    TEV pressure test



    Don't try this before answering.

    Let's take a TEN2 (R134 TEV from Danfoss) and fit an orifice in it.
    Connect the inlet to nitrogen and the outlet of 1/2 to a pressure indicator.
    Apply pressure of 30 bar on the inlet. What happens on the outlet?



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46
    hi peter.

    please tell us.

    I will not try it anyway. I have a feeling the consequences are still on the ceiling.


    chemi

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34
    Originally posted by chemi-cool
    hi peter.

    please tell us.

    I will not try it anyway. I have a feeling the consequences are still on the ceiling.


    chemi
    Or what do you think that should happen? What do you expect?

    What do you mean Chemi with "the consequences are still on the ceiling"

    With many post, i have to look in a dictionary for expressions, quotes, words, especially those of Marc.
    Also for this reason is this forum usefully for me.

  4. #4
    shogun7's Avatar
    shogun7 Guest
    Peter Just a guess but you would probably get a combination vapor and liquid,
    Roger

  5. #5
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24
    Hi Peter
    I would think the valve would slam shut and little or nothing would come out of it, but I really wouldn't like to test that theory
    Regards. Andy.

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60
    Originally posted by Andy
    Hi Peter
    I would think the valve would slam shut and little or nothing would come out of it, but I really wouldn't like to test that theory
    Regards. Andy.
    Yes, or you blow the head off it
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34
    Blow the head off
    No, you can safely test it till 35 bar.
    We needed to test them at 30 bar according to a controller when doing a PED test.

    We had following set up from which I posted some pictures in thread Plate cooling.
    We had a coil underneath a stainless steel plate.
    Thereafter a static evap which we also connected.
    Connection: liquid 3/8 in - T 3/8 - divided to each TEN2 - each TEN ejects in his evap - LP coming out both evaps connected in a 5/8 T - final 5/8 out of the counter.

    Before installing the counter we did a pressure test like we always did in the past.
    We pinche the 5/8 and soldered it closely. In the 3/8 we installed a schraeder valve. Pascal, our tech pressure tested it via the schraeder on 25 bar and left it there until the next morning.
    Pressure had dropped from 25 bar to 5 bar.
    He had other work to do, so put some R22 into it till 5 bar and then increased pressure with nitrogen till 25 bar. Controlled in the afternoon (pressure decreased to 18 bar) with the old fashioned leak lamp (still aslo my favourite leak searching device) Found no leak. Pascal had to leave the site to do a repair but not before he increased pressure again to 30 bar.
    Next morning: pressure on 10 bar.

    I told him I shouls help him the next morning searching the leak, hopefully not in the coil undernetah the ss plate.

    So what we did (pressure dropped to 10 bar) searching for a leak for at least 20 minutes (with 2 persons) - nothing.
    I installed also a schraeder in the 5/8 and connected a pressure gauge. Applied pressure on the common inlet of the 2 TEVs and pressure on the outlet very slowly increased to 5 bar. Heated the bulb with my leak flame, nothing happened.
    I thought a restriction in the orifice but in both ?????

    Removed orifices and installed twice a 6 to be sure. Same result.
    Removed ext. eg. ofthe TEN, plugged it of, same result.

    Finally took a new TEN2 and did a liitle set up as I described at the start of this thread. Connected a reduction nut of 3/8 F -->/1/4 M on the outlet and a 1/2 - ->1/4 on the outlet.
    Pressure tested inlet on 30 bar and outlet goes till 6 to 7 bar and that's it, even if you heat it with a cigarette lighter to 50°C.
    did the test als owith anbother TEN with same result.

    This was strange.

    So can someone continue this story with an explantion because most of those I have spoken all said "Well,.. pressure should stabilise to same pressure as inlet"

    And nobody in this thread was 100% sure of his answer I think, even of how far you can pressurise it, so ...i'ts a litlle confusing.

  8. #8
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46
    morning peter,

    I would check the pressure gages just to be sure.

    you can apply the pressure on both sides of the TEN and see what will hapened.

    I also think, that andy has a point.

    let us know how it goes.

    chemi

  9. #9
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34
    Originally posted by chemi-cool
    morning peter,

    I would check the pressure gages just to be sure.

    you can apply the pressure on both sides of the TEN and see what will hapened.

    I also think, that andy has a point.

    let us know how it goes.

    chemi
    Chemi,
    Factory (on the other side of my street) where counter is is closed today.
    Gages reads correct.

    We did it also the reverse way (applying pressure on the outlet of the TEN) Chemi, same result.

    Andy, you wouldn't like to test the theory because of what? Exploding of the valve? You can safely test it till 35 bar and then there is still some safety margin of 1,5 to 2.

    But it remains something we - and others in this thread - hadn't expected and with which we lost a lot of valuable time before we realised that we hadn't a leak. We almost ordered disassembling the counter.

    We now applied pressure on both sides (5/8 and 3/8) to be sure that counter is leak tight. Otherwise we will block the further progress of the ongoing works of the van.

    But I will do the test again next week on a TEN2 which isn't connected to an evaporator.

    We've scheduled the start up end next week.

    Will take some pictures of it if I don't forget it.

  10. #10
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34
    External egalisation connected or not, result didn't changed anything.

  11. #11
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46
    ok marc,

    please explain why?


    chemi

  12. #12
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34
    Originally posted by Marc O'Brien
    Only if the external equaliser was open to atmosphere would the full 30bar be seen in the evaporator. But internal leakage would result in some nitrogen loss to atmosphere from the uncapped external equaliser.
    Will do the test Monday again with an open external equaliser.

  13. #13
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46
    thanks marc.

    chemi

  14. #14
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46
    no, but it helps me to understand, what exactly do you mean.


    chemi

  15. #15
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    510
    Rep Power
    24
    Marc is of course correct concerning the TEV pressure test. Any static pressure test of the system's low side with either the TEV's equalizer connected or capped off must be done downstream of the TEV. Conversely, any pressure test of the system's high side with either the TEV's equalizer connected of capped off must be done upstream of the TEV

    The Prof has had several occasions to explain to OEM QC folks why applying pressure to one part of the system having a TEV will not equalize thru the entire system.

    One way to get around this problem is to cap off the equalizer line itself and leave the equalizer connection on the TEV open to atmosphere. With internally equalized TEVs, you're out of luck...
    Prof Sporlan

  16. #16
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46
    hi marc,

    your modesty should be admired.

    chemi

  17. #17
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46
    thats allright mark, just kidding,

    never realy had the need to check a system with such high pressure, so I was wondering why.

    as a gentelman gesture to another one, it was a good explanation.

    chemi

  18. #18
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34
    Originally posted by chemi-cool
    thats allright mark, just kidding,

    never realy had the need to check a system with such high pressure, so I was wondering why.

    as a gentelman gesture to another one, it was a good explanation.

    chemi
    According to the VLAREM II law in Belgium (environemental law), we have to pressurise 1,5 x max operating pressure, therefore not exceeding the max allowable pressure of the components.
    So this can be 25 bar.

    In VLAREM I (15 yeras ago) could be read : Every pressure vessel, including ***** vessels has to be pressurised each 5 year with water"!!!

    But ever pressurised tubes in an evaporator??
    You can go almost to 100 bar before it explodes. Tried it myself.

    Do you have an idea of the burst pressure of a simplet PET cola bottle?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  19. #19
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    510
    Rep Power
    24
    In VLAREM I (15 yeras ago) could be read : Every pressure vessel, including ***** vessels has to be pressurised each 5 year with water"!!!
    Now the Prof understands how Danfoss has been able to sell so many filter-driers in Belgium...
    Prof Sporlan

  20. #20
    Join Date
    May 2002
    Location
    The Netherlands
    Age
    48
    Posts
    274
    Rep Power
    22
    I did the pressure test with the Danfoss TUAE R507 TEV, with MOP at -20C. Just to find out how high the leakage rate was with TEV fully closed.

    When pressurizing the inlet with 18 bar of air (sorry, I'm a hobbyist), the pressure at the coil outlet rose to 2 bar, and stayed there. After 24 hours, pressure was still at 2 bar.

    This showed me that I could not expect TEV leakage to equalise pressures during off-cycle in a reasonable amount of time.

  21. #21
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34
    Originally posted by DaBit
    I did the pressure test with the Danfoss TUAE R507 TEV, with MOP at -20C. Just to find out how high the leakage rate was with TEV fully closed.

    When pressurizing the inlet with 18 bar of air (sorry, I'm a hobbyist), the pressure at the coil outlet rose to 2 bar, and stayed there. After 24 hours, pressure was still at 2 bar.

    This showed me that I could not expect TEV leakage to equalise pressures during off-cycle in a reasonable amount of time.
    Agree 100%, same result. Some other posted different opinions without trying it themself.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  22. #22
    Join Date
    May 2002
    Location
    The Netherlands
    Age
    48
    Posts
    274
    Rep Power
    22
    Originally posted by shogun7
    Peter Just a guess but you would probably get a combination vapor and liquid,
    Roger
    Nitrogen's critical temperature is -147C....

    Though, if you used WAY more pressure than 30 bar, and you left the output open to atmosphere, you might encounter droplets of liquiefied nitrogen
    (but I think you will find pieces of the TEV orbiting the earth before that happens)

  23. #23
    Join Date
    Nov 2003
    Location
    holland europe
    Age
    65
    Posts
    78
    Rep Power
    21

    Re: TEV pressure test

    hey that is not strange at all:
    You are looking at a valve that should be closed when high pressure is on it.
    The membrane is pushed to a close as the topside is pressed by your nitrogen.
    So it will happen both sides. Only way to test it is take out the insert.
    If you take off the equalisation line and put it in open air while charging it will be fine. After charging mount again and pressure test.
    It looks the same as with a MOP filling. even without a MOP there is a maximum to it.
    If you reaaly want to know everything then use a pressure and a temp and make a scale of it. Same problem by the way with these electronic valves.

Similar Threads

  1. Pressure piping test
    By Volnei in forum Industrial
    Replies: 7
    Last Post: 03-07-2010, 10:30 PM
  2. dry air for pressure test
    By Lc_shi in forum Fundamentals
    Replies: 2
    Last Post: 23-02-2006, 03:06 PM
  3. pressure test
    By watana in forum Fundamentals
    Replies: 3
    Last Post: 31-12-2005, 10:55 AM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •