    Exclamation Environmental Room



    I have been asked by one of our customers if it is possible to build a couple of small environmental rooms. These are to test the storage of aerosol canisters. They want to run the rooms at 40C and then bring back down to 20C. There will be two rooms approx 2.5 x 3.0 metres. Both require to run independently of each other. The problem that I have is I can’t find any equipment small enough to look after the rooms. Naturally small splits are out as they will not go upto 40C. Ducted systems are too large for these rooms and start at 5KW. I need something that is still what I would call basic control, not controlled by a microprocessor, preferably that can have electrical heaters fitted to them. Does anyone know of anything that is on general supply in the UK. I have tried the usual Airedale and IMI but they do not have anything to offer.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Environmental Room

    Have you approached any AHU manufacturers about the problem?

    They should be able to come up with a simple solution for these rooms.

    Such as..

    http://www.nuaire.co.uk/Product/Comm...Handling_Units
    Last edited by Brian_UK; 25-11-2008 at 11:35 PM.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Environmental Room

    Environmental chambers are very specialized. I have worked on a few for engine emission testing and large AC rooftop units. They are nothing like a split unit, etc.

    The refrigeration systems are either custom designed for the project by an enterprising company or provided by a manufacturer who does this type of work almost exclusively.
    If all else fails, ask for help.


  4. #4
    Join Date
    Sep 2008
    Location
    Lancs - UK
    Age
    67
    Posts
    30
    Rep Power
    0

    Re: Environmental Room

    Quote Originally Posted by US Iceman View Post
    Environmental chambers are very specialized. I have worked on a few for engine emission testing and large AC rooftop units. They are nothing like a split unit, etc.

    The refrigeration systems are either custom designed for the project by an enterprising company or provided by a manufacturer who does this type of work almost exclusively.
    These rooms are not true environmental rooms as we know them, I have a number of large environmental chambers on contract. It is the small size of these rooms that is the problem, they are to enable the aerosols to be tested at 40C storage conditions. Finding equipment that as low as 2Kw on a ducted type is near impossible, and we dont have any hot water/steam near by either, so we are left with electrical heat again can't find anythig this low for close control equipment.

  5. #5
    Join Date
    Jan 2010
    Location
    Southern California
    Posts
    19
    Rep Power
    0

    Re: Environmental Room

    I started my career working for Conviron, Controlled Environments Inc. They specialize in environmental chambers and growth chambers. This is a very specialized field.

    I can help you design the system you need.

    Drop me an email at c38refrigeration@yahoo.com


    Jeff P.

Similar Threads

  1. Heat transfer coefficient - Coolpack
    By Graham in forum Fundamentals
    Replies: 10
    Last Post: 28-05-2008, 01:08 AM
  2. Thawing Room (defrosting Room For Meat)
    By arunuae in forum Commercial
    Replies: 3
    Last Post: 09-02-2008, 09:24 AM
  3. Air conditioning for operating room
    By lana in forum Air Conditioning
    Replies: 17
    Last Post: 08-04-2007, 08:36 PM
  4. troubleshoot a two door storage room
    By duraid in forum Fundamentals
    Replies: 7
    Last Post: 13-12-2006, 06:57 AM
  5. Freezer Room Panels
    By Feeze in forum Technical Discussions
    Replies: 10
    Last Post: 22-04-2005, 05:58 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •