    AHU Calculations



    I have a AHU system and I am trying to establish the system performance. I actually
    Have not got too much experience in AHU.


    i visited some website and downloaded some software .Absolutely superb. Now trouble is that i need to know a bit more in order to be able to use it properly. I bought myself a velocity meter (digital) and it reads RH %
    dry bulb, velocity fpm.I tried it on Rheem system about 14-15 kw.
    I got at some grilles 360 fpm, 30’C supply temp and 44 % RH. In the room the
    set temp is 25 and it reached 23 without a problem and I had a 100 fpm at some other grilles and supply 23’C.Question is How to get more calculations and apply it to the software so i can get a proper results.
    Read somewhere to use a measuring tape which is i presume to measure the duct size and then if i know the area, the system kw,the RH,the dry bulb, wet bulb
    so how can i apply this formulae. I prefer sometimes formulas in order to understand better instead of only software which will do the maths but actually it won't show me how it is done. Also i read somewhere about the formulae calculations about round duct ...Area x r (3.14) x r (3.14)

    one more Q Is there any filters in the systems so i can clean them?



  2. #2
    dyar's Avatar
    dyar Guest

    Re: AHU Calculations

    my name dyar Iwant help any proplem
    dyarmohammed@yahoo.com

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: AHU Calculations

    There certainly should be some filters fitted.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: AHU Calculations

    Quote Originally Posted by SUBCONTRACTOR View Post
    I have a AHU system and I am trying to establish the system performance. I actually
    Have not got too much experience in AHU.


    i visited some website and downloaded some software .Absolutely superb. Now trouble is that i need to know a bit more in order to be able to use it properly. I bought myself a velocity meter (digital) and it reads RH %
    dry bulb, velocity fpm.I tried it on Rheem system about 14-15 kw.
    I got at some grilles 360 fpm, 30’C supply temp and 44 % RH. In the room the
    set temp is 25 and it reached 23 without a problem and I had a 100 fpm at some other grilles and supply 23’C.Question is How to get more calculations and apply it to the software so i can get a proper results.
    Read somewhere to use a measuring tape which is i presume to measure the duct size and then if i know the area, the system kw,the RH,the dry bulb, wet bulb
    so how can i apply this formulae. I prefer sometimes formulas in order to understand better instead of only software which will do the maths but actually it won't show me how it is done. Also i read somewhere about the formulae calculations about round duct ...Area x r (3.14) x r (3.14)

    one more Q Is there any filters in the systems so i can clean them?
    Hi Sub, this might be of used to you.

    http://www.engineeringtoolbox.com/ai...rties-t_8.html

    Norm
    My wife used to say you never listen to a word I say at least I think that what she said

  5. #5
    Join Date
    Dec 2007
    Location
    London
    Age
    57
    Posts
    83
    Rep Power
    17

    Re: AHU Calculations

    Guys thanx for the replies .Once the notorious Bruce Lee said: knowing is not enough ,we must apply

    Hence my questions,i had a lot of software and stuff my simply i have not been involved in AHU before and that's what confuses me a bit and i was thinking to clarify this by applying the knowledge.I got some readings from the grille 200 fpm ,23'C supply,44 % RH
    Question is do i divide the system total kw into the quantity grilles( 15 : 3=5 kw) so i can expect around 5 kw per grille and how to calculate the airflow by measring at the duct size??

  6. #6
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    545
    Rep Power
    18

    Re: AHU Calculations

    if you are measuring velocity at the grilles it can be tricky

    the air comes jetting out a 'vena contracta' or something like that.

    you need to apply a correction factor, one place to get them is from the grille manufacturer

    Some times the correction is refered to as a free area, other times an "Ak" factor

    now if you are maesuring heating, neglecting the humidty levels will not cause much of an error.

    Measuring the tenperature drawn into return grilles as well as the temperature coming out of the supplies can be used to work out how much heat is being supplied to the room.

    What the above method will not tell you though for sure is how much heat the air handler is transfering. My reason for saying this is there could be duct leaks drawing in untreated air if the ducts were in unconditioned sapce, the return ducts could be improperly insulated and losing heat if they were running in a cool attic, or you could have deliberate fresh ventilation air drawn into the return.

    Supply ducts could lose heat as well.

    if you need to know what exactly the ahu is doing then you need to measure the air going into and leaving the coil.

    for cooling with dehumdifiaction it gets a little more involved
    Take the V out of HVAC and you are left with a HAC job

  7. #7
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    545
    Rep Power
    18

    Re: AHU Calculations

    you need to go to your user cp, and click that it is alright for you to receive PMs on this site
    Take the V out of HVAC and you are left with a HAC job

  8. #8
    Join Date
    Dec 2007
    Location
    London
    Age
    57
    Posts
    83
    Rep Power
    17

    Re: AHU Calculations

    So the best results should be air on and air off the coil .Question is why measure the duct in this case ,for me there must ot be some rule of thumb calculations about a duct size
    +air velocity+%RH+friction factor+type of grille which actually restrict the air flow i bit+WB+DB...

    OK' guys what do you do when you clean the filters and you want to know how the system is performing ?
    Last edited by SUBCONTRACTOR; 25-12-2008 at 09:20 AM. Reason: missed a bit

  9. #9
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    545
    Rep Power
    18

    Re: AHU Calculations

    well meausiring at the diffusers then at the coil will tell you if you have duct losses for one.

    measuring at the coil trells you what the unit is actually doing, measuring at the grilles tells you what the room is receiving.

    When there is a big descrepancy (especially if ducts run in unconditioned space) there is room for big improvements to stop wasting energy


    you move more air through a clean filter than a loaded one

    I think you will be most accurate maesuring the air flow into the returns
    Take the V out of HVAC and you are left with a HAC job

  10. #10
    Join Date
    Dec 2007
    Location
    London
    Age
    57
    Posts
    83
    Rep Power
    17

    Re: AHU Calculations

    Quote Originally Posted by Abby Normal View Post
    well meausiring at the diffusers then at the coil will tell you if you have duct losses for one.

    measuring at the coil trells you what the unit is actually doing, measuring at the grilles tells you what the room is receiving.

    When there is a big descrepancy (especially if ducts run in unconditioned space) there is room for big improvements to stop wasting energy


    you move more air through a clean filter than a loaded one

    I think you will be most accurate maesuring the air flow into the returns

    Thank you guys.

  11. #11
    Join Date
    Dec 2007
    Location
    London
    Age
    57
    Posts
    83
    Rep Power
    17

    Re: AHU Calculations

    Started to get the knack of it.Today i took some measurments return air flow,duct size,temp.,RH % and i compared to the other system.One of them was running O'K and comparing to the unhealthy one i can spot the difference.We all learn every day.

  12. #12
    Evap0rat0r's Avatar
    Evap0rat0r Guest

    Re: AHU Calculations

    Formulas:

    Airflow (CFM) = Air Velocity (fpm) * Cross-sectional Area of Opening (ft sq).

    You need to ensure to keep units consistent or account for them using appropriate conversion factors.

    1 ton ref = 12000 btu/hr = 3.516 kW.

    The specs on your unit is typically the nominal capacity as determined by the manufacturer. To determine the theoretical performance of the system given the temp and humidity conditions you mentioned, you would need to do the following:

    Measure the cross-sectional opening of the duct and convert your result to feet squared; multiply this value by your fpm air velocity reading; the product will give you your air flow in CFM.

    You know your room supply temp and the room RH%. You need to find out the entering (outside) air temp and RH%. Now, it gets a bit confusing for a novice: you need to consult your psychrometric chart and plot the state point for the OA conditions and the SA conditions. Get the delta h value between these two state points. Then, apply the formula for total cooling capacity:

    Qtotal = 4.5 X CFM X delta h

    you can convert your answer to kW and then divide this result by the nominal provided by the manufacturer, multiplied by 100, you get the percentage utilization of the system capacity.

    Of course, this is a fairly simplistic view of the processes taking place here, but you asked for some formulas to curb your enthusiam so there you go.

  13. #13
    Join Date
    Dec 2007
    Location
    London
    Age
    57
    Posts
    83
    Rep Power
    17

    Re: AHU Calculations

    Quote Originally Posted by Evap0rat0r View Post
    Formulas:

    Airflow (CFM) = Air Velocity (fpm) * Cross-sectional Area of Opening (ft sq).

    You need to ensure to keep units consistent or account for them using appropriate conversion factors.

    1 ton ref = 12000 btu/hr = 3.516 kW.

    The specs on your unit is typically the nominal capacity as determined by the manufacturer. To determine the theoretical performance of the system given the temp and humidity conditions you mentioned, you would need to do the following:

    Measure the cross-sectional opening of the duct and convert your result to feet squared; multiply this value by your fpm air velocity reading; the product will give you your air flow in CFM.

    You know your room supply temp and the room RH%. You need to find out the entering (outside) air temp and RH%. Now, it gets a bit confusing for a novice: you need to consult your psychrometric chart and plot the state point for the OA conditions and the SA conditions. Get the delta h value between these two state points. Then, apply the formula for total cooling capacity:

    Qtotal = 4.5 X CFM X delta h

    you can convert your answer to kW and then divide this result by the nominal provided by the manufacturer, multiplied by 100, you get the percentage utilization of the system capacity.

    Of course, this is a fairly simplistic view of the processes taking place here, but you asked for some formulas to curb your enthusiam so there you go.
    Brilliant stuff.This is what i am after something straight forward and quick calculations.Actually i use a software to apply the measurments.The folmulaes i need just to understand what is what.Btw can you upload a psycrometric example of what you explained.When i start adding these values i am not 100% sure whether the state point is for the room temp. or outdoor temp. and of course is it room RH% i put or ambient RH%.
    Thanx

  14. #14
    Join Date
    Dec 2007
    Location
    London
    Age
    57
    Posts
    83
    Rep Power
    17

    Re: AHU Calculations

    Downloaded a few ASHRAE books,each one has about 700-800 -900 pages but man it is full of complicated Einstein formulaes and a small engineer with no such a brain like Einstein feels like sh** reading this stuff.

  15. #15
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: AHU Calculations

    That's the fun part of the job that we had to go through at some time
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  16. #16
    Join Date
    Dec 2007
    Location
    London
    Age
    57
    Posts
    83
    Rep Power
    17

    Re: AHU Calculations

    I think the great art of all that is to bring it down to a few useful formulaes and make it practically appliable.Theory is a theory but at the end of the day customer don't care how much you know in theory he wants the job done and the better the application of the knowledge into practice the finer the job will be.

  17. #17
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    545
    Rep Power
    18

    Re: AHU Calculations

    the formulae are simple, the great art is accurately measuring airflow
    Take the V out of HVAC and you are left with a HAC job

  18. #18
    Join Date
    Apr 2009
    Location
    WI USA
    Posts
    27
    Rep Power
    0

    Re: AHU Calculations

    Quote Originally Posted by SUBCONTRACTOR View Post
    So the best results should be air on and air off the coil .Question is why measure the duct in this case ,for me there must ot be some rule of thumb calculations about a duct size
    +air velocity+%RH+friction factor+type of grille which actually restrict the air flow i bit+WB+DB...

    OK' guys what do you do when you clean the filters and you want to know how the system is performing ?
    Here in the USA, we use a manual D for residential duct system design. We size duct system's airflow for the cooling heatload.

    I have a lot of web pages on duct design & proper sizing of duct systems for adequate & efficient delivery of airflow to each room.

    Formula for finding CFM Airflow
    If you can measure the air velocity coming from a duct, here is a rough ballpark formula to get the CFM:
    CFM = (velocity in (FPM) Feet per Minute times the square footage of the duct area, or free-air-area (Ak) of the supply-air diffuser.

    Diffuser Ak .225-sq.ft., X's 650-fpm velocity = 146.25-CFM.

    FIGURING ROOM CFM - DUCT SIZES
    Do a manual J load calc first for each room
    Quick method: The heat gain and Btu/hr of cooling is done for each room.
    At 400-CFM per/ton of cooling, 12,000-BTUH / 400-cfm = 30-BTUH for each (CFM) Cubic Foot per Minute of Airflow.
    At 450-CFM per/ton cooling use 12,000 / 450-cfm = 26.66-BTUH per each CFM, etc.

    Then Select Supply duct size by CFM, velocity, & optimal Supply Air (FR) Friction Rate.

    A Room requires 3000-Btu/hr divided / by 30 equals 100-CFM, or around a 6" dia. RD metal duct.

    You need-> Five duct runs for 1.5-ton unit, 18,000-BTUH: (Equal room loads,ha!) 18000 / 5-runs= 3600-BTUH / 30 = 120-CFM each 6" duct velocity 611-fpm.

    The larger the tonnage system the more supply runs that will be needed to deliver that CFM of airflow at proper velocities with reasonable duct sizes.

    A manual D incorporates the AHU's delivery capability with the engineered duct design. - Darrell

  19. #19
    krishsreekanth's Avatar
    krishsreekanth Guest

    Re: AHU Calculations

    i can mai u with fig of CalcaULATING the Airt Velocity and more of AHU PERFORMANCE CAN U WAIT FOR ONE DAY

  20. #20
    pratheepkumar's Avatar
    pratheepkumar Guest

    Re: AHU Calculations

    how to calculate ahu perfamance?

  21. #21
    Join Date
    Jul 2008
    Location
    philippines
    Posts
    7
    Rep Power
    0

    Re: AHU Calculations

    help me to how to control the operation of re circulating pump? iwe have 6 units of water heater (edwards), 2 units of re ciculating pump.. what devices do i need to install to trigger the pumps to run and off? please help... tnx

Similar Threads

  1. Cooling Load Calculations
    By hamidpia in forum Tools and Calculators
    Replies: 7
    Last Post: 05-02-2009, 09:57 PM
  2. Soap Plant Load Calculations
    By tjk2007 in forum Fundamentals
    Replies: 0
    Last Post: 25-11-2007, 06:59 AM
  3. cold room calculations
    By andyg in forum New to RE
    Replies: 2
    Last Post: 25-07-2007, 05:54 PM
  4. Cold Storage Calculations
    By HAROON in forum Fundamentals
    Replies: 7
    Last Post: 29-03-2007, 10:13 AM
  5. A/C Calculations
    By Latte in forum Air Conditioning
    Replies: 27
    Last Post: 03-09-2006, 08:34 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •