Results 1 to 21 of 21

Hybrid View

  1. #1
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Oil Lifting Problem in NH3 screw compressor

    Quote Originally Posted by SURESH YADAV
    We drain the 10 liter oil for every 24 hrs running from PHE chiller surge drum.
    If you have to drain this much oil every 24 hours, then the compressors/oil separators are pushing too much oil into the system.

    And, your problem may be caused by this...

    Quote Originally Posted by SURESH YADAV
    Opoeration at -6 deg. evaporation, 30 deg condensing, 150 psi discharge
    Since you provided the discharge pressure in psi, are the temperatures above in °C or °F?
    If all else fails, ask for help.


  2. #2
    Join Date
    Sep 2008
    Location
    India
    Age
    39
    Posts
    24
    Rep Power
    0

    Re: Oil Lifting Problem in NH3 screw compressor

    Quote Originally Posted by US Iceman View Post
    If you have to drain this much oil every 24 hours, then the compressors/oil separators are pushing too much oil into the system.

    And, your problem may be caused by this...



    Since you provided the discharge pressure in psi, are the temperatures above in °C or °F?
    Discharge temparature is 100 °C

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Oil Lifting Problem in NH3 screw compressor

    If the condensing temperature is 30°C (86°F) and you have 100°C (212°F) discharge temperatures the discharge superheat of the compressor is 70° (or 126° on the F Scale). That is very high!

    At the same time you say the discharge pressure is 150 psi, which is fairly close to the saturation temperature of your condensing temperature.

    You either have extremely high suction superheat or no oil cooling based on what this seems to be.

    Another possible cause for high volumes of oil loss is if the discharge pressure suddenly decreases. Do you have hot gas defrost on the evaporators? When the coils go into defrost, what happens to the discharge pressure?
    If all else fails, ask for help.


  4. #4
    Join Date
    Mar 2008
    Location
    united states
    Posts
    32
    Rep Power
    0

    Re: Oil Lifting Problem in NH3 screw compressor

    Another thing to look for is a bad check valve in another machine that may be off.. If you have another machine on the same system and it is off close the suction valve see if this solves your problem. (had similar issues here) Not sure how its piped in. But if you have a machine that is losing allot of oil i would start there. Are you draining the oil from the compressor or the surge drum? Is the sight glass on the oil separator side full? Is the pump in working order for oil return? Just some other ideas
    Last edited by Poodzy; 28-01-2009 at 02:18 AM. Reason: adding stuff

  5. #5
    vinodvlimaye's Avatar
    vinodvlimaye Guest

    Re: Oil Lifting Problem in NH3 screw compressor

    Quote Originally Posted by SURESH YADAV View Post
    Discharge temparature is 100 °C
    Have you installled secondary filter with what mesh size ?
    & coalsecent filter with what size ?

  6. #6
    vinodvlimaye's Avatar
    vinodvlimaye Guest

    Re: Oil Lifting Problem in NH3 screw compressor

    Quote Originally Posted by US Iceman View Post
    If you have to drain this much oil every 24 hours, then the compressors/oil separators are pushing too much oil into the system.

    And, your problem may be caused by this...



    Since you provided the discharge pressure in psi, are the temperatures above in °C or °F?
    Have you used the Bitzer oil seperator , or you have made its own

Similar Threads

  1. SCREW Compressor Problem
    By lana in forum Trouble Shooting
    Replies: 17
    Last Post: 24-01-2010, 04:31 AM
  2. Strange compressor problem
    By Spoc in forum Trouble Shooting
    Replies: 15
    Last Post: 09-10-2007, 05:04 PM
  3. Cupper in Screw Compressor
    By Dalmo in forum Trouble Shooting
    Replies: 7
    Last Post: 09-10-2007, 12:00 PM
  4. Stal Screw Compressor R5-mkii 100kw
    By REFSOO in forum Trouble Shooting
    Replies: 1
    Last Post: 20-01-2007, 01:09 AM
  5. Screw compressor (ATLAS GA510)
    By AndEdtec in forum Trouble Shooting
    Replies: 7
    Last Post: 21-07-2006, 08:34 PM

Posting Permissions