Results 1 to 6 of 6
Thread: a project cascade syetem
-
08-12-2008, 07:33 AM #1
a project cascade syetem
i has a project :
1:-7 deg c EVAPOTATE TEMPRATURE, cooling capacity :60KW
2:-45 DEG C EVAPOTATE TEMPRATURE, cooling capacity:30KW
3:-70 DEG C EVAPOTATE TEMPRATURE, cooling capacity :10kw
how can i deal with it ,would you give me some advice?
-
08-12-2008, 11:07 PM #2
Re: a project cascade syetem
Contact someone who can design a system for you.
They will also be able to provide a price for the finished items.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
08-06-2009, 03:35 PM #3
Re: a project cascade syetem
You can use a two stage cascade system. Also use R404 A in high stage and R23 in low stage.
Best regards
Mayank Jindal
-
17-07-2009, 11:48 AM #4
Re: a project cascade syetem
i think you can use R404A for 1st stage and R508B for 2nd stage it's working until -86C
-
20-07-2009, 12:16 PM #5
Re: a project cascade syetem
I CAN SUGGEST SUITABLE COMPRESSORS FOR THE CASCADE YOU ARE LOOKING FORWARD TO WITH R-404A & R-23 REFRIGERANTS . HOWVER THE SYSTEM BUILDING YOU WILL NEED TO ORGANIZE YOURSELF . HOWEVER NOT CLEAR YOUR REQUM ; AS I UNDERSTAND IT
>>>>>>>>>>>>>>>>>>>>>>>>>>>>
-70 DEG C EVAP ............ 10 KW
THIS INFO IS SUFFICIENT TO DO COMPRESSOR SELECTION , EXCEPT YOU WILL HAVE INDICATE THE HIGH SIDE CONDENSING TEMPERATURE ON THIS APPLICATION .
BASED ON YOUR CONDENSING TEMP AN INTERMEDIATE PRESSURE CAN BE WORKED OUT & IT WILL BE SUFFICIENT TO ARRIVE AT SUITABLE SELECTIONS . HENCE SEND THE HIGH SIDE COND TEMP
>>>>>>>>>>>>>>>>>>>>>
I DO NOT KNOW WHY OTHER PARAMETERS AT -45 DEG C & -7 DEG C ARE GIVEN.
FURTHER DISC ON BY PM : ddk0123@gmail.com
-
24-07-2009, 01:54 PM #6
Re: a project cascade syetem
just for information, if 2nd stage evaporator -70 c. you should setting you 1st stage evaporator until -42c cause if 2nd stage cycle your evaporator warm until -36 c, this same like my project.and i using danfoss compressor GS.
Similar Threads
-
R-23 cascade system
By S.M.Gokhale in forum IndustrialReplies: 22Last Post: 08-08-2009, 08:04 AM -
Building a 3 stage cascade
By NoL in forum CPU OverclockersReplies: 9Last Post: 27-03-2009, 08:42 PM -
ORC project
By Agiraias in forum New TechnologiesReplies: 2Last Post: 15-10-2007, 01:25 AM -
ORC project with refrigerants
By Agiraias in forum RefrigerantsReplies: 3Last Post: 13-09-2007, 08:49 AM -
Refrigerant for multi-stage and cascade systems
By lraja in forum RefrigerantsReplies: 0Last Post: 15-01-2007, 01:27 AM