07-2007, 05:54 PM
  4. Cold Storage Calculations
    By HAROON in forum Fundamentals
    Replies: 7
    Last Post: 29-03-2007, 10:13 AM
  5. A/C Calculations
    By Latte in forum Air Conditioning
    Replies: 27
    Last Post: 03-09-2006, 08:34 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •