    Angry Problem with R409A system



    Hello all! Need some help. I have been working on a R409A system, it is 130 psi head, and around 27 pound suction. First call out I got was unit was tripping out on lp, drier was 100 years old (as always), moisture in system, tx had iced up so I replaced tx and orifice (probably didnt really need to) and did some filter changes every couple of weeks (ran fine). But customer had complained that evap always ices up (for last four years) . I know if unit is to small it will ice up, but checked unit, not to bad could be a little bigger but power is and issue, but distributor on this system will ice up about one minute after running, and evap coil will ice straight away as well. Now i have new drier, only other thing between drier and valve is sight glass, I have new tx valve, correct orifice (I have checked). and recently bypassed heat exchanger because I thought it may have had a small leak and was not getting full liquid line. But no joy! Distributor is not blocked. So would anyone know why this system would ice up so quickly? It is really starting to do my head in.



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Problem with R409A system

    What is superheat, subcooling, air temperatures, evaporator fins distance? Make full measurements if you wish some well taught answer!

  3. #3
    Join Date
    May 2007
    Location
    Northants
    Posts
    290
    Rep Power
    17

    Re: Problem with R409A system

    Check air flow over evap, (fan rotation), is the cond unit oversized e.g evaporating far to low with a big TD over the coil, this could cause icing, other thing to check is the humidity in the room far higher than it should be???

    CB

  4. #4
    Join Date
    Dec 2007
    Location
    US ALASKA
    Age
    62
    Posts
    16
    Rep Power
    0

    Re: Problem with R409A system

    Just about every system I've used R409a in ran with a head pressure of 150-180psi range to get satisfactory suction pressure and system charge... The sight glass didn't always clear up either but there's too many variables to address here without more data like nike is talking about...

  5. #5
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Problem with R409A system

    Quote Originally Posted by bennybluetoes View Post
    Hello all! Need some help. I have been working on a R409A system, it is 130 psi head, and around 27 pound suction. First call out I got was unit was tripping out on lp, drier was 100 years old (as always), moisture in system, tx had iced up so I replaced tx and orifice (probably didnt really need to) and did some filter changes every couple of weeks (ran fine). But customer had complained that evap always ices up (for last four years) . I know if unit is to small it will ice up, but checked unit, not to bad could be a little bigger but power is and issue, but distributor on this system will ice up about one minute after running, and evap coil will ice straight away as well. Now i have new drier, only other thing between drier and valve is sight glass, I have new tx valve, correct orifice (I have checked). and recently bypassed heat exchanger because I thought it may have had a small leak and was not getting full liquid line. But no joy! Distributor is not blocked. So would anyone know why this system would ice up so quickly? It is really starting to do my head in.

    I may have read it wrong but did you change
    the refrigerant for new? 409 is a blend and if
    it has lost any of it's composition it will work
    differently to how you expect it to work.

    Just a thought.

    If it has had new gas in then it's not that, if it is
    on the original refrigerant then I would replace it
    for new.

    Cheers taz

    .

  6. #6
    Join Date
    Jan 2009
    Location
    australia
    Age
    68
    Posts
    16
    Rep Power
    0

    Re: Problem with R409A system

    check fins aren't blocked restricting air flow

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Problem with R409A system

    It would be kinda nice if the original poster came back with some sort of reply to the help he is being given.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Jan 2009
    Location
    jax, fl,
    Posts
    23
    Rep Power
    0

    Re: Problem with R409A system

    409 is crap. sounds like the txv needs to be opened up or replaced. It is starving the evap. dont be scared of that valve. open it (turn it counterclockwise) and watch the frost disappear and then check and adjust the superheat, if you know how. you will need a full column of liquid to that txv. (full sightglass)409 is the worst and was the first R-12 drop in refrigerant made. good luck.

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. problem in Auto Refrigeration Cascade System
    By ernestlin in forum Trouble Shooting
    Replies: 17
    Last Post: 01-07-2009, 12:41 PM
  3. Heating not working on split system what is the problem?
    By airflo in forum Air Conditioning
    Replies: 10
    Last Post: 22-07-2008, 06:42 PM
  4. Mr Slim problem
    By Andy AC in forum Air Conditioning
    Replies: 1
    Last Post: 12-02-2007, 10:21 PM
  5. Automotive A/C Vent Temp Range vs System
    By Don Browney in forum Air Conditioning
    Replies: 1
    Last Post: 15-05-2002, 06:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •