21-11-2008, 11:40 PM #1
Gravity liquid/vapor separator to little?
Hi
Im from Peru, i have problems with liquid carryover to suction line compressors in ammonia system for an IQF tunnel, aeroheat model 2010, 2 Mycom N42WB, Gravity Liquid/vapor horizontal separator (2200 mm length x 600 mm dia).
When start 2nd compressor, at 67% capacity, liquid carryover right to compressors. The contractor said the size of the separator is small, need to change for 3500 mm lenght x 1200 mm dia. because when we will load the tunnel could be worse.
is that correct?
thanks
aphun
-
21-11-2008, 11:58 PM #2
Re: Gravity liquid/vapor separator to little?
i forgot diagram
-
22-11-2008, 06:45 PM #3
Re: Gravity liquid/vapor separator to little?
Hi Aphun,
600 mm is really little, at least 1000 mm
-
22-11-2008, 10:04 PM #4
Re: Gravity liquid/vapor separator to little?
The high pressure liquid level makeup is suspect by your schematic also .
It is close to dry suction, so higher velocities could cause carryover .
Make sure regulating valve is adjusted so it is feeding liquid makeup 70 - 75 % of the time when at max load .
Also make sure liquid reciever has good level so no hi pressure gas blasting into surge drum .
-
22-11-2008, 10:27 PM #5
Re: Gravity liquid/vapor separator to little?
Thanks Josef/Ranger1
Here a contractor thinks if we place a liquid acumulator tank before suction compresors could we avoid that.
But, that means increase the suction length in 10 mts (actual 18mts 5"dia) more, does it afect the suction temperature of the gas in order to get -35ºC in the tunnel?
Thanks
aphun
-
22-11-2008, 10:43 PM #6
Re: Gravity liquid/vapor separator to little?
Wont affect temps but you then also have to have heat source to boil off refrigerant that comes back to suction trap .
ie liquid line coil inside suction trap also hi level cut out float control .
-
22-11-2008, 10:51 PM #7
Re: Gravity liquid/vapor separator to little?
Hi Ranger
if the contractor wants to put inside this tank a heater like oil compressor with a level switch, in order to eliminate the liquid every time this turn on?
thanks
-
17-12-2008, 06:26 AM #8
Re: Gravity liquid/vapor separator to little?
Hi
About the liquid carryover, its not the size of vessel; we raise the suction pipe over the level of the LVS, and remove the demister pad inside, instead put drop eliminator; and the problem is gone.
aphun
-
17-12-2008, 12:33 PM #9
Re: Gravity liquid/vapor separator to little?
Originally Posted by aphun
If that is the case, then you had insufficient separation distance to dis-engage the liquid form the vapor stream.If all else fails, ask for help.
-
17-12-2008, 05:45 PM #10
Re: Gravity liquid/vapor separator to little?
With out going in and doing a design calculation on your surge drum, I would first look at a few things.
-Liquid level
-where the liquid enters the vessel in relation to suction and liquid level.
-location of wet return
-suction location
-excessive oil in the drum
You would be surprised at the number of so-called refrigeration experts that can not properly design a suction or pump drum.
Ken
-
17-12-2008, 06:02 PM #11
Re: Gravity liquid/vapor separator to little?
Originally Posted by TXiceman
I agree with you though. Most of the "experts" use rating tables and have no appreciation for the actual mechanics involved.If all else fails, ask for help.
Similar Threads
-
gravity coil
By nh3simman in forum FundamentalsReplies: 5Last Post: 25-10-2008, 02:09 PM -
Gravity liquid/vapor separator x knockout drum
By Volnei in forum NH3Replies: 23Last Post: 06-06-2008, 02:27 PM -
Gravity Recirculated PHE
By gwapa in forum NH3Replies: 37Last Post: 04-04-2007, 04:23 AM -
DX v/s Gravity
By Hemant Anand in forum IndustrialReplies: 7Last Post: 19-07-2006, 02:16 AM -
Gravity Deli not defrosting completely.
By kengineering in forum CommercialReplies: 13Last Post: 26-04-2006, 11:25 AM