Check discharge & evaporating temperature !
Hello every body , i have a simple question , may i know the accuracy of using digital temperature control to check the temperature at suction temperature at evaporator outlet.For example Danfoss EKC201 , Eliwell EWPC901 , Dixell XR20C and etc.
Can i buy a analogue thermometer with a prode ( range
20°c to 160°c ) to check the temperature at compressor output or condenser output ? Thank you .
-
28-11-2008, 03:10 PM #2
Re: Check discharge & evaporating temperature !
Some people say , not all the probe are suitable for surface contact , if i use those instruments , will i get the correct temperature ? should i spend more time to look for analogue thermometer ( it is quite difficult to buy the range from 20°c - 160°c ) ? i really want to learn the correct way .
-
28-11-2008, 03:22 PM #3
Re: Check discharge & evaporating temperature !
I use a surface probe for digital type 'k' digital thermometers like this:
http://us.fluke.com/usen/products/Ac...&category=PRTP)
I've used a few different types of surface probes, that one has lasted the longest without wearing/breaking thoughLast edited by paul_h; 28-11-2008 at 03:25 PM.
-
28-11-2008, 04:01 PM #4
Re: Check discharge & evaporating temperature !
Thanks for your reply and infomation provided !
-
28-11-2008, 05:31 PM #5
Re: Check discharge & evaporating temperature !
The round sensors delivered with those comercial regulators does quite well. Use some heat conducting grease between the sensor and the pipe, fasten it with two plastic strips and insulate well with cell foam like armaflex. Pt 1000 omh sensors delivered with the EKC201 or even better the still cheap AKC 402 has the best accuracy. The PTC sensors delivered with say Eliwell has poorer accuracy.
This setup may fit a semi permanent supervision for the evaporator outlet of a comercial system. For a quick check of the superheat a portable instrument is maybe the simplest. Be however aware of the difficulties in accurately measuring tempereatures well below freezing with a portable instrument like Fluke or any other make on a freezer system
-
29-11-2008, 07:28 PM #6
Re: Check discharge & evaporating temperature !
Thanks for your reply, i am going to evaluate again which method to use .
Similar Threads
-
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Superheat and Subcooling
By Chunk in forum FundamentalsReplies: 42Last Post: 15-01-2011, 01:24 AM -
Thermo King OptiSet
By REEFER-TEK in forum TransportReplies: 4Last Post: 06-12-2007, 07:23 PM -
TK basic micro-p features and functions
By REEFER-TEK in forum TransportReplies: 0Last Post: 05-12-2007, 06:25 PM -
Article in ACH&R News
By Gary in forum FundamentalsReplies: 8Last Post: 20-05-2003, 12:27 AM