    Lennox outdoor unit



    Hi guys ,
    removed cover from outdoor unit ,compressor not running,fan spinning ok,contactor not energised traced wiring, the neutral for the 240v coil is non exsisting it goes through some kind of switch on the suc line................ are these switches valves removable?the unit looks very old are they beyond repair? are spares easy to get ? any help for an old spark ???
    Cheers Frank Mc Bride.



  2. #2
    shogun7's Avatar
    shogun7 Guest
    Frank,
    the sw, on the suction line could be a low pressure cut out to protect the compressor if the system looses it's gas charge. If it's a 3 phase system then from that control you should have a wire to that goes to the compressor motor starter coil and the condenser fan contactor coil (parallel) This is very unuasual it may indicate a bad compressor or out of gas so it was disconnected.
    Roger

  3. #3
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25
    Yes It Probably is a LPCO Switch. We have quite a few of these units still working out this way & they are all S***

    Regards

    Raymond

  4. #4
    Join Date
    Feb 2004
    Location
    scotland
    Age
    62
    Posts
    15
    Rep Power
    0
    Thanks guys,it`s a single phase job,i`ll have another go at it tomorrow if the bloody rain stays off...............

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Lennox outdoor unit

    Originally posted by frankmcbride
    (A) the unit looks very old are they beyond repair?

    (B) are spares easy to get ?
    (A) Yes, chuck it

    (B) Don't waste time on it.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25
    Hello Frank,
    Got to aggree with Brian on this one especially if it's one of them S***ty units that has gas going to the indoor unit for heating.

    Get them to buy a cople of splits, it will work out cheaper in the long run just think of the power these old units consume even before you start taking into account repair costs

    Regards

    Raymond

    P.S. What part of Scotland are you from.

  7. #7
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46
    hi frank,

    every switch that have two wires is a contact switch, HP,LP .

    the HP is usualy has a manual reset but the LP dont, try to "bridge " it ( hope its the right term) so you will know if its that switch.


    if works, dont waste time and and leave it bgidged.

    chemi

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51
    Nottingham

Similar Threads

  1. Lennox fan coil unit question
    By THERMOACC in forum Fundamentals
    Replies: 2
    Last Post: 17-02-2006, 10:31 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •