    R22 leaking into a boiler



    what would happen??



  2. #2
    Join Date
    Mar 2005
    Location
    u.a.e
    Age
    68
    Posts
    169
    Rep Power
    20

    Re: R22 leaking into a boiler

    You can ask your Doctor if survived, that what happened to me?

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Age
    58
    Posts
    158
    Rep Power
    18

    Re: R22 leaking into a boiler

    A bit more info would help here - be specific.
    Is it R22 vapour entering the air inlet to the combustion chamber?
    Or R22 entering the water supply to the boiler - such as a leaking heat exchanger before the boiler?

    I've seen the effects of R22 entering a boiler thru the air intake, the effects can be somewhat dramatic.
    8 out of the 12 boilers exploded, in each case a flame over 15' (5M) long shot out of the 2' (600mm) square exhaust flue.
    The heat will break the R22 down, it will then react with the water in air and exhaust fumes to produce some very nasty acids and phosgene gas.
    The acids will destry the combustion tube in the boiler, an explosion will shortly follow.

    Shut down the boiler.
    Fix the leak.

    Then get the boiler inspected, before it fails.

    Steve

  4. #4
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: R22 leaking into a boiler

    .



    R22, in common with many chlorinated refrigerants and other types, produce toxic gases during combustion.

    Please read the Safety Data sheets for each type for more detailed info


    If you are responsible for it, you don't want to get caught, but should be.

    If you are in the vicinity - don't inhale it - get away quickly.


    .

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: R22 leaking into a boiler

    Do we assume from the question that you have an R22 system with a pressure relief valve discharging into a boiler room ?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. Old Servel Refrigerator Boiler Temp?
    By Pippo in forum Trouble Shooting
    Replies: 0
    Last Post: 30-10-2008, 03:23 AM
  2. Replies: 2
    Last Post: 12-10-2008, 09:41 AM
  3. Leaking service valve
    By airefresco in forum Air Conditioning
    Replies: 37
    Last Post: 26-09-2008, 11:09 PM
  4. Ducted AirCon Leaking into Ceiling
    By plucka99 in forum Air Conditioning
    Replies: 10
    Last Post: 15-03-2007, 03:22 PM
  5. Leaking X430LS shaft seals
    By reefermadness in forum Transport
    Replies: 14
    Last Post: 02-04-2006, 08:00 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •