    new coolroom and freezer question



    we have recently installed new coolroom and freezer units (evaps and condensing units ) on r404a and have had no success . Coolroom seems to go ok but then coil ices up and Freezer wont go below -10C .I did not actually set up the units and have no ideas any help, units are supposed to be correct size for rooms



  2. #2
    Join Date
    Jul 2008
    Location
    taguig city
    Posts
    36
    Rep Power
    0

    Re: new coolroom and freezer question

    Icemakerman,
    Welcome to RE
    Will ask the following.

    1.insulation thickness?
    2.kind of defrost?
    3.does the system has pumpdown cycle?
    4.size of coldroom
    5..capacity ratings?

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: new coolroom and freezer question

    In order to evaluate selection of your refrigeration system we need also this data.

    Conditions of air in surrounding and placemant conditions
    Amount, loading frequency and type of processed goods
    Make and model # of condensers and evaporators
    Make and model# of TEV
    Make and model of control panel or controller
    Last edited by nike123; 12-12-2008 at 04:45 PM.

  4. #4
    Join Date
    Jul 2007
    Location
    LIbya
    Age
    58
    Posts
    72
    Rep Power
    17

    Re: new coolroom and freezer question

    Dear Icemakerman.
    I agree with Nike because all these information are necessary to solve the problem specially the type of the metering device and the controller in order to analyze and understand the reasons for the unit bad operation.
    Best regard.

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: new coolroom and freezer question

    Is this the first cold room / freezer that you or your firm has installed?

    Is it any different from any others that you have installed?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Mar 2008
    Location
    Melbourne, Australia
    Age
    40
    Posts
    48
    Rep Power
    0

    Re: new coolroom and freezer question

    -Who did your engineering of the systems?

    -Have the systems been commissioned properly and all the control settings set properly?

  7. #7
    Join Date
    Dec 2008
    Location
    Australia
    Age
    61
    Posts
    44
    Rep Power
    0

    Re: new coolroom and freezer question

    thanks for all the questions guys......turns out the installers drilled a hole in the freezer coil and had it on vacuum after ...thus inducing a lot of moisture, I have replaced driers on both units and evacuated to 250 microns for 2hrs each system...recharged and both systems now acheive temps required(also installed a suction drier to freezer system) i suspect it is possibly the first low temp equipment the other tech has installed, my only concern now is the sight glass indicators still show yellow indicating moisture however i am going to let sleeping dogs lie..... if it aint broke dont fix it.

  8. #8
    Join Date
    Dec 2008
    Location
    Australia
    Age
    61
    Posts
    44
    Rep Power
    0

    Re: new coolroom and freezer question

    Quote Originally Posted by boy View Post
    Icemakerman,
    Welcome to RE
    Will ask the following.

    1.insulation thickness?
    2.kind of defrost?
    3.does the system has pumpdown cycle?
    4.size of coldroom
    5..capacity ratings?
    1. 100mm (4")
    2. Electric timed by carel cellarman controller
    3. yes
    4. small aprox 1.2m x 2.4 x 2.1 h
    5. unit is supposedly rated @ 1.5kw R404a Danfoss tes2 with no1 orifice ....

    was called back on sat night (after 43c ambient) unit was at -7c iced up on top half of evap ... opened valve up 1/4 turn ... ambient has been a lot lower last few days ,system has yet to reach -18 system is only 2 months old (usually work on a/c not much experience in freezers but system is supposedly engineered to correct size) would appreciate any suggestions

  9. #9
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: new coolroom and freezer question

    Quote Originally Posted by icemakerman View Post
    1. 100mm (4")
    2. Electric timed by carel cellarman controller
    3. yes
    4. small aprox 1.2m x 2.4 x 2.1 h
    5. unit is supposedly rated @ 1.5kw R404a Danfoss tes2 with no1 orifice ....

    was called back on sat night (after 43c ambient) unit was at -7c iced up on top half of evap ... opened valve up 1/4 turn ... ambient has been a lot lower last few days ,system has yet to reach -18 system is only 2 months old (usually work on a/c not much experience in freezers but system is supposedly engineered to correct size) would appreciate any suggestions

    Check your filter driers for temperature drop across them. If higher than 2K change it.
    It is probably moisture related problem if we consider history.

Similar Threads

  1. Freezer to coolroom conversion