Pressure Test Levels
Hi friends...one question is bothering me from a very long time...CAN WE CHARGE OUR REFRIGERATION SYSTEM (compressor, condenser, Evaporator and refrigerant control device: i mean complete system) with 400psg. N2 or dry air pressure for leak testing purpose is this is advisable or not ??
-
29-11-2008, 09:13 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: beginer questions
For split system air conditioning (found on Mitsubishi HI manual):
Required pressure for testing air tightness in connecting pipes and indoor units of split system air conditioners prior to opening service valves and evacuation is:
R22 = 2.94MPa = 368PSIG
R407C = 3.23MPa = 468PSIG
R410A = 4.15MPa = 602PSIG
For outdoor unit, maximum pressure could depend on installed elements max pressures indicated at each element (compressor and etc...).