    checkind daikin compressors and inverter board



    Hi i would like some help on how to check if a compressor is faulty and how to check if an inverter is faulty. Any help would be much appreciated



  2. #2
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: checkind daikin compressors and inverter board

    firstly you will want to check the resistance of the compressor with it unplugged from the pcb with the power off. Makke sure there is no earth resistance.
    Once this is ok check the resistance between the 3 windings and make sure that the resistance is equal.
    Test it like a 3 phase compressor.
    This will tell you that the compressor is electrically sound but won't tell you if it is seized.
    As for the inverter board, do a voltage output check from the board. The 3 phase voltage out of the board needs to be equal and balanced within about 5% of each other.
    If your compressor is down to earth replace the compressor and inverter printed circuit board as it will have suffered a high current through it..most likely damaged.

  3. #3
    Join Date
    Jul 2009
    Location
    Berkshire
    Age
    50
    Posts
    175
    Rep Power
    15

    Re: checkind daikin compressors and inverter board

    Quote Originally Posted by brunstar View Post
    Makke sure there is no earth resistance.
    By this I assume you mean there is no continuity to earth? A mega tester is invaluable in checking inverter compressors to earth. A normal continuity meter may not always pick up the smaller values. (I learnt the hard way)

    There are also inverter testers on the market that you can attach to the compressor output leads for a few seconds to confirm good phase balance.
    If at first you DO succeed, try to hide your astonishment!!

  4. #4
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: checkind daikin compressors and inverter board

    yeah it was meant to say make sure your compressor windings do not have earth resistance from the windings to ground.

  5. #5
    Join Date
    Jun 2009
    Location
    East Anglia
    Age
    38
    Posts
    204
    Rep Power
    15

    Re: checkind daikin compressors and inverter board

    Quote Originally Posted by brunstar View Post
    yeah it was meant to say make sure your compressor windings do not have earth resistance from the windings to ground.
    Surely you want infinate resistance between windings and earth?

  6. #6
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: checkind daikin compressors and inverter board

    yes, infinate resistance means that there is no resistance to earth..

  7. #7
    Join Date
    Jun 2009
    Location
    East Anglia
    Age
    38
    Posts
    204
    Rep Power
    15

    Re: checkind daikin compressors and inverter board

    Right, were both thinking the same thing. But if something is infinate then it does exsist, there for there is resistance. To say no resistance makes it sound like there is a fanststic connection between the compressor and earth resulting in no resistance, thus a fault.

  8. #8
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: checkind daikin compressors and inverter board

    yes this is right, it would be a dead short with Zero Impedance.

Similar Threads

  1. Testing DC inverter compressors
    By frankv1@maltane in forum Trouble Shooting
    Replies: 10
    Last Post: 08-06-2010, 11:43 AM
  2. Inverter board Repairs
    By Latte in forum Electrical
    Replies: 2
    Last Post: 24-05-2009, 01:10 PM
  3. Daikin Inverter board failures
    By Greengrocer in forum Air Conditioning
    Replies: 10
    Last Post: 21-05-2009, 04:35 PM
  4. Ammonia compressor's energy saving by inverter
    By torranin in forum Industrial
    Replies: 5
    Last Post: 23-01-2008, 01:00 PM
  5. Replacement Compressors for Inverter A/C
    By Electrocoolman in forum Air Conditioning
    Replies: 2
    Last Post: 30-03-2007, 08:59 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •