    york chiller motor rotation error



    hello can anyone help about chiller problem, its about this york maxe chiller that we are to startup.... when the chiller was to be started the error msg motor rotation would come up... weve already used a phase sequencer and checked the sequence... the chiller have a acrel adr3-800H motor protection in the starter.. weve tried to disable the phase sequence protection but the motor rotation still comes out.. even if we bypass QE its still the same... anybody have an idea???? the chiller is a york maxe yr model.. 350tons.



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: york chiller motor rotation error

    Did you checked correct wiring inside of control panel? Do you have all three phases at phase control relay? Did you checked phase imbalance?

  3. #3
    Join Date
    Jun 2008
    Location
    Philippines
    Posts
    16
    Rep Power
    0

    Re: york chiller motor rotation error

    well im just a beginner, actually im just an operator so i have no idea about that phase control relay. but the one who have done the wiring was our technician.. i have downloaded a manual of the said acrel ard3 motor protection, and tried to help our technician solve the problem. there was a p010 setting for the device which is the motor phase protection.. it was set at 8 which we changed to 1. (0 is disable, 1 is enable; but was set to 8) so we tried to set it to 1 and the motor run for about 8 secs, and then there it was again, motor rotation msg. it seems like the motor cant run in delta.. after secs of running in wye it stops and the msg appears in the chiller control panel...

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: york chiller motor rotation error

    Then post link for that manual thru your visitor message!
    Last edited by nike123; 11-12-2008 at 05:04 PM.

  5. #5
    Join Date
    Dec 2008
    Location
    MIDWEST, USA
    Age
    52
    Posts
    22
    Rep Power
    0

    Re: york chiller motor rotation error

    Who is the manufacture of the starter? Is the motor turning the direction that is shown casted on the compressor? What is the message displayed on the control panel of the chiller?
    I seems to me that the starter may not be seeing the motor current properly, then timing out, and not transitioning.

  6. #6
    Join Date
    Aug 2007
    Location
    Germany
    Posts
    36
    Rep Power
    0

    Re: york chiller motor rotation error

    Is the chiller equipped with a unit fitted liquid cooled solid state starter or with an external motor starter?

    regards,
    Entropie

  7. #7
    Join Date
    Jun 2008
    Location
    Philippines
    Posts
    16
    Rep Power
    0

    Re: york chiller motor rotation error

    guys problem was solved already....thanks anyways.. current coils inside the motor starter were interchanged thus showing motor phase error in the chiller screen and yes, not transitioning. There were 2 problems. the other one was that the acrel motor protection in the wye-delta starter or in the mains was not configured thus the manual i downloaded was a very big help. because in the acrel site there was no other downloadable manual except for the chinese manual and what a problem it would be to those who are not able to read chinese...like me

  8. #8
    Join Date
    Dec 2008
    Location
    MIDWEST, USA
    Age
    52
    Posts
    22
    Rep Power
    0

    Re: york chiller motor rotation error

    Quote Originally Posted by cesarnino View Post
    guys problem was solved already....thanks anyways.. current coils inside the motor starter were interchanged thus showing motor phase error in the chiller screen and yes, not transitioning. There were 2 problems. the other one was that the acrel motor protection in the wye-delta starter or in the mains was not configured thus the manual i downloaded was a very big help. because in the acrel site there was no other downloadable manual except for the chinese manual and what a problem it would be to those who are not able to read chinese...like me
    cesarnino, glad to have seen you have solved your ploblems. BTW, was this a new start-up? Just for my information. Thanks.

Similar Threads

  1. York Chiller problems
    By ingherrera in forum Commercial
    Replies: 18
    Last Post: 26-07-2011, 03:10 PM
  2. Clima Roca York Chiller
    By Chinua in forum Air Conditioning
    Replies: 5
    Last Post: 13-04-2011, 07:03 PM
  3. need help on YORK chiller
    By nassersh in forum Commercial
    Replies: 4
    Last Post: 16-12-2008, 01:47 PM
  4. York Screw Chiller How low will it go?????
    By bruceboldy in forum Industrial Compressors
    Replies: 11
    Last Post: 10-08-2007, 10:29 PM
  5. York process chiller repairs
    By Matt in forum Commercial
    Replies: 5
    Last Post: 24-03-2004, 12:07 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •