    Supermarket cold room



    Hi, I have to do an assignment for a cold room inside a conditioned supermarket with an ambient of 20degC.
    I have set my hottest ambient outdoor temp as 32degC for SE England, where the condensing unit will be mounted. I will be chilling 2000kg of beef to 0degC, arriving at 10 degC. I have calculated the heat load for the plant to chill using the 20degC store ambient, for conducton through the insulation, and not the 32degC. However I am now being thrown a curve ball by some people who say I should use the 32degC for my heat load calcs. I have used this 32degC in my condensing calculations allowing for 45degC condensing temp using 134a. I feel that I have calculated correctly, but I may be wrong! I am not using software, but doing it the old skool way.
    Please advise.
    Thanks!
    Marc



  2. #2
    Join Date
    Jul 2008
    Location
    taguig city
    Posts
    36
    Rep Power
    0

    Re: Supermarket cold room

    Burrah boy,

    welcome,and you are on the right track.do it manually just like yhe old school.

    1.application of coldroom.
    2.temperature?

    regards,

  3. #3
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Supermarket cold room

    Quote Originally Posted by Burrah Boy View Post
    Hi, I have to do an assignment for a cold room inside a conditioned supermarket with an ambient of 20degC.

    I have calculated the heat load for the plant to chill using the 20degC store ambient, for conducton through the insulation, and not the 32degC.

    Please advise.
    Thanks!
    Marc
    If you are wrong then I would be too.
    You have done it like I would

    Cheers taz.

  4. #4
    Join Date
    Jul 2008
    Location
    England
    Posts
    9
    Rep Power
    0

    Re: Supermarket cold room

    If the ambient is 20degC then it is 20degC! I would work it out from that because at the end of the day that is the actual temperature and not the standard figure that is set by text books. Plus the unit will probably be over sized after calculations are done for 32degC

Similar Threads

  1. Insulation for Cold Room
    By tjk2007 in forum Fundamentals
    Replies: 25
    Last Post: 19-03-2010, 02:54 AM
  2. Cold room floor
    By Andy AC in forum Commercial
    Replies: 8
    Last Post: 19-02-2009, 04:26 PM
  3. Cold room panels
    By LLCooLJ in forum Commercial
    Replies: 6
    Last Post: 07-04-2008, 04:18 PM
  4. cold room
    By CHILLED4 in forum Trouble Shooting
    Replies: 5
    Last Post: 16-11-2007, 11:44 PM
  5. Installation of cold room
    By Josip in forum Legal-Business-Marketing
    Replies: 12
    Last Post: 12-03-2006, 09:20 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •