    Why multiple 4 way valves on VRF systems



    Something that has always puzzled me on VRV/F is why there are multiple 4 way valves on the inside of the condensor. These can range from being very big to very small. I've seen up to 3 4 way valves inside and i dont know why 3?


    The difference between genius and stupidity is that genius has its limits.

    Marc

  2. #2
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Why multiple 4 way valves on VRF systems

    Alot of 3 pipe VRV / VRF heat recovery systems will have 2 reversing valves.
    Each outdoor unit will have 2 outdoor coils.
    At low load conditions only one is needed & then as load increases the outdoor unit at some point will use both coils.
    For heat recovery mode the outdoor unit can use when nessessary one coil for cooling & one for heating.

    The flow of refrigerant through the outdoor coils is controlled with the 4w reversing valves.
    Cool only mode, heat only mode & heat recovery heating & cooling simultaneously.

    For multiple outdoor units linked together each one will have 2 reversing valves.

    For Mitsubishi City Multi R2 heat recovery there is only one 4w reversing valve to change from heat to cool mode at the outdoor unit.
    But 4 seperate solenoid valves to control refrigerant flow through 4 sections of the outdoor coil + 1 section permanantly open.
    Cool only, cool main, heat main, heat only modes.

    The refrigerant flow diagrams in the service manuals are a bit complicated ( dont tell Gary )
    but if you spend some time you can trace the refrigerant flow through the outdoor unit & system for all the modes.

    When you fully understand the refrigerant flow in heat recovery mode then you see why consultants specify VRV / VRF for energy efficiency.

  3. #3
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Why multiple 4 way valves on VRF systems

    Ah right, that makes a bit more sense now, thanks. Next time i'm at the condensor of one i'll try tracing the pipes as well.
    The difference between genius and stupidity is that genius has its limits.

    Marc

Similar Threads

  1. Co2 Systems in Supermarkets
    By 750 Valve in forum Supermarket Refrigeration
    Replies: 22
    Last Post: 19-10-2007, 08:51 AM
  2. dan foss tx valves
    By fuzzy in forum Trouble Shooting
    Replies: 7
    Last Post: 02-10-2007, 01:11 PM
  3. My local Apprentice Training Classes
    By shogun7 in forum Training
    Replies: 12
    Last Post: 17-03-2007, 03:10 PM
  4. HFCs for flooded systems?
    By garyb in forum Refrigerants
    Replies: 15
    Last Post: 21-04-2006, 10:02 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •