01-12-2008, 12:39 AM #1
Panasonic wall split inverter problem
REQUIRE FAULT CODE DIAGNOSIS CS-CUE15HKR
CODE H11
UNIT IS ONLY ONE DAY OLDLast edited by Brian_UK; 01-12-2008 at 07:18 PM. Reason: Thread moved to correct section
-
01-12-2008, 04:21 AM #2
Re: Panasonic wall split inverter
Comms error.
See if you have ~20-30v at the indoor unit between the neutral and the signal terminal after reseting the power.
If not, somethings wrong with the wiring or ourdoor unit.
If you have that voltage there, somthing is wrong with the indoor unit.
-
02-12-2008, 02:04 AM #3
Re: Panasonic wall split inverter problem
H11 is the first fault code that pops up when checking fault codes, are you sure it is H11? move up and down using the timer buttons to confirm.
If it is H11, than the indoor unit has not had a reply from the outdoor units for 60 seconds, communications are performed over interconnects 2 and 3.
Check your interconnect for poor connections or shorts
If all connections are good, than measure beteeen them on the DC range, and it should be fluctuating between 20 and 50 V DC
If it is, than it may be a faulty indoor PCB, if it is not, than disconnect number 3 at the outdoor unit, and measure what comes out of the PCB on 3, in reference to number 2,it should be about 20 - 70 Vdc
If this voltage is not there, than the outdoor PCB may be faulty
-
02-12-2008, 05:32 AM #4
Re: Panasonic wall split inverter problem
Good point.
When you get into test mode, the error isn't displayed on the controller, you use the time up and down buttons to scroll through the codes, watching for the code that makes the indoor unit beep multiple times (5?).
It starts the codes at H11, so go scrolling through the m all and back to H11 to confirm it's a H11 fault and not something else.
Similar Threads
-
daikin L0 inverter problem
By robin r33 gtr in forum Air ConditioningReplies: 17Last Post: 11-03-2010, 11:25 PM -
Faulty Fujitsu invertor wall split
By nick_nst@aapt.n in forum Trouble ShootingReplies: 7Last Post: 30-06-2008, 08:04 PM -
Panasonic inverter -Power factor protection
By Blackbird in forum Air ConditioningReplies: 3Last Post: 28-06-2008, 01:17 PM -
panasonic 3 phase split
By mike live in forum Air ConditioningReplies: 18Last Post: 18-08-2006, 11:54 PM