Thread: foster ps 500 lt r404a
05-12-2008, 05:00 PM #1
hi there everyone.. im currently working on a fault with a fosters ps 500lt 404a, both the con and evap fans are working,but the freezer is not freezing,it is staying at 22 oc. my work mate will be pressure testing it monday, for a loss of refrigerate. any ideas what the problem could be,if its not a leak?
thanks mark...
ps.. im a spark who works with a air con engineer..
05-12-2008, 05:15 PM #2
Re: foster ps 500 lt r404a
Comp not pumping/ blockage in fridge circuit, assuming condenser fan is running and condenser is clear, check defrost heaters are not stuck on.
You really should be fitting your manifold set and anylising the system before you do anything.
Let us know how you get on
05-12-2008, 06:06 PM #3
The little bi metallic clicky thing has gone open circuit on the compressor mate, you need a new one.... i am good cc
05-12-2008, 06:23 PM #4
thanks for your help,i will relay that info to my work mate... and will let you know the outcome..
05-12-2008, 06:25 PM #5
I do assume the compressor is running
PP
05-12-2008, 07:34 PM #6
Accidentally mixed R404A with R134a
By toma in forum Trouble ShootingReplies: 1Last Post: 13-08-2008, 03:33 PM -
R507 to R404a
By Andy AC in forum CommercialReplies: 2Last Post: 09-08-2008, 05:36 PM -
R404a
By tjk2007 in forum RefrigerantsReplies: 5Last Post: 20-11-2007, 11:33 PM -
Why not R404a?
By afak in forum Technical SpeculationsReplies: 12Last Post: 02-04-2007, 08:58 PM -
R134a or R404a
By jingua_ph in forum RefrigerantsReplies: 4Last Post: 27-09-2006, 03:31 PM