    Wink York ycaj Danfoss EKS65 phtq info



    Hi guys, looking for a little help with info on the electronic expansion valve option on the ycaj, namely the Danfoss phtq valve controlled by the Danfoss EKS 65 controller, circa 2001, I am getting flood back on both circuits, and need the info for setting/calibrating the EKS 65 to ensure proper superheat control.
    Does any one know of any regular problems with these valves in this application? or is it the temperature sensors out of whack causing mal adjustment,

    Dont mean to be picky, but I have checked everything else, i.e. the wax filled actuator, orifice cage, transducers, and resistance values for the thermistors, but have no reference data to check the thermistor accuracy?

    Can any one offer advice, or links for the kit, the Danfoss site only gives up to date products unfortunately.



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: York ycaj Danfoss EKS65 phtq info

    Welcome Tom.
    If I remember correctly these can suffer from sensor issues.

    Hopefully the attached pages may be of help.
    I have more loose leaf data somewhere, I will see if I can find it tomorrow.
    Grizzly

  3. #3
    Join Date
    Sep 2008
    Location
    Ireland
    Age
    57
    Posts
    15
    Rep Power
    0

    Re: York ycaj Danfoss EKS65 phtq info

    Many thanks, looks promising... will let you know how I get on. Thanks again, much appreciated.

  4. #4
    janieho's Avatar
    janieho Guest

    Re: York ycaj Danfoss EKS65 phtq info

    Hi Tom

    Do you possibly have a description of signal lights on EKS 65

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: York ycaj Danfoss EKS65 phtq info

    Quote Originally Posted by janieho View Post
    Hi Tom

    Do you possibly have a description of signal lights on EKS 65
    Grizzly here.
    Just in case Tom has yet to see this post.
    On the front of the Controller there are three coloured LED's.

    The Red power LED flashes as power is sent in 24vac pulse trains to the ptc circuit in the Q Actuator.

    The Amber LED is on when the controller is above or below the set point reference.

    The Green LED comes on and the amber goes off when the controller is in the neutral Zone around the set point reference
    A useful tip with these controllers is if either sensor goes open or short circuit or goes out of range.
    The valve will force close!
    This will show up with the Red & Green LED's totally OFF and the AMBER LED ON.

    I hope this helps?
    Grizzly
    Last edited by Grizzly; 10-12-2008 at 08:48 PM.

  6. #6
    janieho's Avatar
    janieho Guest

    Re: York ycaj Danfoss EKS65 phtq info

    Hi Grizzly

    Thanks for the info it was very helpfull

    Janieho

  7. #7
    Join Date
    Sep 2006
    Location
    Ireland
    Posts
    37
    Rep Power
    0

    Re: York ycaj Danfoss EKS65 phtq info

    Tom if you get the danfoss product code off the EKS, call dean&woods in Tallaght. Jacintha can get the Danfoss manual for those, with menus and PSWD.
    I have it on paper (not on soft copy) or I would send it to you.
    good luck

  8. #8
    Join Date
    Sep 2008
    Location
    Ireland
    Age
    57
    Posts
    15
    Rep Power
    0

    Re: York ycaj Danfoss EKS65 phtq info

    Hi Grizzly, Hope you can help with this, YCAJ again GSI, with the programme refrigerant message on it, I assume the back up battery on the realtime clock went flat and thecontrol was off for some time, but the panel wont allow me to enter the value, "22" any clues, I thought this model didnt have any passwords etc...

  9. #9
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: York ycaj Danfoss EKS65 phtq info

    Tom

    i think the password is 2876 or 7396, but if the battery went dead the board may need replacing.

    we previously had this on boards that got wet, micro borad had to be replaced.

    Press program and enter the code, hope this helps.

    PM me if you need local assistance!

    al

  10. #10
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: York ycaj Danfoss EKS65 phtq info

    Quote Originally Posted by tomireland View Post
    Hi Grizzly, Hope you can help with this, YCAJ again GSI, with the programme refrigerant message on it, I assume the back up battery on the realtime clock went flat and thecontrol was off for some time, but the panel wont allow me to enter the value, "22" any clues, I thought this model didnt have any passwords etc...
    All Chillers have Passwords especially The bigger Guys.
    In all fairness Al knows what he is talking about.
    Give him a call,
    He is a good chap!
    Grizzly
    Although i can't help in this instance I have sent some info that might be helpful in the future?
    Cheers Grizzly.

  11. #11
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: York ycaj Danfoss EKS65 phtq info

    Grizz

    You're a star!! some kind soul must of misplaced those manuals!!

    Al

  12. #12
    Join Date
    Sep 2008
    Location
    Ireland
    Age
    57
    Posts
    15
    Rep Power
    0

    Re: York ycaj Danfoss EKS65 phtq info

    thanks guys, very much appreciated. If I can ever return the favour!

  13. #13
    Join Date
    Sep 2008
    Location
    Ireland
    Age
    57
    Posts
    15
    Rep Power
    0

    Re: York ycaj Danfoss EKS65 phtq info

    Thanks Al, very kind of you... much appreciated. If I can ever return the favour, dont suppose you know who misplaced the manuals :-)

  14. #14
    Join Date
    Sep 2006
    Location
    Ireland
    Posts
    37
    Rep Power
    0

    Re: York ycaj Danfoss EKS65 phtq info

    Al is right, hit program 7396 and enter thru it to refrigerant , put in 22.

Similar Threads

  1. Replies: 4
    Last Post: 13-04-2010, 06:06 PM
  2. York info
    By unibar in forum Air Conditioning
    Replies: 5
    Last Post: 02-09-2008, 01:04 AM
  3. Low oil temperature YORK YCAJ 77SU7
    By exxu in forum Commercial
    Replies: 9
    Last Post: 03-04-2008, 02:38 PM
  4. Danfoss PHTQ Valve
    By dallan in forum Industrial
    Replies: 5
    Last Post: 29-07-2006, 11:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •