    Dual condensors in parallel



    Is it ok to pipe two condensors in parallel of different sizes and if so would staging the fans on a pressure switch cause any problems. Thanks for your help



  2. #2
    Join Date
    Jul 2008
    Location
    wet coast B. C.
    Age
    76
    Posts
    122
    Rep Power
    16

    Re: Dual condensors in parallel

    fireandice In my small NH3 plant one of my enginerooms has 4 different sized condensors in parallel.The lead condensor has pressure switch for controll of fans and water pump. The other condensors are manual on off. I havent noticed any condensing problems. C.D.

  3. #3
    Join Date
    Aug 2008
    Location
    Englewood, CO
    Posts
    23
    Rep Power
    0

    Re: Dual condensors in parallel

    Connecting pipe work must be performed properly. Suggest you go to www.baltimoreaircoil.com and click on 'evaporative condensers'. Order their free piping manual.

  4. #4
    Join Date
    Aug 2007
    Location
    NZ
    Age
    56
    Posts
    18
    Rep Power
    0

    Re: Dual condensors in parallel

    Would the piping layout be the same for air cooled condensers, after reading the description it looks like the condensers are required to be a reasonable height above the receiver, is there anyway around this to still make it work correctly? I am looking at adding a 30kw condenser in parallel to the existing 70kw condenser rather than replacing the 70kw unit with a completely new 100kw one. I am a bit worried about how the flow rate will be divided up between the condensers when both are running. Would like to get it right the first time without spending the extra for the new condenser, otherwise the project will not go ahead. Thanks for the replies.

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Dual condensors in parallel

    You must add a large U bend (3 to 6 feet) at the condenser outlet and then collect both in 1 collector to counteract pressure difference in both.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. Replies: 9
    Last Post: 30-01-2009, 07:50 AM
  2. Parallel compressor problem
    By dsltung in forum Fundamentals
    Replies: 21
    Last Post: 16-11-2008, 07:32 PM
  3. opinion on uneven parallel condensers
    By Dimitris in forum Technical Discussions
    Replies: 2
    Last Post: 28-05-2008, 04:23 PM
  4. Coil in Coil condensors and subcooling.
    By Bernoulli in forum Industrial
    Replies: 5
    Last Post: 16-12-2006, 08:21 AM
  5. Dual vs. Parallel Piped
    By Cool Temp in forum Industrial
    Replies: 0
    Last Post: 28-09-2005, 03:32 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •