    How to eliminate the Ice frost in a freezer



    After some years in operations ,a freezer has huge amount of ice frost all around.
    Some water as vapor form got in side

    The freezer is working at -25ºC. It storage ice cream in plastic containers.

    The question is How can one get rid the frost out without stop the freezer?
    Thanks for your ideas
    Regards
    Gwapa



  2. #2
    Join Date
    Dec 2008
    Location
    MIDWEST, USA
    Age
    52
    Posts
    22
    Rep Power
    0

    Re: How to eliminate the Ice frost in a freezer

    gwapa,

    What kind of freezer are you talking about? Is it a upright, chest, walkin?

  3. #3
    Join Date
    Jul 2008
    Location
    taguig city
    Posts
    36
    Rep Power
    0

    Re: How to eliminate the Ice frost in a freezer

    gwapa,

    do you mean removing ice build up even though equipment is running?

    regards,

  4. #4
    Join Date
    Sep 2006
    Location
    Venezuela
    Posts
    259
    Rep Power
    18

    Re: How to eliminate the Ice frost in a freezer

    it is a freezer 30 x 60 x 12 m
    It has two additional cold room(vestibule). One at the product entry where it is paletaizerred (stack on pallet) .The other one is in the poduct outlet where a group of worker makes the picking and load the trailer
    Both vestubule are at -18ºC

    Boy ,yes I mean removing ice build up even though equipment is running and prouct are inside
    Thanks

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: How to eliminate the Ice frost in a freezer

    gwapa,

    If you can reduce the moisture infiltration into the freezer, then the frost build-up will sublimate on it's own.

    I know that sounds simple to do, but more difficult to provide. If the vestibules are conditioned at -18°C, are the areas adjacent to the vestibules also conditioned at say 4.5°C?

    The higher temperatures with evaporators will remove a lot of water in a liquid state by condensation. Then if a part of the remaining water is picked up by the evaporators in the -18°C vestibules (as frost), you have less water available in the freezer to accumulate frost.

    One of the other issues with this is... Any moisture flowing into the freezer will form as frost wherever the moisture comes into contact with a surface temperature below the dew point of the moisture. That can be wall, racks, or products. If the moisture is not entrained in the air as it flows to the evaporators, the moisture will stick to the cold surfaces before it enters the coils. I see this a lot of times.

    Where the air infiltration comes into the freezer I like to have the evaporator fans blowing at these openings so that the cold air picks up the moisture instead of the walls, racks, or products.

    The only other way I know of reducing the moisture is to use something like this: http://www.hcrdoors.com/

    Hope that is useful...
    If all else fails, ask for help.


  6. #6
    Join Date
    Sep 2006
    Location
    Venezuela
    Posts
    259
    Rep Power
    18

    Re: How to eliminate the Ice frost in a freezer

    Hi US Iceman

    Are the areas adjacent to the vestibules also conditioned at say 4.5°C? No the areas adjacent are at ambient conditions . The adjacents area are production rooms and you can find a lot of water on floor due to continuos washing.The temperature is 24-26ºC

    I agree with your statemens. however if I could reduce the water vapor entries to the freezer I think the evaporators will take to much time to eliminate the frost . It is due to the fact that the Relative Humidity in the freezer is to high .More than 95%

    The HCR courtines reduce the entries of humidity to the Freezer I am not sure if those could eliminate the frost once formed.





  7. #7
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: How to eliminate the Ice frost in a freezer

    Quote Originally Posted by gwapa
    The HCR courtines reduce the entries of humidity to the Freezer I am not sure if those could eliminate the frost once formed.


    They can help to reduce the moisture flowing into the freezer so that the frost already there can sublimate. the air curtain of the HCR door has heat added to increase the moisture holding ability of the air. The cold air of the freezer stays behind this curtain.

    I've seen several of these curtains/doors and it is amazing to see and feel the difference. Walking though the door; one step and you are warm and another step and you are cold. They really seem to work...

    I believe they have some information on their site somewhere about this.

    see this... http://www.hcrdoors.com/hcraction/problem1.htm

    If all else fails, ask for help.


Similar Threads

  1. Hotpoint FFA71 Freezer High Temp Light / Fridge is Freezing
    By sumnerpa in forum Trouble Shooting
    Replies: 1
    Last Post: 19-08-2008, 03:16 PM
  2. Freezer compressor running 20 Hours/day
    By rickcw in forum Domestic
    Replies: 12
    Last Post: 08-03-2008, 11:50 PM
  3. Zanussi Frost Free Fridge Freezer
    By john123 in forum Domestic
    Replies: 2
    Last Post: 31-12-2007, 06:53 AM
  4. Need help quick with walk-in freezer issues!
    By hysiderafter in forum Commercial
    Replies: 5
    Last Post: 12-12-2007, 12:57 AM
  5. Trolley freezer & blast freezer
    By smpsmp45 in forum NH3
    Replies: 0
    Last Post: 25-08-2007, 07:29 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •