    Panasonic wall split inverter problem



    REQUIRE FAULT CODE DIAGNOSIS CS-CUE15HKR
    CODE H11
    UNIT IS ONLY ONE DAY OLD
    Last edited by Brian_UK; 01-12-2008 at 07:18 PM. Reason: Thread moved to correct section



  2. #2
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Panasonic wall split inverter

    Comms error.
    See if you have ~20-30v at the indoor unit between the neutral and the signal terminal after reseting the power.
    If not, somethings wrong with the wiring or ourdoor unit.
    If you have that voltage there, somthing is wrong with the indoor unit.

  3. #3
    Join Date
    Feb 2008
    Location
    QLD
    Age
    53
    Posts
    74
    Rep Power
    17

    Re: Panasonic wall split inverter problem

    H11 is the first fault code that pops up when checking fault codes, are you sure it is H11? move up and down using the timer buttons to confirm.

    If it is H11, than the indoor unit has not had a reply from the outdoor units for 60 seconds, communications are performed over interconnects 2 and 3.

    Check your interconnect for poor connections or shorts

    If all connections are good, than measure beteeen them on the DC range, and it should be fluctuating between 20 and 50 V DC

    If it is, than it may be a faulty indoor PCB, if it is not, than disconnect number 3 at the outdoor unit, and measure what comes out of the PCB on 3, in reference to number 2,it should be about 20 - 70 Vdc
    If this voltage is not there, than the outdoor PCB may be faulty

  4. #4
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Panasonic wall split inverter problem

    Good point.
    When you get into test mode, the error isn't displayed on the controller, you use the time up and down buttons to scroll through the codes, watching for the code that makes the indoor unit beep multiple times (5?).
    It starts the codes at H11, so go scrolling through the m all and back to H11 to confirm it's a H11 fault and not something else.

Similar Threads

  1. daikin L0 inverter problem
    By robin r33 gtr in forum Air Conditioning
    Replies: 17
    Last Post: 11-03-2010, 11:25 PM
  2. Faulty Fujitsu invertor wall split
    By nick_nst@aapt.n in forum Trouble Shooting
    Replies: 7
    Last Post: 30-06-2008, 08:04 PM
  3. Panasonic inverter -Power factor protection
    By Blackbird in forum Air Conditioning
    Replies: 3
    Last Post: 28-06-2008, 01:17 PM
  4. panasonic 3 phase split
    By mike live in forum Air Conditioning
    Replies: 18
    Last Post: 18-08-2006, 11:54 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •