10-12-2008, 12:05 PM #1
out door walkin freezer
i am new to this site and decided to give a try for one of my units i am having trouble with what i have is an overcharge i think but i want to check subcooling to verify charge in unit problem is the unit has a fan cycle switch the ambient temp out side is 20 f. can i bypass the fan cycle to allow for a constant air flow allowing me to check the a accurate subcooling reading or is there a better way of checking for an overcharge in a freezer in a low ambient temp.
-
11-12-2008, 05:23 AM #2
Re: out door walkin freezer
Why do you think it's overcharged? does it have a receiver and sight glass?
-
11-12-2008, 05:38 AM #3
Re: out door walkin freezer
If it is outside, and you bypass the fan control to give constant air flow, you will over cool the condensor, which will give it the appearance of being undercharged.
You are running this unit in winter conditions...do you have a headmaster on it? I am thinking that when it gets really cold, even with a fan control you will over condense this unit, unless you also have a head master. But if you have a head master, you dont need to cycle the fan.
More info is needed.
-
11-12-2008, 11:53 AM #4
Re: out door walkin freezer
thanks for the reply's i have got it all figured out i knew it was over charged because i had one of my new guys watching the scale while i finished up with the contractor when i came back out in stead of shutting the gauges off at 8 lbs of gas he just let it suck the refrigerant in and when i looked at the scale it said 17lbs double the charge of what was need i knew i had to pull the gas out but i didnt know with the winter temps out side if i could still get a subcooling value when bypassing the fan it would make some sense but i would also had to bolck the air flow across the condenser to get a higher condensing temp right or should i justs go off of superheat in the winter.
-
11-12-2008, 11:15 PM #5
-
12-12-2008, 01:01 AM #6
Re: out door walkin freezer
Seriously....this site has got some good stuff, but this just sounds like a wind up. If you know that the system takes 8lbs and your offsider put in 17lbs...well let me think....mmmmmmmmmmm....maybe take out 9lbs.....and I'm breathing, slowly in, slowly out....
-
16-12-2008, 01:50 AM #7
-
16-12-2008, 10:54 PM #8
Re: out door walkin freezer
I'm assuming this is a TXV system?
Without bypassing or blocking, add refrigerant until the superheat is right. At this point there is sufficient refrigerant for current conditions. This is the minimum charge (although this may not be enough for colder conditions).
Next, block off the condenser until the head pressure simulates summer temperatures.
Now add refrigerant until the subcooling is about 15F/8.5C. This is the maximum charge (although this could be too much for warm weather operation if the receiver is undersized).
Anywhere in between will do the job.
-
17-12-2008, 12:35 AM #9
Re: out door walkin freezer
Somebodies got a short fuse........I do most humbly apologize for offending thee........
Gary, you have the patience of a saint and I like your posts.
Similar Threads
-
ice cream truck freezer
By GaryC in forum TransportReplies: 7Last Post: 06-12-2008, 02:19 AM -
Hotpoint FFA71 Freezer High Temp Light / Fridge is Freezing
By sumnerpa in forum Trouble ShootingReplies: 1Last Post: 19-08-2008, 03:16 PM -
Freezer compressor running 20 Hours/day
By rickcw in forum DomesticReplies: 12Last Post: 08-03-2008, 11:50 PM -
Trolley freezer & blast freezer
By smpsmp45 in forum NH3Replies: 0Last Post: 25-08-2007, 07:29 AM -
Project needs a freezer box.
By NC-Joey in forum FundamentalsReplies: 14Last Post: 16-08-2007, 01:27 PM