    I have a problem with a york chiller model YSCA CA50FB, first, with the joint of york and Jhonson controls the web page is under constructions for months, so i cannot find the tech manual for that chiller.
    We lost comunicacion between the chiller and the chiller link and the BMS, some months ago we change the main borad of the chiller but we did not have the manual to make the settings on the board.
    Does someone have information about that york model? or URL link?
    V
    Dec 2008
    MIDWEST, USA
    52
    22
    Re: York Chiller problems
    Ingherrera,
    If you haven't found your information for the Microgateway, I can help you. P/M me.
    royalvino's Avatar
    royalvino Guest
    Exclamation Re: York Chiller problems
    Quote Originally Posted by ingherrera View Post
    V
    Dec 2008
    59
    22
    Hi ingherrera can I ask you to confirm the model no. only I dont recognise a YSCA, also there are some digits missing from your posted model no., if its a YCAS I can probably get you a manual. It wil also help if you can state if its 50 or 60Hz and what type of controller.
    Dec 2008
    MIDWEST, USA
    52
    22
    Quote Originally Posted by yorkie10 View Post
    His Model No. may not be correct, YSCA CA50FB.
    I think he has a YS, not a YCAS. At any rate, he has one of the following issues.
    1) Comm wiring issue to the microboard that he just replaced.
    2) Jumpers on microboard not set up properly.
    I assume that all is well with his MicroGateway to the BAS, since he only disconnect the Comm line to microboard. He will have to change his control on panel from Local to Remote (if single line panel), or to ISN (if Optiview), if he wants to start/stop, and control setpoints via BAS.
    4,698
    Is it a YSCA or a YCAS?
    See below
    for explanation.
    Dec 2005
    Centroamérica
    12
    HI, I haven't found the information colud you help me
    Quote Originally Posted by ChillyWilley View Post
    Ingherrera,
    Dec 2005
    Centroamérica
    12
    The model is YSCA CA SO CFB
    See below
    for explanation.
    Feb 2004
    132
    Wussup 32?
    Split Croatia
    6,151
    Quote Originally Posted by absrbrtek View Post
    Wussup 32?
    Do you care to translate that to plain English?
    Jun 2009
    Istanbul
    48
    1
    I need a York chiller catalog. Chiller model number is YSCA205-50-9001.
    Thank you...
    Sincelery
    Aug 2007
    Germany
    I suspect that there is a screw chiller type YS ment. CA CA does mean the cooler and condenser size where S0 is the compressor (YCCH163S). 50 is 380/400V 50Hz and FB the motor size. What type of BMS is the chiller connected to? Modbus, BacNet, Lon....?
    RTFM always thoroughly!
    Vacuum sucks!
    Sience rules!
    jaudiel's Avatar
    jaudiel Guest
    Hi, i´m new here but i hope any of you guys can help me, i´m having problems with a york chiller model YCAS140 60hrtz 460v , at firs it did´nt do scrap, untill i replace both of the current control transducers, i have to mention that due to some rust that we find inside sistem 1 we had to toke a part almost the hole system to replace every gasket (including evaporator end cap on both sides) and replace filters oil, two presure transducers and the gaskets of the volt terminals (this chiller was seriously neglected for several years due to a total lack of maintenance) and finally it was cleaned with R141b pumped tru the sistem and filtered (yes it was a lot of work) but my problem now is with the electrical sistem, sistem 2 works fine bust sistem 1 does´nt starts, i do have signal coming from the 20 terminal on the relay switch board (as manual says) but my problem is that it does´nt has signal coming from the 8 terminal for the Y Delta start up so it does´nt stars runing but if i press the contactor manualy and let go it all works fine, I already check every single transducer and termistor but everything seems fine, help i´m driving insane cant get it out of my head
    Sep 2009
    China
    11
    Quote Originally Posted by jaudiel View Post
    Pls check the relay connecting to the compressor contactors, cable between them and their fitting.
    Oct 2009
    merida mexico
    282
    to change the primary card uses the same eprom memory cards don't come with the configuration of manufactures in field is changed the chip of the old card
    sauditvengineer's Avatar
    sauditvengineer Guest
    hello guys... hope you can help me i have a problem with our chiller everytime we start up it will trip off with a det. protector cut-out signal in the control panel. Pls. explain what happens to the chiller when that signal activates... thank you
    Split Croatia
    6,151
    Quote Originally Posted by sauditvengineer View Post
    What chiller model is and what is "det. protector"?
    Do you have electrical diagram?
    Oct 2009
    merida mexico
    282
    sauditv
    could be more detailed the problem you have to help
    engineer:
    Jul 2007
    singapore
    discontinued model made in malasyia with han bell screw compressor (R407 gas)
  1. chiller problems
    By iceman6869 in forum Technical Discussions
    Last Post: 19-11-2009, 07:47 AM
  2. York & Trane Reciprocating Chiller
    By Gigas in forum Air Conditioning
    Last Post: 21-05-2008, 12:21 AM
  3. York Liquid Chiller problems.
    By kanodogg in forum Commercial
    Last Post: 09-05-2008, 09:16 PM
  4. problems with york yaa c chiller
    By paulwild in forum Commercial
    Last Post: 21-08-2007, 08:20 PM
  5. York Screw Chiller How low will it go?????
    By bruceboldy in forum Industrial Compressors
    Last Post: 10-08-2007, 10:29 PM