    cabinet icing up



    hello fello fridgeys,
    i have a self contained critically charged salad bar that i have replaced the condensing unit on and cut out the liquid reciever which is constantly icing up over a period of days. there is a dixell xr20 controller in place set to cut in at 4 and out at 2 (manurfacturers specs) there is no weight on the label and i have charged the system to run at 52psi suction pressure and roughly 270psi head pressure on r404a. the liquid line feels great and there is nice sweat coming back on the suction line. the cabinet easily achieves temp and cycles well but it continues to ice up.
    any advice would be greatly appreciated as i am having night terrors
    cheers



  2. #2
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: cabinet icing up

    Critically charged but had a reciever?
    Critcally charged but you charged to a certain pressure?
    Sorry, none of that makes any sense.

    Is it a self contained unit or remote condenser?
    Is it a cold plate or fan forced?
    What are the controllers defrosting setpoints?
    Did you fit the same type of condensing unit?

  3. #3
    Join Date
    Oct 2005
    Location
    In a 2 bedroom unit. Why's That? :)
    Posts
    314
    Rep Power
    19

    Re: cabinet icing up

    I have never seen an iced up reciever. The sub cooling must be insane.

    An Accumulator will ice up, that's why they have drain trays, burn off trays and/or are insulated.

    Get out your PH chart and do a system check. Check sub cooling and super heat. Air flows over condenser and evap.


    If the reciever is iceing up there is something a miss.

    Isn't there?



    _dogma-

  4. #4
    Join Date
    Mar 2008
    Location
    australia
    Age
    44
    Posts
    10
    Rep Power
    0

    Re: cabinet icing up

    sorry guys i meant the evap coil is constantly icing up

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: cabinet icing up

    You say you replaced the condensing unit.

    What happened to the old one?

    Is the new one an exact replacement?

    Or a little larger?

  6. #6
    Join Date
    Oct 2007
    Location
    Australia
    Age
    49
    Posts
    24
    Rep Power
    0

    Re: cabinet icing up

    Petwa,

    I will begin by interpreting several factors you have stated in a different manner to the other posters, firstly I think what you are saying is that you have replaced a condensing unit ( it would be excellent if you could say why) and have had to cut the receiver out, which was factory fitted, because the existing refrigerant metering device is a capillary tube.
    I am assuming once you have re-commisioned the saled bar, a number of call backs have occurred due to the evaporator icing up 'which is constantly icing up'. There is no way the receiver is icing up while my ass is pointing to the ground.

    Just provide a little more information and I'm sure you will begin to receive some productive advice:
    Old condensing unit type and model....
    NEW condensing unit type and model....
    R.M.D......
    Evaporator type.....
    Controller defrost settings........
    Open salad bar? Deli type?

  7. #7
    Join Date
    Oct 2007
    Location
    Australia
    Age
    49
    Posts
    24
    Rep Power
    0

    Re: cabinet icing up

    Petewa,

    Sorry mate I just read your short post correcting yourself, that the evaporator is icing up, but you still need to provide a bit more information.
    I would like to know if there is any difference between the old and new condensing units, control settings, evap type(finned-natural or forced convection) e.t.c.

  8. #8
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: cabinet icing up

    Pete who manufactures this cabinet?

    As requested previously need to know if you are talking forced/induced draft or natural convection finned coil.

    Silly question but is there a TXV? If there is then why no receiver?

    Where is the Dixell stat measuring its temp from, return air, supply air, cabinet temp, coil temp?

    How many defrosts per day and what duration?

    What temps are you seeing and where are you taking them from?

    Got any pics?

    Whats the superheat and subcooling when case is close to desired temp?

    Cheers
    ...and she said "give it to me you big fridgie"

  9. #9
    Join Date
    Oct 2007
    Location
    Australia
    Age
    49
    Posts
    24
    Rep Power
    0

    Re: cabinet icing up

    You look and sound familiar 750 valve.

  10. #10
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: cabinet icing up

    perhaps... ever worked in pub and club Mobbsy?
    ...and she said "give it to me you big fridgie"

  11. #11
    Join Date
    Oct 2007
    Location
    Australia
    Age
    49
    Posts
    24
    Rep Power
    0

    Re: cabinet icing up

    That I have, the moustache was a dead give away. Your identity is safe with me big fridgie. Sales and service, it just feels like yesterday.

  12. #12
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: cabinet icing up

    Mobbsy my how the years fly - good old sales vs service skirmish, the bongo van from hell (column shift OYB512) and the smell of an old pub's cellar - or the bars for that matter

    BUT....

    Watch out looks can be decieving and if you go by my avatar pic I haven't been up for air since July 2001! Next time I see you at ARBS you better buy me a beer if you can get away from those TAFEies

    Its certainly a small world, I know petwa too (whether he realises it or not I don't know) - who posted the original question too but he seems to have disappeared for a while, maybe it got the better of him
    ...and she said "give it to me you big fridgie"

  13. #13
    Join Date
    Oct 2007
    Location
    Australia
    Age
    49
    Posts
    24
    Rep Power
    0

    Re: cabinet icing up

    The years go by too quickly, and the unique aromas of a cellar never leave you.

    No air since 2001! Well some do say snorkels are handy over a wide range of situations, and you provide a convincing argument supporting this notion.

    I will buy a you beer for sure, but if we see each other before ARBS, I'll be certain to shout you a shandy (middi of course).

  14. #14
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: cabinet icing up

    750 valve
    Your aviator. question ? whose groin are you smothered with, I think I can recognise it.
    magoo

  15. #15
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: cabinet icing up

    Quote Originally Posted by Magoo View Post
    750 valve
    Your aviator. question ? whose groin are you smothered with, I think I can recognise it.
    magoo
    By smell or coiffure? I don't smell anything!

Similar Threads

  1. Freezer cabinet problem
    By klimek in forum Technical Discussions
    Replies: 6
    Last Post: 17-03-2008, 11:28 AM
  2. small display cabinet keeps seizing up CF motors
    By paul_h in forum Commercial
    Replies: 8
    Last Post: 11-11-2007, 01:56 PM
  3. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM
  4. Modifying cabinet temps
    By james in forum Fundamentals
    Replies: 16
    Last Post: 01-05-2002, 08:49 PM
  5. Calculating Cabinet Temperature?
    By mepgkyc in forum Trouble Shooting
    Replies: 0
    Last Post: 18-01-2002, 05:16 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •