Hi friends...one question is bothering me from a very long time...CAN WE CHARGE OUR REFRIGERATION SYSTEM (compressor, condenser, Evaporator and refrigerant control device: i mean complete system) with 400psg. N2 or dry air pressure for leak testing purpose is this is advisable or not ??
-
29-11-2008, 09:33 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
01-12-2008, 02:36 PM #3
Re: Need help ASAP
pramoddhiman,
what a name,anyway dry nitrogen is recomended for leak testing and a 200 psi pressure that stands for 24 hours is sufficient.a 400 psi pressure is too much and may burst a type M copper pipe as i have seen before.
regards,
-
02-12-2008, 08:01 AM #4
Re: Need help ASAP
the tests pressure depends on gas used and max pressure of parts fitted