    4210 error mitsu



    hi
    tried starting up a vrf system today after fixing a leak.. compressor was giving off a hummming noise, with no sign of pressure change, displayed a 42 10 error after a period of time.....checked voltage to compressor terminalsd and found all evenish, apart from a differentail of 8volts on 1 phase...checked current off each phase..2 x phases had 16amps and 1 phase with the slight differential absorbing nothing....checked windings for ballance etc...all ok, any ideas whats happening????

    rgrds phil (bit pissed writing this since were in a recession in all) thanks



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: 4210 error mitsu

    Quote Originally Posted by philjd26 View Post
    hi
    tried starting up a vrf system today after fixing a leak.. compressor was giving off a hummming noise, with no sign of pressure change, displayed a 42 10 error after a period of time.....checked voltage to compressor terminalsd and found all evenish, apart from a differentail of 8volts on 1 phase...checked current off each phase..2 x phases had 16amps and 1 phase with the slight differential absorbing nothing....checked windings for ballance etc...all ok, any ideas whats happening????

    rgrds phil (bit pissed writing this since were in a recession in all) thanks
    Inverter circuit faulty or compressor one phase fault!
    Check inverter with inverter checker or 3 light bulbs of corresponding power connected in star.
    Check compressor insulation with insulation tester.
    Last edited by nike123; 20-12-2008 at 07:51 PM.

  3. #3
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: 4210 error mitsu

    Could have been compressor warm up function.

    outside air on TH6 sensor is less than about 10 deg C when 3ph power up the outdoor control circuit board considers that the compressor must be cold & crankcase heater not had time to warm up compressor & boil off any liquid refrigerant in the compressor shell.
    So it goes for comp warm up = lots of amps into the windings but no rotation just lots of humming noise.

    4210 = overcurrent.

    After warm up mode check power supply to comp with comp disconnected & confirm correct ballanced 3ph output from inverter.

    If the system has been running SOG then comp could be damaged.

  4. #4
    Join Date
    Feb 2007
    Location
    SIDE OF THE ROAD
    Posts
    262
    Rep Power
    18

    Re: 4210 error mitsu

    thanks for replies, i will take a look in the morning..