Results 1 to 2 of 2
Thread: 407c press. temp. tables
22-11-2008, 12:48 AM #1
Have just started working with 407c. Don't come across it to much in Australia yet and didn't look at it in any detail at Trade School.
This question probably is covered by general gas laws but....
How does bubble/dew pressures affect my gauge readings?
Should I be using bubble press/temp for high or low side readings, or are all readings of refrigerant related to Dew press/temp chart????
Any good articles on the web with a simple answers?
Thanks
22-11-2008, 07:08 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: 407c press. temp. tables
The evaporator (or compressor suction) superheat is derived from the Saturated Vapour (often known as the Dew Point) P-T table.
Sub-cooling of the condensed liquid is derived from the Saturated Liquid (Bubble Point) P-T table.
www.centrogalileo.it/nuovaPA/Articoli%20tecnici/INGLESE%20CONVEGNO/RIVOIRA%20inglese.docLast edited by nike123; 22-11-2008 at 07:11 AM.
Similar Threads
Temp. Rise at duct outlet
By jwasir in forum Trouble ShootingReplies: 13Last Post: 10-05-2008, 04:22 PM -
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM -
toshiba 407c vrf problem
By philjd26 in forum Air ConditioningReplies: 4Last Post: 11-12-2007, 12:20 PM -
press or temp.?
By aaron crimmins in forum CommercialReplies: 1Last Post: 30-03-2002, 05:54 AM