    Do i need to pump down???



    Hi all

    i am making a system to de-humidify air.
    The system consists of cond unit, evap, internal equalized tev, drier, sight glass, hot gas bypass valve to maintain close control on suction temperature.
    The system has a duty of around 900watts running on R404a maintain a evap temperature of 0deg C.
    Pipe runs are very short (only about 1mtr)

    Do i need to fit a llsv for pump down when the humidity has reached it's set point??? and the comp cycle's off??

    If i don't use pump down will the evap fill with liquid emptying the condenser/reciever, threatening the comp on re start.

    CB



  2. #2
    Join Date
    Oct 2007
    Location
    NZ
    Posts
    85
    Rep Power
    17

    Re: Do i need to pump down???

    you make get bad floodback on start up so a pump down system with llsv would be ideal , you could put an accumulator on but depending if a cch is fitted it may be a pointless as it wont over come the crankcase filling with liquid during extended off cycles anyway

  3. #3
    sunil4seasons's Avatar
    sunil4seasons Guest

    Re: Do i need to pump down???

    A crank case heater will help your compressor to have a smooth restart when u start ur system after longtime

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Do i need to pump down???

    Also, compare the quantity of refrigerant that your system will contain with the maximum charge that the compressor was designed for.

    If you are below that amount then things should be OK but include a CCH anyway.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Do i need to pump down???

    ChillyB,
    if you are concerded about short pipe runs and floodback install LLSV and cycle it with compressor, not necessarily a pump down cycle.
    magoo

  6. #6
    Join Date
    Nov 2006
    Location
    Arizona
    Age
    48
    Posts
    47
    Rep Power
    0

    Re: Do i need to pump down???

    Quote Originally Posted by Brian_UK View Post
    Also, compare the quantity of refrigerant that your system will contain with the maximum charge that the compressor was designed for.
    Can you elaborate on this statement? Maybe I'm losing something in the translation. I know of total system charge or receiver/ condenser charge but not compressor charge. Are you maybe talking about compressor CFH or CFM?

Similar Threads

  1. liquid ammonia pump calvitation
    By Kathleen in forum Trouble Shooting
    Replies: 23
    Last Post: 20-05-2011, 02:18 AM
  2. Replies: 14
    Last Post: 27-08-2008, 08:57 PM
  3. Troubleshooting a vacuum pump and gauge set.
    By Old Codger in forum Fundamentals
    Replies: 7
    Last Post: 08-08-2008, 05:13 PM
  4. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  5. SL/SB-400 Pump Down Procedures
    By absolute-zero in forum Transport
    Replies: 1
    Last Post: 29-01-2008, 09:27 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •