    York Solid State Starter Fault



    Hi Guys,
    have been dealing with this problem for about 18 months. Have a Model YK, R-134a chiller with Style B Solid State Starter. Every few months the unit shuts down after several hours running with high phase heatsink temp, this is followed by a number of other faults. See attach. for details, note Phase B current, don't think this is correct.
    York Techs don't know, has anyone else had this problem. Is it the temp sensor or is it the whole board.
    Attached Images Attached Images



  2. #2
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: York Solid State Starter Fault

    Hi Bill
    the temp sensor is obviously faulty, and looks like the board too. Do your measurements first on voltage and current at motor - allow about 2%V and 10% current imballance. There could also be some crossed wiring between A B and C. I've seen a board blow when another tech used ground of controller to check the 400V supply (accidentally metre switched to ohms). Use a Fluke to capture any inrush current (if any). Hobo data loggers are also good for trouble shooting this type of problem. Also use an IR thermometer to check for hot spots. Be careful.

  3. #3
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: York Solid State Starter Fault

    Hi Bill,
    Has your starter got internal or external bypass. Normally solid state (soft starts) switch in a bypass contactor when unit reaches end of ramp to prevent heat being generated within unit.
    Perhaps you have a faulty contact on your bypass (could be internal to unit).

  4. #4
    Join Date
    Nov 2008
    Location
    Slovenia
    Posts
    34
    Rep Power
    0

    Re: York Solid State Starter Fault

    Phase B takes more power than the input power is ? 0.o

  5. #5
    Bill at 101's Avatar
    Bill at 101 Guest

    Question Re: York Solid State Starter Fault

    I have had the unit go into alarm again after running for about 4hrs, have included photo of recent alarms, similar but different parameters. Any help will be appreciated,
    Regards .............. Bill
    Attached Images Attached Images

  6. #6
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: York Solid State Starter Fault

    There's nothing wrong with the voltage, but at least in the first image I see a lot of differences between current absorptions on the three phases, and a geniune phase b heatsink alarm on phase B (111°C, presumable setpoint 110°C).
    Is the heatsink clogged by scale?

    Also, why POWER FAULT? Is the mains stable?

  7. #7
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: York Solid State Starter Fault

    Bill
    Maybe the attached will help a little?
    At least I hope it will?
    Grizzly

  8. #8
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: York Solid State Starter Fault

    Hello bill at 101 send me your email and i,ll post you complete manual

  9. #9
    Bill at 101's Avatar
    Bill at 101 Guest

    Re: York Solid State Starter Fault

    Thanks again Guys,
    I have all the complete manuals and this problem is not included anywhere.
    However have spoken with a guy who know an ex-York guru in Sydney and he has pointed us in the direction of the "SSS Communications Error Statistics" page in the diagnostics area. Apparently this counter can only hold 256 bits or errors and when it is full wacky things can happen. So these counters need to be reset to '0' every now and then. In later units York have given this a value of 20,000 or something. Anyway the unit is running fine now with no more faults and I will keep an eye on the counter to see how quick it goes up.
    Regards ............. Bill
    Attached Images Attached Images

  10. #10
    Bill at 101's Avatar
    Bill at 101 Guest

    Re: York Solid State Starter Fault

    Thanks Ghaz,
    as stated have full set of manuals.

    Regards .............Bill
    bburgess@101collins.com.au

  11. #11
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: York Solid State Starter Fault

    Quote Originally Posted by Bill at 101 View Post
    Thanks again Guys,
    I have all the complete manuals and this problem is not included anywhere.
    However have spoken with a guy who know an ex-York guru in Sydney and he has pointed us in the direction of the "SSS Communications Error Statistics" page in the diagnostics area. Apparently this counter can only hold 256 bits or errors and when it is full wacky things can happen. So these counters need to be reset to '0' every now and then. In later units York have given this a value of 20,000 or something. Anyway the unit is running fine now with no more faults and I will keep an eye on the counter to see how quick it goes up.
    Regards ............. Bill
    Good of you to reply Bill.
    Thanks for the info.
    Grizzly

Similar Threads

  1. YORK YAEP recip chiller fault
    By chiller1 in forum Trouble Shooting
    Replies: 8
    Last Post: 04-06-2010, 10:41 AM
  2. Solid State Starter
    By pinto joseph in forum Technical Discussions
    Replies: 4
    Last Post: 04-02-2009, 05:32 PM
  3. Fault with Tango cassette
    By airefresco in forum Air Conditioning
    Replies: 8
    Last Post: 19-09-2007, 08:42 AM
  4. York Water cooled solid state starter?
    By Dave the Fridge in forum Trouble Shooting
    Replies: 6
    Last Post: 27-03-2007, 05:03 PM
  5. solid state relays
    By Temprite in forum Commercial
    Replies: 2
    Last Post: 11-02-2005, 10:17 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •