    TEV pressure test
    Don't try this before answering.
    Let's take a TEN2 (R134 TEV from Danfoss) and fit an orifice in it.
    Connect the inlet to nitrogen and the outlet of 1/2 to a pressure indicator.
    Apply pressure of 30 bar on the inlet. What happens on the outlet?
    Sep 2003
    ISRAEL
    72
    4,248
    hi peter.
    please tell us.
    I will not try it anyway. I have a feeling the consequences are still on the ceiling.
    chemi
    Oct 2003
    5,630
    Originally posted by chemi-cool
    hi peter.
    please tell us.
    chemi
    Or what do you think that should happen? What do you expect?
    What do you mean Chemi with "the consequences are still on the ceiling"
    With many post, i have to look in a dictionary for expressions, quotes, words, especially those of Marc.
    Also for this reason is this forum usefully for me.
    shogun7's Avatar
    shogun7 Guest
    Peter Just a guess but you would probably get a combination vapor and liquid,
    Roger
    Jun 2001
    N.Ireland
    1,630
    Hi Peter
    I would think the valve would slam shut and little or nothing would come out of it, but I really wouldn't like to test that theory
    Regards. Andy.
    Originally posted by Andy
    Hi Peter
    Regards. Andy.
    Yes, or you blow the head off it
    Oct 2003
    5,630
    Blow the head off
    No, you can safely test it till 35 bar.
    We needed to test them at 30 bar according to a controller when doing a PED test.
    We had following set up from which I posted some pictures in thread Plate cooling.
    We had a coil underneath a stainless steel plate.
    Thereafter a static evap which we also connected.
    Connection: liquid 3/8 in - T 3/8 - divided to each TEN2 - each TEN ejects in his evap - LP coming out both evaps connected in a 5/8 T - final 5/8 out of the counter.
    Before installing the counter we did a pressure test like we always did in the past.
    We pinche the 5/8 and soldered it closely. In the 3/8 we installed a schraeder valve. Pascal, our tech pressure tested it via the schraeder on 25 bar and left it there until the next morning.
    Pressure had dropped from 25 bar to 5 bar.
    He had other work to do, so put some R22 into it till 5 bar and then increased pressure with nitrogen till 25 bar. Controlled in the afternoon (pressure decreased to 18 bar) with the old fashioned leak lamp (still aslo my favourite leak searching device) Found no leak. Pascal had to leave the site to do a repair but not before he increased pressure again to 30 bar.
    Next morning: pressure on 10 bar.
    I told him I shouls help him the next morning searching the leak, hopefully not in the coil undernetah the ss plate.
    So what we did (pressure dropped to 10 bar) searching for a leak for at least 20 minutes (with 2 persons) - nothing.
    I installed also a schraeder in the 5/8 and connected a pressure gauge. Applied pressure on the common inlet of the 2 TEVs and pressure on the outlet very slowly increased to 5 bar. Heated the bulb with my leak flame, nothing happened.
    I thought a restriction in the orifice but in both ?????
    Removed orifices and installed twice a 6 to be sure. Same result.
    Removed ext. eg. ofthe TEN, plugged it of, same result.
    Finally took a new TEN2 and did a liitle set up as I described at the start of this thread. Connected a reduction nut of 3/8 F -->/1/4 M on the outlet and a 1/2 - ->1/4 on the outlet.
    Pressure tested inlet on 30 bar and outlet goes till 6 to 7 bar and that's it, even if you heat it with a cigarette lighter to 50°C.
    did the test als owith anbother TEN with same result.
    This was strange.
    So can someone continue this story with an explantion because most of those I have spoken all said "Well,.. pressure should stabilise to same pressure as inlet"
    And nobody in this thread was 100% sure of his answer I think, even of how far you can pressurise it, so ...i'ts a litlle confusing.
    Sep 2003
    ISRAEL
    72
    4,248
    morning peter,
    I would check the pressure gages just to be sure.
    you can apply the pressure on both sides of the TEN and see what will hapened.
    I also think, that andy has a point.
    let us know how it goes.
    chemi
    Oct 2003
    5,630
    morning peter,
    chemi
    Chemi,
    Factory (on the other side of my street) where counter is is closed today.
    Gages reads correct.
    We did it also the reverse way (applying pressure on the outlet of the TEN) Chemi, same result.
    Andy, you wouldn't like to test the theory because of what? Exploding of the valve? You can safely test it till 35 bar and then there is still some safety margin of 1,5 to 2.
    But it remains something we - and others in this thread - hadn't expected and with which we lost a lot of valuable time before we realised that we hadn't a leak. We almost ordered disassembling the counter.
    We now applied pressure on both sides (5/8 and 3/8) to be sure that counter is leak tight. Otherwise we will block the further progress of the ongoing works of the van.
    But I will do the test again next week on a TEN2 which isn't connected to an evaporator.
    We've scheduled the start up end next week.
    Will take some pictures of it if I don't forget it.
    Oct 2003
    5,630
    External egalisation connected or not, result didn't changed anything.
    Sep 2003
    ISRAEL
    72
    4,248
    ok marc,
    please explain why?
    chemi
    Oct 2003
    5,630
    Originally posted by Marc O'Brien
    Only if the external equaliser was open to atmosphere would the full 30bar be seen in the evaporator. But internal leakage would result in some nitrogen loss to atmosphere from the uncapped external equaliser.
    Will do the test Monday again with an open external equaliser.
    Sep 2003
    ISRAEL
    72
    4,248
    thanks marc.
    chemi
    Sep 2003
    ISRAEL
    72
    4,248
    no, but it helps me to understand, what exactly do you mean.
    chemi
    St. Louis, MO
    509
    Marc is of course correct concerning the TEV pressure test. Any static pressure test of the system's low side with either the TEV's equalizer connected or capped off must be done downstream of the TEV. Conversely, any pressure test of the system's high side with either the TEV's equalizer connected of capped off must be done upstream of the TEV
    The Prof has had several occasions to explain to OEM QC folks why applying pressure to one part of the system having a TEV will not equalize thru the entire system.
    One way to get around this problem is to cap off the equalizer line itself and leave the equalizer connection on the TEV open to atmosphere. With internally equalized TEVs, you're out of luck...
    Prof Sporlan
    Sep 2003
    ISRAEL
    72
    4,248
    hi marc,
    your modesty should be admired.
    chemi
    Sep 2003
    ISRAEL
    72
    4,248
    thats allright mark, just kidding,
    never realy had the need to check a system with such high pressure, so I was wondering why.
    as a gentelman gesture to another one, it was a good explanation.
    chemi
    Oct 2003
    5,630
    chemi
    According to the VLAREM II law in Belgium (environemental law), we have to pressurise 1,5 x max operating pressure, therefore not exceeding the max allowable pressure of the components.
    So this can be 25 bar.
    In VLAREM I (15 yeras ago) could be read : Every pressure vessel, including ***** vessels has to be pressurised each 5 year with water"!!!
    But ever pressurised tubes in an evaporator??
    You can go almost to 100 bar before it explodes. Tried it myself.
    Do you have an idea of the burst pressure of a simplet PET cola bottle?
    St. Louis, MO
    509
    Now the Prof understands how Danfoss has been able to sell so many filter-driers in Belgium...
    Prof Sporlan
    May 2002
    The Netherlands
    48
    274
    I did the pressure test with the Danfoss TUAE R507 TEV, with MOP at -20C. Just to find out how high the leakage rate was with TEV fully closed.
    When pressurizing the inlet with 18 bar of air (sorry, I'm a hobbyist), the pressure at the coil outlet rose to 2 bar, and stayed there. After 24 hours, pressure was still at 2 bar.
    This showed me that I could not expect TEV leakage to equalise pressures during off-cycle in a reasonable amount of time.
    Oct 2003
    5,630
    Agree 100%, same result. Some other posted different opinions without trying it themself.
    May 2002
    The Netherlands
    48
    274
    Roger
    Nitrogen's critical temperature is -147C....
    Though, if you used WAY more pressure than 30 bar, and you left the output open to atmosphere, you might encounter droplets of liquiefied nitrogen
    (but I think you will find pieces of the TEV orbiting the earth before that happens)
  23. #23
    Nov 2003
    holland europe
    66
    78
    Re: TEV pressure test
    hey that is not strange at all:
    You are looking at a valve that should be closed when high pressure is on it.
    The membrane is pushed to a close as the topside is pressed by your nitrogen.
    So it will happen both sides. Only way to test it is take out the insert.
    If you take off the equalisation line and put it in open air while charging it will be fine. After charging mount again and pressure test.
    It looks the same as with a MOP filling. even without a MOP there is a maximum to it.
    If you reaaly want to know everything then use a pressure and a temp and make a scale of it. Same problem by the way with these electronic valves.
  1. Pressure piping test
    By Volnei in forum Industrial
    Last Post: 03-07-2010, 10:30 PM
  2. dry air for pressure test
    Last Post: 23-02-2006, 02:06 PM
  3. pressure test
    By watana in forum Fundamentals
    Last Post: 31-12-2005, 09:55 AM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Last Post: 13-07-2004, 08:28 PM