    need help on YORK chiller



    YORK chiller model YCAS0373 with 2 number DXS screw compressors.
    The problem i have with one of the compressors is that it hunts while on load - i.e the suction pressure oscillates between 70 psi and 75 psi. Its not stable though its fully loaded with the sliding valve on step 75 indicating fully open and loaded. We never had any problem with it before, it all started after we carried out comprehansive service on it. The service included change of oil, change of core filters, vacuumed and refilled new refrigerant R22.

    Readings from the compressor -
    • <LI class=MsoNormal style="COLOR: navy; mso-list: l1 level1 lfo4">water in temperature – read from the thermometer on the water line to the chiller – 15 deg. C. Water out - read from the thermometer on the water line from the chiller – 7 deg.C <LI class=MsoNormal style="COLOR: navy; mso-list: l1 level1 lfo4">Suction pressure – read from the gauge – 72 - 74PSI; discharge pressure – read from the gauge – 205 - 210PSI
    • Readings from the chiller panel

    • <LI class=MsoNormal style="COLOR: navy; mso-list: l3 level1 lfo3">Oil – 12.7 BERG. SP -4.83; DP -14 BERG <LI class=MsoNormal style="COLOR: navy; mso-list: l3 level1 lfo3">Oil – 54.1 deg C. ST -11.4. DT -73.9 deg C <LI class=MsoNormal style="COLOR: navy; mso-list: l3 level1 lfo3">S1 SAT SUCT – 4.4. SUCT SHEAT – 7.2 deg C <LI class=MsoNormal style="COLOR: navy; mso-list: l3 level1 lfo3">S1 SAT DSCH – 39.3. DSCH SHEAT – 34.7 deg c
    • Steps – 53
    Any idea to how can i solve the hunting problem.

    Thanks.



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: need help on YORK chiller

    Quote Originally Posted by nassersh View Post
    YORK chiller model YCAS0373 with 2 number DXS screw compressors.
    The problem i have with one of the compressors is that it hunts while on load - i.e the suction pressure oscillates between 70 psi and 75 psi. Its not stable though its fully loaded with the sliding valve on step 75 indicating fully open and loaded. We never had any problem with it before, it all started after we carried out comprehansive service on it. The service included change of oil, change of core filters, vacuumed and refilled new refrigerant R22.




    Readings from the compressor -
    • <LI class=MsoNormal style="COLOR: navy; mso-list: l1 level1 lfo4">water in temperature – read from the thermometer on the water line to the chiller – 15 deg. C. Water out - read from the thermometer on the water line from the chiller – 7 deg.C <LI class=MsoNormal style="COLOR: navy; mso-list: l1 level1 lfo4">Suction pressure – read from the gauge – 72 - 74PSI; discharge pressure – read from the gauge – 205 - 210PSI
    • Readings from the chiller panel

    • <LI class=MsoNormal style="COLOR: navy; mso-list: l3 level1 lfo3">Oil – 12.7 BERG. SP -4.83; DP -14 BERG <LI class=MsoNormal style="COLOR: navy; mso-list: l3 level1 lfo3">Oil – 54.1 deg C. ST -11.4. DT -73.9 deg C <LI class=MsoNormal style="COLOR: navy; mso-list: l3 level1 lfo3">S1 SAT SUCT – 4.4. SUCT SHEAT – 7.2 deg C <LI class=MsoNormal style="COLOR: navy; mso-list: l3 level1 lfo3">S1 SAT DSCH – 39.3. DSCH SHEAT – 34.7 deg c
    • Steps – 53
    Any idea to how can i solve the hunting problem.

    Thanks.
    It sounds like a cassic case of hunting?
    I might be wrong but please check....
    Your expansion valve operation and Superheat
    Grizzly
    Just an additional thought someone hasn't managed to loose a liquid line filter felt gasket in the system have they?
    It has been done before!
    Last edited by Grizzly; 01-12-2008 at 04:20 PM.

  3. #3
    Join Date
    Dec 2008
    Location
    MIDWEST, USA
    Age
    52
    Posts
    22
    Rep Power
    0

    Re: need help on YORK chiller

    nassersh,

    This maybe a stupid question, but are you sure this is not your economizer cycling?

  4. #4
    nassersh's Avatar
    nassersh Guest

    Re: need help on YORK chiller

    we dont have economiser on our chiller!

  5. #5
    Join Date
    Dec 2008
    Location
    MIDWEST, USA
    Age
    52
    Posts
    22
    Rep Power
    0

    Re: need help on YORK chiller

    Re: need help on YORK chiller
    we dont have economiser on our chiller! 10-12-2008 05:48 AM
    I'm looking in FORM 201.18-NM2 IOM and it specs one for each system on your chiller. Check your TEV and refrigerant charge/subcooling.

Similar Threads

  1. York Chiller problems
    By ingherrera in forum Commercial
    Replies: 18
    Last Post: 26-07-2011, 03:10 PM
  2. Clima Roca York Chiller
    By Chinua in forum Air Conditioning
    Replies: 5
    Last Post: 13-04-2011, 07:03 PM
  3. York Chiller
    By HVACGod in forum Commercial
    Replies: 12
    Last Post: 11-09-2010, 06:05 AM
  4. York & Trane Reciprocating Chiller
    By Gigas in forum Air Conditioning
    Replies: 3
    Last Post: 21-05-2008, 12:21 AM
  5. York Screw Chiller How low will it go?????
    By bruceboldy in forum Industrial Compressors
    Replies: 11
    Last Post: 10-08-2007, 10:29 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •