01-12-2008, 11:58 PM #1
York Solid State Starter Fault
Hi Guys,
have been dealing with this problem for about 18 months. Have a Model YK, R-134a chiller with Style B Solid State Starter. Every few months the unit shuts down after several hours running with high phase heatsink temp, this is followed by a number of other faults. See attach. for details, note Phase B current, don't think this is correct.
York Techs don't know, has anyone else had this problem. Is it the temp sensor or is it the whole board.
-
02-12-2008, 05:27 AM #2
Re: York Solid State Starter Fault
Hi Bill
the temp sensor is obviously faulty, and looks like the board too. Do your measurements first on voltage and current at motor - allow about 2%V and 10% current imballance. There could also be some crossed wiring between A B and C. I've seen a board blow when another tech used ground of controller to check the 400V supply (accidentally metre switched to ohms). Use a Fluke to capture any inrush current (if any). Hobo data loggers are also good for trouble shooting this type of problem. Also use an IR thermometer to check for hot spots. Be careful.
-
02-12-2008, 12:18 PM #3
Re: York Solid State Starter Fault
Hi Bill,
Has your starter got internal or external bypass. Normally solid state (soft starts) switch in a bypass contactor when unit reaches end of ramp to prevent heat being generated within unit.
Perhaps you have a faulty contact on your bypass (could be internal to unit).
-
02-12-2008, 04:56 PM #4
Re: York Solid State Starter Fault
Phase B takes more power than the input power is ? 0.o
-
03-12-2008, 02:47 AM #5
Re: York Solid State Starter Fault
I have had the unit go into alarm again after running for about 4hrs, have included photo of recent alarms, similar but different parameters. Any help will be appreciated,
Regards .............. Bill
-
03-12-2008, 07:43 AM #6
Re: York Solid State Starter Fault
There's nothing wrong with the voltage, but at least in the first image I see a lot of differences between current absorptions on the three phases, and a geniune phase b heatsink alarm on phase B (111°C, presumable setpoint 110°C).
Is the heatsink clogged by scale?
Also, why POWER FAULT? Is the mains stable?
-
03-12-2008, 06:59 PM #7
Re: York Solid State Starter Fault
Bill
Maybe the attached will help a little?
At least I hope it will?
Grizzly
-
03-12-2008, 09:21 PM #8
Re: York Solid State Starter Fault
Hello bill at 101 send me your email and i,ll post you complete manual
-
04-12-2008, 04:07 AM #9
Re: York Solid State Starter Fault
Thanks again Guys,
I have all the complete manuals and this problem is not included anywhere.
However have spoken with a guy who know an ex-York guru in Sydney and he has pointed us in the direction of the "SSS Communications Error Statistics" page in the diagnostics area. Apparently this counter can only hold 256 bits or errors and when it is full wacky things can happen. So these counters need to be reset to '0' every now and then. In later units York have given this a value of 20,000 or something. Anyway the unit is running fine now with no more faults and I will keep an eye on the counter to see how quick it goes up.
Regards ............. Bill
-
04-12-2008, 04:22 AM #10
Re: York Solid State Starter Fault
Thanks Ghaz,
as stated have full set of manuals.
Regards .............Bill
bburgess@101collins.com.au
-
04-12-2008, 06:01 AM #11
Similar Threads
-
YORK YAEP recip chiller fault
By chiller1 in forum Trouble ShootingReplies: 8Last Post: 04-06-2010, 10:41 AM -
Solid State Starter
By pinto joseph in forum Technical DiscussionsReplies: 4Last Post: 04-02-2009, 05:32 PM -
Fault with Tango cassette
By airefresco in forum Air ConditioningReplies: 8Last Post: 19-09-2007, 08:42 AM -
York Water cooled solid state starter?
By Dave the Fridge in forum Trouble ShootingReplies: 6Last Post: 27-03-2007, 05:03 PM -
solid state relays
By Temprite in forum CommercialReplies: 2Last Post: 11-02-2005, 10:17 PM