Results 1 to 38 of 38
Thread: Phase Loss Detection
16-03-2004, 01:11 AM #1
Here's one for all the design guys,
Surely there is something out there so when a unit loses a phase it doesn't blow the trips, just cuts the other two phases and then automaticly restores all 3 once they are all up again.
YES i have just been to a site and had to reset nine seperate condensing units following a power cut to a phase
Raymond
16-03-2004, 08:35 AM #2
Hi ray
What was the cause? phase loss, single phase out of three for example?voltage drop?phase inbalance?phase voltage surge?.
There are phase failure modules available,but they cant protect against every situation and ££££££.
Regards Mark
16-03-2004, 08:46 AM #3
Ray
A contactor starter c/w manual reset overload ,(Hopefully) cuts power to windings etc before irrepairable damage occurs.
If auto reset were fitted on certain pieces of equiptment then this could lead to more problems
Regards Mark
16-03-2004, 03:02 PM #4
hi raymond,
yes, there is such thing!
a phase failure, phase sequence and voltage drop protectio, all in one.
three phses are connected from one side, common, NO and NC contacts on the other side.
if one fase is missing, or, sequence has changed, or, voltage drop below set, relay change position, and alarm goes on. when things go back to normal, it will stop the alarm and restore tention to controls.
hope that helps.
chemi
16-03-2004, 06:46 PM #5
Situation i had last night was a common problem at this store which is located in the High Street in a fairly large town.
For some reason every 5-6 months the 400amp fuse on a phase blows at the local substation. Most other shops are either completly off or on depending which phase supplies them but obviously this supermarket has all three phases going to it.
What this means is the trip/overloads blow to protect the compressors but an engineer has to wait on site until the electricity board restores power to that phase so everything can be reset.
My point was could this be done some other way !!!
Raymond
16-03-2004, 06:55 PM #6
Ray, it could be possible to fit a phase failure monitor that would open a three phase contactor to remove ALL power from the condensers (or whatever plant).
If the condensers are self restarting on power up then it should work.
Obviously some cost involved but shouldn't be horrendous.Brian - Newton Abbot, Devon, UK
16-03-2004, 07:10 PM #7
hi raymond,
the way you describe it, there is not much you can do untill electricity supply comes back.
what i meant was to protect the refrigeration gear, once any phase gone - it stops, when all three phase back in the right order, machines come back to work.
as simple as that.
chemi
17-03-2004, 10:59 AM #8
What about having a fat 3-phase relay with 220V coil, and 3 small relays with 220V coil?
Now, the 3-phase relay switches all three phases. The other three relays must be switched in series, feeding the 3-phase relay coil. Power for the three small relay coils should come from each phase.
Now, if one phase fails, the associated relay opens up, cutting power to the 3-phase relay, switching off all three phases.
I don't think you can do it cheaper or easier than this, but you need the neutral connection too (in addition to L1, L2, L3 and earth), which is not always available.
in a simple ASCII graph:
Code:L1 N L2 N L3 N | | | | | | UUUUUU UUUUUU UUUUUU L1 ---- Relay1 ------- Relay2 -------- Relay3 ------>coil 3ph N ------------------------------------------------->coil 3ph
17-03-2004, 04:30 PM #9
hi dabit.
thats fine but more complicated from the little device that I offer him.
you can get it at any electric supplier.
chemi
17-03-2004, 06:09 PM #10
Ray i hope this is chargeable work Lol
Regards Mark
29-11-2004, 09:27 PM #11
Re: Phase Loss Detection
you can put a phase fault monitor and protector by marrs or whoever makes one, and a delay on break and make, and if you want you can, you can take the break to the units on/off toggle or system off switch, take it to break the signal leg or control voltage leg that calls for cooling and that should end that, period!
29-11-2004, 10:29 PM #12
Originally Posted by frankBrian - Newton Abbot, Devon, UK
23-12-2004, 09:14 PM #13
We use a phase loss monitor on incoming voltage to the control panel. There is also a phase loss monitor on each of the compressors. These monitor the incoming lines to the contactors as well as the outgoing lines to the motors. The monitor phase loss, phase inbalance, and low or high voltage. They are also able to be set for manual or auto reset.
I had the fortunate chance to walk into a room at the right time. A breaker lost a leg on a 100 HP motor and was single phasing. The customer was fortunate it was caught in time and caused no permanent damage to the motor.
Since then I feel the added cost is cheap compared to the replacement of a compressor or motor whichever is the case.
02-01-2005, 09:57 PM #14
A Phase loss detector can be made by using 3 relays , let the main contactor coil current pass by 3 relays in series , than the coil of the first relay will have current from Phase 1 and the second from phase 2 and the 3rd from phase 3 , any phase failure will causes a relay to stop, which brakes the current line of the contactors coil ==> the contactor will return to the normally open position and the compressor motor will be protected , as soon as the failure phase go on again , the contactor will work and the motor compressor will work again .
I advise to put a timer delay relay to protect the compressor from quik ON after an off.Engineering, sciences, math, physics and my brain will generate "not responding " soon
03-01-2005, 06:32 AM #15
In that case is a motor protector much cheaper. According Belgium regulations, a motor protector is even obliged in all 3 phase motor systems.
And if you install a motor protector, you don't have to install a fuse anymore.
So why make it difficult if it can be done easy and reliable.Last edited by Peter_1; 03-01-2005 at 10:42 AM.
03-01-2005, 09:22 AM #16
Peter
Can you please post a picture of a motor phase protector?
Thank You
03-01-2005, 10:47 AM #17
You know what I mean, ity's my bad English again
17-03-2004, 07:27 PM #18
OH YEEH,
It's the contract that has just gone fully comp but i have put chargable in large letters on my jobsheet as i assume this is chargable.
The kind of callout i like (And there isn't many i do). Sit about at a store for a couple of hours, drinking Coffee's waiting for the power to come back on, Can't beat it.
I could have spent the time constructively cleaning cases but then OH Well!!!!
regards
Raymond
17-03-2004, 07:51 PM #19
Inevitably you took a flask full of coffee with you
Lol
17-03-2004, 09:03 PM #20
OH NO
Experience tells us down here that it is always the yellow phase that blows at the substation. The Tea room plugs sockets obviously work off the blue or red because these always work.
All that cuts out at the store are some of the store lights and obviously the compressors.
Raymond
17-03-2004, 09:52 PM #21
No wonder you cant sleep Lol
Too much caffeine
Cant see you being a de-caff man
17-03-2004, 10:06 PM #22
Next time you see my van have a look inside, all the ingredients are in there for the engineer on call.
Empty coffee cups & a packet of Pro-Plus on the dash.
Must not forget the B & H in the door pocket as well
Raymond
17-03-2004, 10:09 PM #23
Some of us dont need chemical motivation
18-03-2004, 07:07 PM #24
Good job there isn't a HEALTH(y) & Safty Forum Raymond, You Wouldn't stand a chance.
18-03-2004, 07:14 PM #25
Just because i am not healthy OR safe doesn't mean i don't know the legalaties of it and how it should be done.
Joking aside, it might be a good idea for a forum or is it coverred in any of the other ones.
regards
Raymond
18-03-2004, 07:34 PM #26
hi raymond,
you might find help here, www.curezone.org.
chemi
18-03-2004, 07:43 PM #27
tried the link Chemi but it said I was not authorised to view it - is this some secret smoking forum you belong to?
18-03-2004, 07:46 PM #28
Sorry Chemi,
Same problem as frank, Not authorise to view.
If its a cure fo smokeing, there is no such thing !!!!!
Raymond
18-03-2004, 07:55 PM #29
what would I do without you,marc?
chemi
18-03-2004, 08:05 PM #30
Thanks for the link Marc however the site did NOT offer any advice about deafness! so I'll carry on pulling my Todger
18-03-2004, 08:28 PM #31
try this one frank,
http://www.defeatingdeafness.org/
chemi
18-03-2004, 08:31 PM #32
Chemi-cool are you sure your not British
(sense of humour)
18-03-2004, 08:33 PM #33
I'm not, my wife is.
chemi
18-03-2004, 08:47 PM #34
Sorry Chemi - what did you say - can't hear you !
23-03-2004, 07:51 AM #35
we always use a phase loss detector on mains lline coming in. Also a low voltage and a preferent trip as i do this on seegoing vessels. If one of these devices alarm the complete installation is stopped immediatly.
After restore the PLC starts up sequentaly.
Single phase contactor
By Andy T in forum CommercialReplies: 9Last Post: 23-10-2006, 01:45 PM -
pressure drop of two phase flow in valves
By Hansss in forum FundamentalsReplies: 2Last Post: 24-06-2006, 05:10 PM -