    Need Help on Design/sizing of Mixing Tank - Industrial Cooling



    Need Help on Design/sizing of Mixing Tank - Industrial Cooling
    Need Help on Design/sizing of Mixing Tank.
    I have a process (Dairy) cooling application where the Chiller Side Supply water is 60 GPM (Temp in 5 Deg C & Return water to Chiller 14 Deg C) and Process Side (3 Nos Plate Heat Exchangers @ total Flow rate of 5 GPM ) Supply water to process is 5 Deg C & Return Water from Process Plate Heat Exch 50 Deg C.
    We have been recommended a Mixing tank of 2000 Gallons.
    Can someone suggest me how to partition the tank for the Hot Well & Cold Well and the locations of the inlet & outlet pipes.

    I would appreciate a detailed suggestion as I have no experience in such a installation.



  2. #2
    Join Date
    Aug 2008
    Location
    Englewood, CO
    Posts
    23
    Rep Power
    0

    Re: Need Help on Design/sizing of Mixing Tank - Industrial Cooling

    Oren:

    The first thing I notice is you don't have a heat balance. Flow rate x Delta T has to be equal for both the chiller and the process.

    Also, your flow rates are starkly different. The flow rate for the chiller should exceed the flow rate for the process by only a marginal amount.

    2,000 gallons sounds like a lot to me.

    I don't know the optimum tank partition location but clearly the cold side will predominate.

    This sounds like a very common application. There should be plenty of 'rules of thumb' in the dairy industry that will get you to the right place.

    Don

  3. #3
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24

    Re: Need Help on Design/sizing of Mixing Tank - Industrial Cooling

    Quote Originally Posted by oren View Post
    Need Help on Design/sizing of Mixing Tank - Industrial Cooling
    Process Plate Heat Exch 50 Deg C.

    I would appreciate a detailed suggestion as I have no experience in such a installation.
    Hello oren

    I have some experience of the dairy industry. Why 50 deg c return

    This sounds like a temperature off a pasturiser WITHOUT the use of regenerative plates in the pasturiser.

    It is normal that the cold milk coming into the pasturiser cools the warm milk leaving the pasturiser, leaving the return to the chiller only about 4 to 6k warmer than the flow from the chiller.

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

Similar Threads

  1. How an expansion tank works?
    By Raadster in forum Fundamentals
    Replies: 6
    Last Post: 25-07-2008, 02:25 PM
  2. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  3. A/C not putting out enough cooling, gauges not happy
    By Larry2 in forum Air Conditioning
    Replies: 13
    Last Post: 13-11-2006, 09:32 PM
  4. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Fundamentals
    Replies: 0
    Last Post: 13-10-2005, 05:14 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •