  1. #1
    Graham Eady's Avatar
    Graham Eady Guest

    Help with energy calcs



    I am using an 'air load' calculator which gives me a total cooling load in kBtu for an installation based on the cfm for different locations around the US.
    The figure that I get is the cooling required to bring the air temp down to the required set point but I want to be able to convert this figure to the required electrical load for the whole cooling plant.
    What I am looking for are some 'rules of thumb' for coming up with the calculation.
    The air supply that is being cooled will be provided via an AHU ( air handling unit ) and the systems are 'full fresh air' ( no re-circulated air ) and I assume that it will have a dx coil or a cooling coil operating on chilled water.
    I have looked at packaged chillers on the web and have a good idea of the general power input to cooling load output --

    what I need now is an idea of the efficiency of a cooling coil and the associated pipe work.
    I have a methodology for different heating systems e.g. if we have a gas fired boiler providing low pressure hot water to a coil in an AHU I assume an efficiency of 80% for the boiler and an efficiency of 66% for the heat tranfer to the air ( includes pipe heat losses and heat tranfer in the coil to the air )
    Can I assume a similar 66% for a chilled water circuit through a cooling coil ?

    If we are using a dx coil in the air stream -- what is the efficiency of the cooling ?

    As you have probably guessed, am an electrical engineer not a refridgeration engineer.

    HELP



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Help with energy calcs

    Efficiency of chiller is about 250-300%!

  3. #3
    Graham Eady's Avatar
    Graham Eady Guest

    Re: Help with energy calcs

    Quote Originally Posted by nike123 View Post
    Efficiency of chiller is about 250-300%!
    Thanks for the reply.
    Do you have any figures for the efficiency of the application -- for example the chiller will produce chilled water according to it's efficiency but then this water is passed through a coil in an AHU -- how much is typically lost in the pipework and efficiency of the cooling transfered to the air passing through the AHU -- in other words the 'application efficiency'

  4. #4
    Join Date
    Mar 2008
    Location
    England
    Age
    68
    Posts
    250
    Rep Power
    17

    Re: Help with energy calcs

    For a typical chilled water A/C application you would expect to gain approx. 1c from the chiller to the AHU inlet & another 1c on the way back. So for a chiller leaving water temp of 7c it would arrive at the AHU at 8c + the AHU DT (normally 5c) sub total 13c +1c for the return & back to the chiller at 14c or so.
    Pipe run lengths, insulation, type of coil in AHU and ambient temps will determine actual overall system efficiency. Pumps might also have a small effect.
    A Dx system will be more efficient than a chilled water but harder to control to match fluctuations in fresh air.
    If in doubt read the instructions. If still in doubt follow them.

Similar Threads

  1. Helpful information
    By chemi-cool in forum Tools and Calculators
    Replies: 2
    Last Post: 30-10-2010, 07:00 PM
  2. Energy Conservation
    By US Iceman in forum Technical Speculations
    Replies: 20
    Last Post: 20-07-2010, 10:52 AM
  3. Thermal Efficiency of Refrigeration System
    By hussain316 in forum Refrigeration Books
    Replies: 5
    Last Post: 31-07-2007, 08:59 PM
  4. A question about energy efficiency rating in Europe
    By pcdata76 in forum Fundamentals
    Replies: 1
    Last Post: 22-05-2006, 10:17 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •