    Superheat Question



    Hey folks

    I know this has been covered alot but,

    I was on a job today and there were schraeder connections at the evaporator inlet and outlet.

    How accurate would it be to convert the pressure readings at both points for calculating superheat?
    Last edited by cmac; 10-12-2008 at 09:51 PM. Reason: spelling



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Superheat

    You should use port at evaporator outlet.
    On inlet (if port is betwen TEV and distributor you have some pressure loss at distributor and evaporator piping) you have false reading.
    If you have short piping, compressor suction is also acceptable!

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Superheat

    I would not use both the inlet and outlet pressures, only the outlet pressure. If you use both pressures the pressure loss of the evaporator could be picked up as superheat, which could lead you to set the valve improperly.
    If all else fails, ask for help.


  4. #4
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: Superheat

    .


    I agree with Iceman.


    There is no point using the inlet test point for working out the superheat, you'll get all sorts of queer reading due to its closeness to the TXV, or what ever you have in place..

    You can get a very accurate profile of the SH during running if you observe and record the simultaneous pressures and temperatures at the exit point - it's worth doing it over a period of time if you can, because the combination of TXV action, coil efficiency and cooling load is not static.

    However, the pressure point at the inlet is not entirely useless. In combination with pressures taken at the exit point, it can give you a good idea of the evaporator pressure drop, if that is significant, because that can effect the efficiency of the TXV and ultimately your SH setting. It's all closely linked.

    While you are at it, you can also record any significant suction line losses, with pressures taken at the unit. Suction losses are often overlooked.

    One point that occurs to me is the issue of Schraeder valves in such a location on the evaporator that is constantly exposed to low temperature and probably frost. They are notoriously prone to leaking and it's very easy to get moisture in the system by attaching gauges to a wet connection.



    .
    Last edited by Argus; 11-12-2008 at 11:11 AM.

  5. #5
    Join Date
    May 2008
    Location
    ireland
    Age
    42
    Posts
    43
    Rep Power
    0

    Re: Superheat

    Okay thanks.
    Was just wondering what the schraeder at the inlet would be used for, as they were factory fitted and I had never seen on other units before

  6. #6
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Superheat

    Hi Cmac

    The inlet could be used to charge liquid to the system?

    al

  7. #7
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: Superheat

    Quote Originally Posted by cmac View Post
    Okay thanks.
    Was just wondering what the schraeder at the inlet would be used for, as they were factory fitted and I had never seen on other units before

    Yes. It's unusual to see a gauge point in that spot. It's also unusual to see one on the exit, but they are useful for setting the TXV, you normally have to get the pressures at the suction service valve and make allowances for the suction line pressure losses.



    Quote Originally Posted by al View Post
    Hi Cmac

    The inlet could be used to charge liquid to the system?

    al

    You can do that at the liquid line service valve.



    .
    Last edited by Argus; 12-12-2008 at 09:41 AM.

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Superheat

    Quote Originally Posted by Argus View Post
    It's also unusual to see one on the exit, but they are useful for setting the TXV, you normally have to get the pressures at the suction service valve and make allowances for the suction line pressure losses.
    It is not unusual in multiple evaporator/TXV systems.

  9. #9
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Superheat

    It's used to measure the pressure drop across the evaporator and diagnose clog.

  10. #10
    Join Date
    May 2008
    Location
    ireland
    Age
    42
    Posts
    43
    Rep Power
    0

    Re: Superheat

    Quote Originally Posted by NoNickName View Post
    It's used to measure the pressure drop across the evaporator and diagnose clog.
    Ok what would the expected pressure drop be if everything was working correctly. It was on a water chiller running on R407C

  11. #11
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Superheat

    I have no idea. You shall ask the evaporator manufacturer. It very much depends on the inner geometry, which is unknown to me.

  12. #12
    Join Date
    Dec 2008
    Location
    Australia
    Age
    61
    Posts
    44
    Rep Power
    0

    Re: Superheat

    [quote=Argus;128599]Yes. It's unusual to see a gauge point in that spot. It's also unusual to see one on the exit, but they are useful for setting the TXV, you normally have to get the pressures at the suction service valve and make allowances for the suction line pressure losses.


    I recently had system with subcooler (heat exchanger at outlet of evaporator) on 404a the increase on suction pressure from evap to compressor was 60KPa (aprox. 9PSI) found charge port at evap outlet was only way to set superheat

  13. #13
    Join Date
    Dec 2008
    Location
    China
    Posts
    87
    Rep Power
    16

    Re: Superheat Question

    Quote Originally Posted by cmac View Post
    Hey folks

    I know this has been covered alot but,

    I was on a job today and there were schraeder connections at the evaporator inlet and outlet.

    How accurate would it be to convert the pressure readings at both points for calculating superheat?
    __________

    schraeder? What's that?

  14. #14
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Superheat Question

    Quote Originally Posted by wilsoncheung View Post
    __________

    schraeder? What's that?
    Access needle valve for connection of gauge manifolds etc.

  15. #15
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Superheat

    Yo Nike123,

    was this an easy or dumb question ???

    (lol)
    Ice

  16. #16
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Superheat

    Quote Originally Posted by icecube51 View Post
    Yo Nike123,

    was this an easy or dumb question ???

    (lol)
    Ice
    Easy one! I would also need to add one of signatures which have Google in it self!

  17. #17
    Join Date
    Jan 2009
    Location
    Australia
    Age
    60
    Posts
    108
    Rep Power
    16

    Re: Superheat

    Taking the pressure reading at the compressor can give you a false reading as pressure drop in the suction line distorts the actual value of the evaporator temperature and therefore the superheat.

    Superheat really needs to be calculated at the evaporator outlet because this is where we are measuring the condition of the superheated vapour. Any other point in the system is subject to pressure differences and delivers distorted results.

  18. #18
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Superheat

    Quote Originally Posted by Scramjetman View Post
    Taking the pressure reading at the compressor can give you a false reading as pressure drop in the suction line distorts the actual value of the evaporator temperature and therefore the superheat.

    Superheat really needs to be calculated at the evaporator outlet because this is where we are measuring the condition of the superheated vapour. Any other point in the system is subject to pressure differences and delivers distorted results.
    Pressure drop from evaporator to compressor could be accurately calculated.

  19. #19
    gitster a/c's Avatar
    gitster a/c Guest

    Re: Superheat

    Normally the extra screider is on to charge up R407c on evaps to allow some evaporation of the liquid . Best usage if weighing in correct charge but if using superheat if could affect the temp at the bulb and shut down tev and show full sightglass you then go away and it settles down and is short of gas. also it can be used for pressure drop . its mainly found in my experience on close control dx.

    Gitster

  20. #20
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: Superheat

    Quote Originally Posted by gitster a/c View Post
    Normally the extra screider is on to charge up R407c on evaps to allow some evaporation of the liquid . Best usage if weighing in correct charge but if using superheat if could affect the temp at the bulb and shut down tev and show full sightglass you then go away and it settles down and is short of gas. also it can be used for pressure drop . its mainly found in my experience on close control dx.

    Gitster


    What?



    .

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Carrier 23xl chiller-Low discharge superheat alarms
    By Bradysmill in forum Trouble Shooting
    Replies: 7
    Last Post: 25-04-2010, 07:43 PM
  3. TEV superheat setting and low temperatures
    By DaBit in forum Fundamentals
    Replies: 11
    Last Post: 01-03-2010, 02:11 AM
  4. Replies: 12
    Last Post: 14-07-2008, 03:00 PM
  5. Superheat
    By shogun7 in forum Fundamentals
    Replies: 24
    Last Post: 23-08-2004, 05:54 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •